Perhaps the benefit of these new superchargers is only to be seen when two cars are charging at the same time, and individual cars will still charge at 90 or 120.
In the Facebook owner's group, someone said he charged at 135 kW in Lone Tree, CO and offered a picture of the 135 kW sticker.
Interesting! I will have to go down there and take a look. Besides, it's the only Colorado Supercharger that I have not tried!
I thought that was a 208V, delta connection. If that is true, with inefficiencies, they would need 400A service or better to get 135 kW out!
... Besides, it's the only Colorado Supercharger that I have not tried!...
No such thing as a 208V delta. However, even if it were a 240V delta arrangement, it would be pretty hefty - 400A 3ph service required for a single cabinet.
You get 208V because in situations where you need a lot of 120V (L-N), you can deliver it from a 208V L-L wye arrangement.
Delta configurations are usually used where you need a lot of 240V... to get 120V from it, one winding is center tapped and grounded. This gives you 120V from N-L on both sides. The "stinger" or "high-delta" leg (phase C) does become 208V, but you can't really use this for heavy loads because of the arrangement.
Do you happen to remember if the other CO SCs charged at 120kW?
Sorry for my confusion on terms. Thank you for your correction. Yes, I meant that I believe it is a 208V L-L wye connection in Lone Tree.
If I understand the way the existing "120kW" Superchargers work, they can get 120kW if they are connected with 277V L-N connections; note the Supercharger label requires the neutral with 480V service, but not with 208V service. These installs are used with 160A, electronic circuit breakers that are rated for 100% continuous load. 12 modular chargers with 4 on each phase use 160A per phase nicely. 160A * 277V * 3 = 133 kW. With 90% efficiency, that provides 120 kW out. In a 208V connection, each set of 4 modular chargers gets one of the 208V, L-L connections. This gives 208V * 160A * 3 = 100 kW draw. At 90% efficiency, that is 90kW out. BTW, the 208V connection needs to draw 160A*sqrt(3) or 277A continuous because of the L-L connections and 3-phase combining. See the label below that shows the need for 280A at 200-240V service and 160A at 480V service.
I think I got all that correct. Please check my math.
View attachment 45723
- - - Updated - - -
Silverthorne, Glenwood Springs, and Grand Junction all have 480V, 3-phase transformers and provide 120kW per Supercharger cabinet. I believe that Lone Tree got the 208V, 3-phase connection because it is uses existing 208V service at the shopping center.
Your math is correct.
I hadn't even considered that they would connect Superchargers to a 208 L-L wye configuration because of the current requirements (as you note you can't hit 120 kW with their specs @ 208V), but yeah, that would work too. However, the cables get too big and it just doesn't make sense to connect things in that way.
I suspect that the Supercharger is still capable of being connected to a 208 wye , but that would be 375A draw without any continuous load overhead considered. That would likely have to be delivered over 750 kcmil wire, which is 1" in diameter, qty 3, plus ground, for each cabinet. That's not going to be cheap if it has to be run any major distances.
I'm guessing they got an upgrade when they put in the new 135 kW units, along with a nearby transformer.
I don't understand this reaction. Technology moves on, we can all expect next years hardware to be better than this years. Even if only future cars can take the full 135kw, older cars would be no worse off than they were before the advancement in supercharger technology. And if the newer superchargers have faster throughput for newer cars, everyone will benefit when the stations are busy.
> Blanding's Box O' Buss Bars [Cottonwood]
What the?? Looks like a Mil-Spec Contract run amok. :biggrin:
--
It takes a lot of copper to carry 2,000 Amps! OTOH, 2,000 Amps at 480 Volts will support up to 12-120 kW or 11-135 kW Supercharger Cabinets at full power or a total of up to 24 Charging Stalls. I am very glad that Tesla is planning ahead for Supercharger capacity as they continue to sell more and more cars!
Random accusation or do you have supporting links? Thanks.
Could this be planning ahead for a battery swap station?
I heard they were delayed trying to decide if an attendant needed to plug the cable in for you... ;-)
I heard they were delayed trying to decide if an attendant needed to plug the cable in for you... ;-)
It takes a lot of copper to carry 2,000 Amps! OTOH, 2,000 Amps at 480 Volts will support up to 12-120 kW or 11-135 kW Supercharger Cabinets at full power or a total of up to 24 Charging Stalls.
Well then, why should we be constrained to those 480V? Why not 1,000V? Or some juicy higher number?
Cotton, Flasher and other gurus:
Well then, why should we be constrained to those 480V? Why not 1,000V? Or some juicy higher number?
That's a serious question: are there reasons other than "well, 480V is the normal max voltage hanging around in mere-mortal situations (ie, downstream of most substations)" not to consider higher voltages? In other words, if we're going to think outside the box....let's stay outside...the weather's fine!