208v can also come from a 240v three-phase delta transformer. The voltage between any two legs will be 240v. The voltage between two of the legs and the neutral (i.e. L2-N and L3-N) will be 120v. The other leg will be 208v to the neutral. That leg is often referred to as the high leg. If your electrician gave you just the 208v high leg and the neutral and that is what he is referring to as 208 single phase then that is probably the cause.
If one of the two hot legs is the high leg that may be the problem but since I do not think the UMC uses the Neutral I do not think that would matter.
Two points of clarification here:
1. The service you describe is “240v three phase high leg delta”. Basically that says that only one phase pair is center tap grounded (neutral). There are other “delta” wiring methods (that could also be 208v or 240v) like corner grounded or ungrounded... We have seen one ungrounded setup discussed here in the forums which is kind of un-nerving as it requires special monitoring to be safe. I know the Wall Connector WILL NOT WORK on an ungrounded system. The UMC is a bit more forgiving in some ways though (specifically that it will accept hot/hot connections or hot/neutral connections without changing a setting unlike the Wall Connector), so I don’t know what it’s behavior is.
2. The UMC does not use the neutral, but it sure as heck does test to make sure ground is good and I suspect the way they do this in part is by measuring voltages from the hots to ground. These tests rely on neutral and ground being bonded and they likely dislike it when from each hot to ground don’t match.