3/4 pvc conduit already occupied with 240V 20A

Oceanwolf

Oceanwolf
Sep 12, 2015
192
88
Morgan Hill, CA
I know, I know I need to check with an electrician. I wanted to be armed with information before I talk to someone.

I have a solar system on top of my detached garage. The main panel is at the main house. Sunpower added a 100A sub panel next to the main panel and have 12 gauge cables running to the garage through a 3/4 Pvc conduit. The distance is about 10 feet

My options are;

- adding a wall charger next to the sub panel and use the full 48A, but figure out a way, how to close the garage door with the cable.
- use the conduit between the subpanel and the inverter to add a 14-50 in the garage. I wonder if I can run another set of 4 6gauge in addition to the 12gauge ones in the same conduit.

What are your thoughts?

Onur

Confirmed MX 70D - who knows when it will show up.
 
Last edited:

Aljohn

Member
Oct 17, 2014
903
502
Georgia
Have you considered pulling the 12 gauge out and running just 6 gauge. That may be an alternative to trying to pull 6 gauge 3 wire through the 3/4 conduit with the other 12 gauge inside.
 

DMage

Member
Dec 14, 2015
55
4
Orlando, FL
4 6ga wires will max a 3/4 conduit fill rating. You'd have to pull the 12 out. Having just done this with 3 6ga and 1 8ga ground in 1" conduit I am glad I upsized.
 

tezco

Sig P85
Nov 9, 2012
819
4
Colorado
You would probably exceed the 40% fill rule if you wanted to add the 6 gauges on top of the existing wiring, and enclosing more than three current carrying conductors requires that you reduce the allowed current to 80%, on top of the 80% you have to allow for continuous current situations.
 

FlasherZ

Sig Model S + Sig Model X + Model 3 Resv
Jun 21, 2012
7,024
1,013
Not only will you have issues with conduit fill, but you will also have to derate. More than 3 current-carrying conductors in a single raceway will require you to derate to 80% (for 4). This means that 12 ga. is only good to 16A, 6 ga will be good to 60A (instead of 75A conductor, 65A @ 75 degC termination).
 

Oceanwolf

Oceanwolf
Sep 12, 2015
192
88
Morgan Hill, CA
Thank you folks. It looks like I need to replace the 12 gauges with 6 gauge.
What do you think about keeping the wall charger outdoors next to the subpanel. It has 25 feet cable, it will definitely reach to the car. I need to figure out how to prevent the garage door damaging the cable.
 
  • Like
Reactions: Ampster

Oceanwolf

Oceanwolf
Sep 12, 2015
192
88
Morgan Hill, CA
I opened both the subpanel and the panel that goes to the inverter. It looks like I have 10 gauge hot and neutral wires and a 2 gauge ground. That was a big surprise to me. I don't think I will mess with the solar setup but I will just bite the bullet and get another conduit run to the garage. Maybe a 1 1/4".
Inverter Box:
17f10a4643b6c657b841ab623fdeb9c1.jpg


Subpanel:
5bd147d99c5cb70acb80a99b2984563d.jpg
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.