3/4 pvc conduit already occupied with 240V 20A

Discussion in 'Model X: Battery & Charging' started by Oceanwolf, Jan 27, 2016.

  1. Oceanwolf

    Oceanwolf Oceanwolf

    Joined:
    Sep 12, 2015
    Messages:
    117
    Location:
    Morgan Hill, CA
    #1 Oceanwolf, Jan 27, 2016
    Last edited: Jan 27, 2016
    I know, I know I need to check with an electrician. I wanted to be armed with information before I talk to someone.

    I have a solar system on top of my detached garage. The main panel is at the main house. Sunpower added a 100A sub panel next to the main panel and have 12 gauge cables running to the garage through a 3/4 Pvc conduit. The distance is about 10 feet

    My options are;

    - adding a wall charger next to the sub panel and use the full 48A, but figure out a way, how to close the garage door with the cable.
    - use the conduit between the subpanel and the inverter to add a 14-50 in the garage. I wonder if I can run another set of 4 6gauge in addition to the 12gauge ones in the same conduit.

    What are your thoughts?

    Onur

    Confirmed MX 70D - who knows when it will show up.
     
  2. Aljohn

    Aljohn Member

    Joined:
    Oct 17, 2014
    Messages:
    548
    Location:
    Georgia
    Have you considered pulling the 12 gauge out and running just 6 gauge. That may be an alternative to trying to pull 6 gauge 3 wire through the 3/4 conduit with the other 12 gauge inside.
     
  3. Oceanwolf

    Oceanwolf Oceanwolf

    Joined:
    Sep 12, 2015
    Messages:
    117
    Location:
    Morgan Hill, CA
    That is another option that I can think about
     
  4. DMage

    DMage Member

    Joined:
    Dec 14, 2015
    Messages:
    51
    Location:
    Orlando, FL
    4 6ga wires will max a 3/4 conduit fill rating. You'd have to pull the 12 out. Having just done this with 3 6ga and 1 8ga ground in 1" conduit I am glad I upsized.
     
  5. tezco

    tezco Sig P85

    Joined:
    Nov 9, 2012
    Messages:
    818
    Location:
    Colorado
    You would probably exceed the 40% fill rule if you wanted to add the 6 gauges on top of the existing wiring, and enclosing more than three current carrying conductors requires that you reduce the allowed current to 80%, on top of the 80% you have to allow for continuous current situations.
     
  6. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    Not only will you have issues with conduit fill, but you will also have to derate. More than 3 current-carrying conductors in a single raceway will require you to derate to 80% (for 4). This means that 12 ga. is only good to 16A, 6 ga will be good to 60A (instead of 75A conductor, 65A @ 75 degC termination).
     
  7. Oceanwolf

    Oceanwolf Oceanwolf

    Joined:
    Sep 12, 2015
    Messages:
    117
    Location:
    Morgan Hill, CA
    Thank you folks. It looks like I need to replace the 12 gauges with 6 gauge.
    What do you think about keeping the wall charger outdoors next to the subpanel. It has 25 feet cable, it will definitely reach to the car. I need to figure out how to prevent the garage door damaging the cable.
     
    • Like x 1
  8. Oceanwolf

    Oceanwolf Oceanwolf

    Joined:
    Sep 12, 2015
    Messages:
    117
    Location:
    Morgan Hill, CA
    I opened both the subpanel and the panel that goes to the inverter. It looks like I have 10 gauge hot and neutral wires and a 2 gauge ground. That was a big surprise to me. I don't think I will mess with the solar setup but I will just bite the bullet and get another conduit run to the garage. Maybe a 1 1/4".
    Inverter Box:
    17f10a4643b6c657b841ab623fdeb9c1.jpg

    Subpanel:
    5bd147d99c5cb70acb80a99b2984563d.jpg
     