No worries, I think I'm tying to work out whether the on-board charger will do what it can to get the combination of volts and amps to reach the 10 kW limit, assuming the supply is large enough.Edit: I (now) see you had "assuming wiring allows" so I didn't mean to come off as telling you something you already knew.
It's the 'whichever comes first' that interests me. If the HPWC was connected to 208 volts with - say - 80 amps available, and a single charger car plugged in, would it pull more than 40 amps to maximize the 10 kW charging rate? I'm wondering if the installation I visited had been set for 40 amps, because the owner had a single charger (or the wiring wasn't quite large enough to go to 80) and the lower voltage wasn't considered.For the second, I am pretty sure the limit for each charging module is 10 kW or 40 Amps, whichever come first. At a 200 Volt J1772 with 50 Amps offered, a single charger MS can accept 200V * 40A or 8 kW; a dual charger MS can accept the full 200V * 50A or 10 kW. The interesting question is if 277 Volts is offered at 50 Amps, I assume that the single charger car could take 10 kW or 36 Amps, and the dual charger car would be able to take 277V * 50A or 13.85 kW.
But to be on topic, I've charged at a public J1772 charge station and also a HPWC at a business in the last week. In both cases, the voltage was in the low 200 volt range. The HPWC was about 206, so I'm inferring it was on a three phase circuit (know just enough to make dangerous assumptions) and the J1772 was 203, so perhaps the same sort of three phase source power.
By way of explanation, typical household services are supplied by a split phase 120/240 volt system. There are two live conductors and a neutral. The live conductors are 180 degrees out of phase, so when you connect them together, you get 240 volts but when you connect either one to the neutral, you get 120 volts. Small commercial businesses are often serviced at 120/208 volts 3-phase, 4 wire. There are 3 live conductors each 120 degrees out of phase and a neutral. Each phase to neutral will yield 120 volts, but taking two phases will yield only 208 volts and not 240 volts because of the different phase relationship.
In either case, the EVSE is supplied by two live conductors, so on a 120/240 volt system the equipment will see 240 volts and on a 120/208 volt system, the equipment will see 208 volts. These are "nominal" voltages and will often be lower due to voltage drops caused by resistance in the system.
Semantical (but annoyingly pedantic) item to get out of the way first:
The public J1772 sites are "charging stations" (not chargers) as the AC charger is in the car itself.
CHAdeMO and Tesla Supercharging stations (on the other hand) are DC charging where the charger is external to the car and they feed DC power directly to the battery pack in the car.
"...when you connect them together..." I think you meant when you connect between them...
Yes, I've had to learn the basics of this on projects where Hydro supplies three phase and the electrical consultant designs 120 v street lights - LOLIn either case, the EVSE is supplied by two live conductors, so on a 120/240 volt system the equipment will see 240 volts and on a 120/208 volt system, the equipment will see 208 volts. These are "nominal" voltages and will often be lower due to voltage drops caused by resistance in the system.
But not for very long...Right! Something completely different happens when you connect them together :scared:
What I'm trying to work out is whether the on-board charger can draw more current to get to the 10 kW maximum, if the voltage is at 208 instead of 240. I'm wondering if the person setting DIP switches in the HPWC might think "the car can only accept 40 amps, so I'll set the switches accordingly, even though I've got circuit capacity for more", when in fact, the 208 source might mean the car could utilize more to maximize charge speed.
The charger in the car will max out at 40A or 10kW, whichever comes first. 40A at 240V = 9.6kW. If you feed >250V, the current draw would decrease to limit total power to 10kW (indications are that the chargers are rated to 277V, but who knows about the rest of the system).Yes, I've had to learn the basics of this on projects where Hydro supplies three phase and the electrical consultant designs 120 v street lights - LOL
I'm doing this from memory, but somewhere I remember seeing a photo of a Model S charger that had a sticker on it that said "100VAC - 277VAC". But I wouldn't try to connect a car to 277 (bad things might happen).I don't remember where I read it, but the Model S chargers are rated 250V 40A max. I don't know what would happen if you connect 277V. My first guess is the car would not allow charging with the voltage out of spec. If it charges at 277 though, it will probably still draw 40A and charge at about 11kW.
10 kW capable on-board charger with the following input compatibility: 85-265 V, 45-65 Hz, 1-40 A (Optional 20 kW capable Dual Chargers increases input compatibility to 80 A)
From Model S Specifications | Tesla Motors
I am certain that at one time I read 250V, but nonetheless it is still shy of 277. If you could find 265 volts, you could charge at 10.6kW.
I don't think I'm making my question clear. Let's say the wiring to the HPWC is capable of 80 amps continuous. Or 5,000 amps. Lots more than we can use.The charger in the car will max out at 40A or 10kW, whichever comes first. 40A at 240V = 9.6kW. If you feed >250V, the current draw would decrease to limit total power to 10kW (indications are that the chargers are rated to 277V, but who knows about the rest of the system).
The car will not (and cannot, without violating the J1772 standard) increase current draw beyond what is advertised by the EVSE to compensate for low voltage (or any other reason), without overloading the EVSE and/or its supply circuit.
The installer cannot (without violating NEC) increase the jumper settings to compensate for low voltage, without overloading the circuit.
Conductors are sized based on current flow, not power. Voltage is irrelevant (assuming you don't reach dielectric breakdown of insulation). 10ga=30A intermittent, 24A continuous at 100V, 120V, 240V, 277V, 480V, or 4800V.
Except if you live in PA, where you take delivery, then have to go to an auto tag service, pay taxes and registration fees, then finally make an appointment with a private mechanic to inspect your brand new vehicle (Tesla isn't licensed to do it).One of the best things about Tesla is stores rather than dealers.
So the question is, since the car decides how much power it can use to a maximum, would setting the HPWC switches to something higher (say 80 amps in case a dual charger car plugged in), allow the car to max to 10 kW, or would it stay at 208 volts times 40 amps? Or stated another way, if a single charger car plugged into a 208 volt HPWC on an 80 amp circuit, would it pull a maximum of 40 amps at 208 volts, or would it ramp up to closer to 45 amps to reach 10 kW?