61851-1 compatibility question

Discussion in 'Europe' started by Kevin Sharpe, Jan 19, 2012.

  1. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    Ive seen some recent reports from people having problems with some of the Type 2 ("mennekes") Charging Stations that are being deployed in the UK.

    I've dug into this a bit and it appears that the behaviour is similar across a number of Charging Stations vendors but one thing that seems consistent is the use of 16A Type 2 to Type 1 cables with a 32A Charging Station.

    I've reviewed IEC 61851-1[ed2.0] and it says "The EVSE shall interrupt the current supply if the current capability of the cable is exceeded"

    What's the reality on the ground in Europe?
     
  2. widodh

    widodh Model S R231 EU

    Joined:
    Jan 23, 2011
    Messages:
    4,822
    Location:
    Middelburg, The Netherlands
    From what I know is that the EVSE 'measures' the capability of the cable and adjust the max current based on that.

    What I think you are seeing is that if the EV starts drawing 32A over a 16A cable without the EVSE ever advertising that current. In that case the EVSE should indeed stop delivering current. I know the EV-Box EVSE's do so, they can do either 16A or 32A and have an internal relay which selects the right fuse. They have a C16 and C32 fuse internally.
     
  3. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    yes, that would be logical and what we've implemented in our protocol controller.

    not exactly... at least one Charging Station vendor supplies no current if a 16A cable is inserted into a 32A charging station :confused:
     
  4. widodh

    widodh Model S R231 EU

    Joined:
    Jan 23, 2011
    Messages:
    4,822
    Location:
    Middelburg, The Netherlands
    As far as I know that should work.

    You plug a 16A cable into a 32A EVSE, the EVSE should see the cable is 'the limit' and adjust the max current to 16A.

    It could however be due to safety regulations. The whole circuit would allow for more then 16A, where the limitation is done by software. You could ignore the EVSE signal and draw more then 16A and burn the cable without tripping a fuse.
     
  5. dpeilow

    dpeilow Moderator

    Joined:
    May 23, 2008
    Messages:
    8,572
    Location:
    Winchester, UK
    There is a resistor in the plug which denotes the cable's capability. The EVSE measures the value and supplies the corresponding max current.

    16A cable in a 32A station should give 16A.

    32A cable in a 16A station should give 16A.


    Either way the PWM pilot signal should change to indicate to the car that it can only have 16A.
     
  6. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    sure... however, I'm aware of two 32A EVSE that supply no current if the 16A cable is fitted and I think the IEC may want a fail safe that trips if the car asks for more current than the cable can supply.... that's what the EV-Box EVSE's do...
     
  7. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    agreed that's logical and what our DIN PWM signal does. However, in a fault condition it's possible to supply 32A with a 16A cable... maybe that's what the IEC are trying to prevent
     
  8. dpeilow

    dpeilow Moderator

    Joined:
    May 23, 2008
    Messages:
    8,572
    Location:
    Winchester, UK
    It's a bad implementation then, because the car should not be able to ask for more if it is getting the correct pilot.

    On a car with Mennekes input there is a second failsafe resistor at that end too. J1772 cars don't have it though.

    I guess I have all this to look forward to...
     
  9. AndrewBissell

    AndrewBissell Member

    Joined:
    Apr 16, 2009
    Messages:
    645
    If EVSEs do this then they are breaking the standard. They become useless for most current EVs.
     
  10. Eberhard

    Eberhard #421 Model S #S32

    Joined:
    Oct 17, 2010
    Messages:
    1,141
    Location:
    Germany
    yesterday, i got my official Tesla-Mennekes cable. I will do tests next few days.
     
  11. widodh

    widodh Model S R231 EU

    Joined:
    Jan 23, 2011
    Messages:
    4,822
    Location:
    Middelburg, The Netherlands
    True, but it might be reality.

    EV-Box told me (like I mentioned) that they install a C16 AND C32 fuse in a 32A EVSE, since technically the possibility exists that due to a malfunction somewhere the EV starts drawing 32A over a 16A cable without tripping a fuse. That could lead to dangerous situations.

    It is however to bad, since an EVSE can increment from 16A to 32A in steps of 4(?) Amps.
     
  12. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    agreed... it makes no sense to me :confused:
     
  13. dpeilow

    dpeilow Moderator

    Joined:
    May 23, 2008
    Messages:
    8,572
    Location:
    Winchester, UK
    Maybe changing the pilot signal on the fly is too complex for these poor vendors...

    Care to name and shame?


    Bottom line is that buying a 16A cable seem to be a false economy. I had that opinion anyway.
     
  14. Kevin Sharpe

    Kevin Sharpe Active Member

    Joined:
    Jul 29, 2010
    Messages:
    1,761
    Location:
    Bradford on Avon, UK
    What's interesting about this is that IEC 61851-1{ed2.0} has four resistor codings for 13A, 20A, 32A, and 63A (3 Phase)/70A (1 Phase) which implies that a 16A cable would be protected by a 16A fuse but would only charge at 13A....
     