Hello, I am hoping to get some advice on wiring setup for a gen 3 WC. I am getting a lot of conflicting info including speaking with licensed electricians. I am planning to install a 3rd gen WC. Originally I was planning on using 6/2 romex, on a 60amp breaker to get the max 48 amps. Now I am reading that this is no good because of continuous load.
So assuming thats correct, my options are:
-Use #6 THHN wire in conduit
-Install the 6/2 on a 50amp breaker and charge at 40 amps
-Use 4/2 romex which doesnt seem to be available
This sound right? For my application I have to go through a wall or two, so would I need to install conduit through the wall if I went with THHN? If I go with the 6/2 on a 50amp route, do I need to use conduit in the portion of my garage where the wire is exposed?