Thanks for posting the diagram. This is probably a little too much for me to try without adult supervision . Is a UPS like this available for sale?
You would have to verify how the UPS charging circuit interacts with the LiFePO4 batteries and the BMS. If it does a simple Constant Voltage regulation (float charge), it will probably be fine. However, if it wants to push a small current regardless and counts on the battery to absorb it, then it would destroy the LiFe batteries. If the charger in the UPS is problematic, you could use a BMS with separate charger input and find a way to separate the UPS's charging circuit from the direct battery connection. The BMS will cut off the charger when the batteries are full. Worst case, you disconnect the charging portion of the UPS and use an external CC/CV charger. These thoughts are all related to standby type UPS. With a double conversion UPS, if the internal charger is not suitable, then you just run a separate charger full time and leave the original UPS plug disconnected.
I have two 24V APC units that I've been intending to do this mod with. One is a very old SmartUPS 700 (SU700NET) and another is a larger SmartUPS 1000XL. The latter could use any size battery because it has an external Andersen connector. Either one could use a 8S1P string of A123 26650 LiFePO4 cells for a short runtime. To reduce the amp draw per cell on the 1000VA unit, you could make a 8S2P pack. That would still fit in the 1000XL battery compartment.