I really prefer people to just not say this, because they usually leave out the really REALLY vital piece of information, which leads people to getting an incorrect understanding of it and doing something dangerous.By code a 60a breaker can be used with #6 romex, provided it is not a continuous load situation that violates the 80% rule. This is because there is no such thing as a 55a breaker.
This phrase I feel is not clear enough in explaining this:
Most people will not get what you're implying here.provided it is not a continuous load situation that violates the 80% rule.
To be really clear, by doing this thing, with rounding up the breaker, IT DOES NOT MAKE IT AN ACTUAL 60A RATED CIRCUIT. The wire still only has a 55A rating, so that's like the lowest common denominator, and is the limit of the circuit rating. And since there is hardly any equipment that can be configured with the settings for a 55A circuit, this just isn't useful in the vast majority of cases.
So since mentioning this is going to cause a lot of people to misunderstand and do something dangerous, I prefer not to bring that up. I've seen way too many threads on this forum of people making this exact mistake.