Hi All,
I took delivery of my Model 2 days ago. In preparation for the purchase, I had a licensed electrician install a NEMA 15-40 outlet powered by 50 amps in my garage. The circuit box, unfortunately, is on the other side of the house so he ran 6/3 MC cable across the width of my basement which was about 75 ft of cable. I purchased the Clipper Creek 40A EVSE as my charger.
40A Level 2 EVSE HCS-50P with NEMA 14-50 | ClipperCreek

My issue is that my breaker seems to occasionally trip (3 times so far) when I open the Tesla app while the charging cord is connected to the car. The car was not actively charging during any of these periods. I have done at least two charges without obvious incident and the app indicated the car was charging with 40 amps at roughly 9-10kW.

I searched the forum and several threads noted that having the breaker on a GFCI may not play nicely with the car. I believe the electrician re-used the breaker that previously was connected to an outside hot tub and I would assume had a GFCI. It seems like this may be what I should pursue but I wanted to get the community's feedback in case there is something about this situation that indicates a different problem.

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.


SUPPORT TMC
Top