1450R outlet?

Bigsm00ve

Member
Oct 12, 2015
6
0
Los Angeles California
I called tesla about my home connection and explained to them over the phone what kind of outlet I have and they said that allegedly I need a 1450r adapter but when contacting my local service center they stated that they didn't see any on the tesla website. I sent them a picture and the response was to have my Electrition look at it. Here is a picture does anyone know of the correct adapted for this outlet!!? Thank you in advance!!
 

Attachments

  • image.jpg
    image.jpg
    571.6 KB · Views: 95

linkster

Active Member
Apr 22, 2013
1,128
267
USAX2
It is a NEMA 6-50 which Tesla no longer offers a UMC connector for (there are some kicking around though). However, you MUST MUST have an electrician inspect said branch circuit before attempting to charge on this device to insure proper wire gauge, proper torque on connections, and safe over-current protection with a proper breaker.

WARNING: 6-50's AND 14-50's are NOTT always what they appear to be as they can be wired in configurations that are to code but not ALWAYS suitable for safe charging.

btw, it looks a little "shady" in that it is missing a cover plate screw, mis-matched color screw, and I think (but others will chime in to state correctly) a 6-50 requires a 2-gang box?
 
Last edited:

FlasherZ

Sig Model S + Sig Model X + Model 3 Resv
Jun 21, 2012
7,024
1,013
btw, it looks a little "shady" in that it is missing a cover plate screw, mis-matched color screw, and I think (but others will chime in to state correctly) a 6-50 requires a 2-gang box?

A single-gang box will not permit a 50-amp receptacle for 14-50 with Romex but is sufficient for other configurations.

314.16(B) dictates box fill requirements. A single-gang box (shallow, 1 3/4") allows 18 cu in., and a deep single-gang allows 24 cu in.

Each conductor has a specific volume requirement - #6 needs 5 cu in., #8 requires 3 cu in., #10 requires 2.5 cu in. - includes grounding conductor
Receptacles count for 2 conductors each at the maximum conductor size attached.
Cable clamps for wire entry count as one if the clamp is inside the box (vs. outside, which doesn't count).
Loops in the conductors to permit pulling the receptacle out can count as another one, depending on how much wire was left.

For a 14-50 receptacle with 50A circuit, NM/Romex (#6 required):
3 x #6 + 1 x #10 = 17.5 cu in conductor volume req (2 hot + neutral + ground)
2 x #6 = 10.0 cu in receptacle volume req
27.5 cu in required (single gang doesn't work)

For a 14-50 receptacle with 50A circuit, wire-in-conduit (#8):
3 x #8 + 1 x #10 = 11.5 cu in conductor (2 hot + neutral + ground)
2 x #8 = 6 cu in receptacle volume
17.5 cu in volume, shallow single gang works provided no clamps required

For a 6-50 receptacle with 50A circuit, NM/Romex (#6 required):
2 x #6 + 1 x #10 = 12.5 cu in conductor (2 hot + ground)
2 x #6 = 10.0 cu in receptacle volume req
22.5 cu in required (deep single gang only will work, provided that no clamps inside the box are required)


6-50 will obviously work with 50A circuit, #8, one less wire.

(and yes, please get good cover screws on that cover! That single screw is a countersunk cover screw, the 6-50 and 14-50 requires pan-head)
 
Last edited:

scaesare

Well-Known Member
Mar 14, 2013
8,242
13,177
NoVA
A single-gang box will not permit a 50-amp receptacle for 14-50 with Romex but is sufficient for other configurations.

Looks like you can just barely see a conduit entering on the right side of the pic?

Hopefully the conductor/box sizes comply with FlasherZ's excellent info...
 

Bigsm00ve

Member
Oct 12, 2015
6
0
Los Angeles California
WOW thank you so much for the feedback inherently more then I would have fathomed seriously just coming straight to the forums for my questions from now on. Some of you guys should really be on the payroll lol. I am having my Electrition come out today and inspect the outlet as well as sharing the information with him that you guys have posted. Thanks so much again! Truly a blessing!
 

FlasherZ

Sig Model S + Sig Model X + Model 3 Resv
Jun 21, 2012
7,024
1,013
No problem - although one other comment: Your best bet is to ask if you could get a neutral pulled into that box and have the receptacle converted to a 14-50. However, that looks like a 1/2" conduit, and the extra conductor (#8) would require a 3/4" conduit, so you'd be replacing the conduit.

If you can find a Tesla 6-50 adapter for sale somewhere (eBay, service centers, etc.) you could charge directly from that receptacle.

If it's close enough to re-work the conduit, I'd recommend that if you can't find the adapter.
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.