The word AMBIGUITY comes to mind. This should be BLACK and WHITE with ZERO room to apply individual interpretations.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Correct me if i am wrong but the ROmex wires cannot be run in conduits? Apparently one must assume your conduits are filled with water at all times so you need something that is wet rated.
The main thing is because of how badly/cheaply the lugs are made, it's much more likely to not get the wires in properly and tightened effectively, so there's more chance of a bad install. The Hubbel, Cooper, and Bryant have better lugs that hold the wires more effectively and I think all use hex wrench screws so they can be tightened better.
NM cable can be run in conduit when needed to be protected from physical damage.
The 2017 National Electrical Code (US) does not prohibit the use of NM cable inside conduit in any part of the code regardless of the length. It can be used for 300FT if desired, but that would be a brutal pull with the NM cable sheathing.NM cable can be run conduit for a short distance to protect it from damage.
When you do that the conduit is called a "sleeve", because running NM cable in conduit raceway is not allowed.
A "Short distance" is up to the local inspector. Typical rules of thumb are a few feet, up to the ceiling/floor, no bends except for one immediately out of the enclosure, and similar ad hoc justifications. Generally you won't be allowed to a complete run of NM in a conduit (ahhh, "sleeve") unless it's between two adjacent enclosures.
You should look up the details if this might apply to you.
Just the fact that there is so much ambiguity in these codes leads me to believe that many times they’re based on what I like to call Colonic Information Extraction (and yes, this occurs all the time, even among qualified engineering talent). All I know is that mine is in, functional, wired tightly, secured appropriately, not getting too hot (I’ve checked during peak ramp up with IR thermometer), and looks good in the garage. Lastly, I can always claim the ultimate true statement, “rednecks do what rednecks do…” LOL
The common usage scenario for this is when you need to transition between two locations. Like you have either above ceiling or inside wall, where NM-B is normally used, and then it needs to come out and run along a wall surface for a bit. NM-B just isn't allowed to be openly exposed on the outside of a wall like that. So frequently that last bit will be put in some conduit to avoid cut, junction box, etc. to switch to wires-in-conduit.
Wow this all gave me a headache, which only got worse when I decided to go check and see how the electrition installed my wall connector. It's on a 60amp breaker with 6/3 Romex, which is apparently not to code. Guess I'll be changing the breaker size to a 50amp, kind of defeated the reason for the wall connector install. I guess I should have just had a 14-50 outlet installed instead. At least I didn't directly pay the electrician, it was installed when I built the house. If I hired him to just do this job and he messed up, I'd be calling him back.
If you don’t want to run conduit and separate wires and want similar convenience of NM cable (Romex), you can pull MC cable. 6/2 is all you need for the Wall Connector and you’ll get 48A on your 60A breaker.
MC Cable | Wire & Cable Your Way
Do you even notice what just happened? Your lack of clear wording shows the problem that probably causes most of these. You're asking why people think 6 gauge is acceptable for a 60A circuit? BECAUSE IT IS! But only if it's individual wires in conduit. It isn't for Romex. But people may have just heard that simple thing: 6 ga = 60A, but don't know enough about the various wire types to understand that it makes a difference, and they pick the wrong type and get it wrong.Why do people continue to believe that it is ok to install 6 gauge wire for a 60A circuit? 55A is the maximum for the circuit rating when using 6 gauge wire regardless of whether the maximum draw is less than 55A, i.e. 48A for the Wall Connector.
Your post helped me realize that my current charging circuit (I believe it uses MC 6/3 wire) may be able to be used with a 60A breaker. I always thought this circuit was limited to 50A. The circuit currently has a 50A breaker because of the 14-50 receptacle. There is nothing printed on the metallic cladding as far as I can see so I will have to ask my electrician what he installed. If it turns out to be 8/3 wire then it is limited to 50A.Do you even notice what just happened? Your lack of clear wording shows the problem that probably causes most of these. You're asking why people think 6 gauge is acceptable for a 60A circuit? BECAUSE IT IS! But only if it's individual wires in conduit. It isn't for Romex. But people may have just heard that simple thing: 6 ga = 60A, but don't know enough about the various wire types to understand that it makes a difference, and they pick the wrong type and get it wrong.
FWIW I've got a Gen2 HPWC running at 60A for 3 years now that's connected half via 6/3 romex, and half via THHN in EMT. Nothing is overheating or causing any issues. When I sized all of the parts for the install, I consulted an electrician. Connect your charger any way you like, but please stop whining about how other people choose to do it. There is a reason you go to a trade school to be an electrician instead of reading forum posts or watching a few you-tube videos.
Huh--that's not good.FWIW I've got a Gen2 HPWC running at 60A for 3 years now that's connected half via 6/3 romex, and half via THHN in EMT.
Sure, and people remove and disable safety features on products all the time and frequently get away with it for quite a while. Not relevant to whether that's a good idea or not.Nothing is overheating or causing any issues.
...not very well, apparently. Either you didn't accurately describe what you were doing, or he gave you and incorrect answer.When I sized all of the parts for the install, I consulted an electrician.
It's certainly not whining. The is very specifically informing people of the code and making them aware of violations they are committing. If they choose to ignore that, and go ahead with non-compliant installations, OK, that is on them, but I wouldn't feel right with people suffering some consequences from just not knowing that they have those violations because no one told them. That would be kind of sad to not help someone out like that.Connect your charger any way you like, but please stop whining about how other people choose to do it.
This is just hilarious! Someone who went to a trade school to become and electrician SHOULD KNOW that this is a code violation and should have told you that was wrong. This is information. It is possible for people to read and know that information, even if they did not go to a training school on that topic. And yes, of course there is a lot more information and methods and techniques someone would learn in training to become an electrician. I don't try to answer a lot of more detailed questions about things in those more general areas, because I do not claim to know those, so I'm not just going to throw out uninformed opinions on them, but this is really basic information documented in ampacity tables of what the various wire types are rated for, so this particular thing pretty easy for a lot of people to know it or look it up.There is a reason you go to a trade school to be an electrician instead of reading forum posts or watching a few you-tube videos.