I have an existing 30A 240V circuit (3 wire, with ground) in my garage that is no longer being used for anything else, and I could re-route the cable and receptacle NEMA 14-30) to a more convenient location for charging my Model Y. I could also free up space in my breaker box for a new double pole breaker, and install a new circuit with some spare 8 gauge cable (2 wire, with ground) I have; I'd use this to put in a NEMA 10-30 receptacle. I don't require anything more than a 30A charging capability for my needs, so my question is whether there is any advantage to choosing one NEMA version over the other if I have the choice. Thanks.
 

jcanoe

Well-Known Member
Oct 2, 2020
5,737
6,358
Maryland
The 10-30 is not allowed for new installations. Use the 14-30 for a 30A circuit as it has the ground connection missing from the 10-30. Existing 10-30 installations, i.e. dryer outlets are grandfathered. These days when you purchase a new electric dryer you also need to purchase the correct power plug wire kit, i.e. 10-30 or 14-30 for your home.
 
10-30 (hot-hot-neutral) isn’t legal for new installs. For a 30A circuit, your choices are 6-30 (hot-hot-ground) or 14-30 (hot-hot-neutral-ground).

If you’re doing this with 2-wire + ground cable you have lying around, it might make sense to install a 6-30 and get a 6-30 adapter from evse adapters. NEMA 6-30 Adapter for Tesla Model S/X/3/Y Gen 2 – EVSE Adapters
 
If you sell the property, the potential new owner might well force you to bring the electrics up to code.

Might be better to update now, rather than have an ungrounded outlet.😃

An electrician is recommended.
Meh. You can always tell them “No”, or that you will disable the outlet. Usually that will quiet the buyer. Buyers have almost no power to make any demands in the current seller’s market.
 
  • Like
Reactions: ucmndd

Rocky_H

Well-Known Member
Feb 19, 2015
8,124
10,350
Boise, ID
If you sell the property, the potential new owner might well force you to bring the electrics up to code.

Might be better to update now, rather than have an ungrounded outlet.
Bring exactly what up to code? I haven't seen anything mentioned yet that is not up to code. He does not currently have a 10-30.
I have an existing 30A 240V circuit (3 wire, with ground)
"with ground"
All code says about these is that you cannot install new 10-30 outlets, which we have already advised him not to do. But code says any existing 10-30 outlets that are already there can stay there and do not have to be changed or upgraded. It even allows replacing a broken 10-30 receptacle with a new 10-30 if that's what it already was.
 

Products we're discussing on TMC...

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.