I must have watched far more than a dozen Wall Connector Install videos on YouTube by NON-Electricians. I think every single one I've seen has either violated the latest NEC code during the install, or has said "you could instead" <fill in the blank> which would violate the latest NEC. This video is no exception.
In the posted video at time stamp 5:00 the presenter explains that the wire he used doesn't meet code, but he couldn't find the correct wire at Home Depot, and didn't want to special order the correct wire.
Page 3 of the Tesla Wall Connector installation manual explicitly states:
The chart the video shows at 5:00 lists the ampacity of 6 AWG, 90° C-rated copper wire as 75 amps, the MINIMUM capacity Tesla specifies for full power operation. The YouTuber choose to instead install 6 AWG, 60° C-rated copper wire instead, which is only rated for 55 amps, two levels down from the specified MINIMUM.. Yet he still stuck a 60 amp breaker on it and claimed it is safe. I would say he didn't know about the code's 80% down rating for continuous duty circuits, but around time stamp 8:48 he explicitly talks about the 80% down rating!
My next gripe is around 6:19 where he says he is going to make the ground wire WHITE. Apparently he was also too ignorant or lazy to purchase a roll of green electrical tape while he was at Home Depot. Then he could have used the green tape to MARK both ends of the WHITE wire as GREEN, and legitimately used it as a GROUND wire. He even talks about how ground and neutral must be separated in sub-panels, but forgets some future home owner might convert what is currently his main panel into a sub-panel. Yet unless psychic would not realize that he had used WHITE wire as GROUND!
NOTE: I have learned a few things from watching Wall Connector install videos. For example, don't screw the wall connector base to the wall until after you connect the wire/conduit. It is much easier to adjust the location you drive screws by a fraction of an inch, than to adjust the location of conduit. It is also important to think about how that charging cable will hang when picking the Wall Connector location. One YouTuber had to relocate their Wall Connector after not giving cable management enough thought.
While actual Electricians can still disagree on details of code, if you are using YouTube for Wall Connector installation guidance, search for generic Electrical instruction, not for Wall Connector install videos. For example, if you are going to be running MC 6/2 cable, you might find these two videos useful.
My disclaimer: I am NOT an Electrician, but I can at least read Tesla's instructions!