100 Amp Main Panel

Discussion in 'Charging Standards and Infrastructure' started by Hut, Dec 7, 2012.

  1. Hut

    Hut Canada

    Joined:
    Dec 7, 2012
    Messages:
    74
    Location:
    Toronto
    I am located in Toronto, Canada.

    The main electric panel is my house is only rated at 100 Amp. I am planning to install the NEMA 14-50 plug in my garage.

    1. Given that I am planning to charge the Model S at night when the electric load / demand is lower. Will my 100 Amp main panel do the job or do I need to upgrade it to 200 Amp?

    2. Do I need a 50A breaker or a 40A breaker for this new NEMA 14-50 plug?

    Thanks!!
     
  2. Lloyd

    Lloyd Active Member

    Joined:
    Jan 12, 2011
    Messages:
    4,885
    Location:
    San Luis Obispo, CA
    You should be OK as long as your load during charging time is 50 amps or less, which I would think it is unless you have electric heat for your house. You need a 50 amp breaker for the 14-50, and the UMC will pull 40 amps which is 80% of the rated 50 for a continuous draw.
     
  3. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,852
    Location:
    Ottawa, Canada
    1. It should be fine. To be safe you should schedule the charge for late night so you're not using the stove, dryer, etc. If you were charging and running the stove and the dryer at the same time it might start getting dicey.

    2. You need a 50A breaker.
     
  4. Hut

    Hut Canada

    Joined:
    Dec 7, 2012
    Messages:
    74
    Location:
    Toronto
    Great info! My house is heated by a natural gas furnace.

    Does anyone have an idea how much to run a NEMA 14-50 receptacle from the basement to the garage?
     
  5. dsm363

    dsm363 Roadster + Sig Model S

    Joined:
    May 17, 2009
    Messages:
    18,235
    Location:
    Las Vegas, NV
    If they have to do a lot of work and upgrading to 200A service isn't that much more, might be worth exploring but sounds like not needed.
     
  6. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    I have very little familiarity with the CEC.

    In the US, the NEC will force you to do a load calculation to determine whether you have appropriate service for your needs. If your appliances (oven/range/furnace) are all gas-based, you should be ok for the average home. If you have an electric range or dryer, load calculations are likely going to require a service upgrade with the additional load.

    Upgrading service will be a rather expensive proposition (in the US, I tell others to expect about $2000-2500 for a 60-125A service upgrade to 200A) compared to running the new circuit. The cost of running a new circuit will depend upon the length of the wiring needed, protection needs (conduit vs. running through walls), special construction needs (fishing wire through walls, drilling joists for romex, etc.), and whether you have spaces free in your panel or some work needs to be done to make room.
     
  7. RandyS

    RandyS Fan of Elon

    Joined:
    Jul 8, 2012
    Messages:
    360
    Location:
    San Diego
    I'm in San Diego, but here is how the load calcs went for my EVSE installation (Blink on a 40amp breaker). I have a 125 amp main breaker for the house. It is interesting to see how the calculations work.

    General loads:
    2469 sq ft x 3va/sq ft = 7407 va
    two small appliance circuits = 3000 va
    microwave = 840 va
    electric oven 8.1 kw = 8100 va
    garbage disposal = 840 va
    dishwasher = 1000 va
    evse = 7200 va
    total general load = 28376 va

    first 8 kva of general load at 100% = 8000 va
    remainder of load at 40% = 8154.8 va
    total net general load = 16155 va

    hvac load:
    1 unit x 29.8A x 240v = 7152 va

    total demand load:
    total net general load = 16155 va
    total hvac load = 7152 va

    total demand load = 23307 va
    23307 va / 240v = 97 amps
    panel size = 125 amps

    calc load is about 30 amps less than panel size. Permit issued and inspector signed off...
     