Are you using a disconnect for your Wall charger ?

regazzoni

Member
Jul 10, 2019
42
3
machu picchu
Just wondering if people generally get a disconnect for a wall charger.
Code probably varies across US. In case anyone has experience in NW suburbs of Chicago I...
 

jjrandorin

Moderator, Model 3, Tesla Energy Forums
Nov 28, 2018
7,650
8,434
Riverside Co. CA
I am not. I think it depends on what code requires for the size of the circuit but I am not 100% on that. I have a 60 amp circuit, which charges my car at 48amps. I believe if its larger than 60 amps it might require a disconnect in some places.
 

eprosenx

Active Member
May 30, 2018
2,065
2,482
Beaverton, OR
Just wondering if people generally get a disconnect for a wall charger.
Code probably varies across US. In case anyone has experience in NW suburbs of Chicago I...

Howdy!

I have posted about this numerous times on this forum (search google for "site:teslamotorsclub.com eprosenx disconnect"). Article 625.43 is the relative code section. I have posted the actual code snippets several times.

Basically unless you have OVER a 60a circuit (a 60a circuit itself is fine), OR you are installing something more than 150 volts to ground (which unless you are doing a 277v feed you are not - a 240v circuit in a residence or 208v in commercial is only 120v to ground) then this provision DOES NOT apply.

When it does apply, my reading of it is that the disconnect just needs to be "readily accessible" and that you can lock it in the off position. Generally a few dollar handle cover on the breaker itself meets these requirements even if the breaker is not in line of sight of the EVSE (there is no requirement for line of sight or a specific distance).

Of course local jurisdictions could have modifications however they like. I am quoting 2017 NEC. Your state or local government might modify that...

I personally think disconnects are ugly and totally un-necessary. You just don't see them here in Portland/Oregon at all. None of the public chargers have them and their power sources are all panels locked up inside... It is not like an HVAC unit that technicians are in and out of constantly...
 

eprosenx

Active Member
May 30, 2018
2,065
2,482
Beaverton, OR
I think proximity to the main panel is a factor in whether a cutoff is required, too.

There is no provision in the code that states this. All that it says is “Readily Accessible” and when looking at definitions for that it says you can’t have to use a ladder, etc...

So even if you install the Wall Connector in the garage and the breaker panel is in the basement I don’t think this a problem. Lock off ability is common for dishwashers and wall heaters in residences. There is not a requirement for these to be in line of sight...

Again though, it may all come down to the local municipality and what a given inspector wants.
 

gfunkdave

Member
Aug 10, 2016
120
165
Portland, ME
My town has adopted: "National Electric Code, 2017 Edition"

Aside code, does it seem like a good idea? or at least a switch?
i.e. Leviton 60 Amp 600 Volt Industrial Grade Double Pole Single Phase AC Manual Motor Controller Toggle Switch - Black-MS602-FW - The Home Depot

Sure, if you want to do it there's no reason not to (and a bunch of mostly convenience reasons to do it). People are just saying there's probably no hard and fast requirement. If it were me, I'd probably put in a disconnect just so I could turn the thing off easily if I wanted to open it up or something.
 

jerry33

(S85-3/2/13 traded in) X LR: F2611##-3/27/20
Mar 8, 2012
19,565
21,936
Texas
No, the breaker is about 20 cm away. Actually, a switch is a kind of silly rule because in the unlikely event the car catches on fire, switching the breaker off won't help, and if the wall charger has an issue, it means the breaker isn't doing it's job.
 
Last edited:
  • Like
Reactions: eprosenx

DrSmile

Member
Nov 7, 2018
219
138
Northern NJ
The town inspector made me put one in. I actually think it's a good idea, if anything goes wrong it's nice to have an accessible switch to turn everything off.
 

ajdelange

Active Member
Dec 10, 2018
1,077
540
Virginia/Quebec
No, the breaker is about 20 cm away. Actually, a switch is a kind of silly rule because in the unlikely event the car catches on fire, switching the breaker off won't help, and if the wall charger has an issue, it means the breaker isn't doing it's job.

Having a way to disconnect in an emergency is only one of the reasons these are required. The ability to lock out the circuit is another. It is common in industrial settings to have a requirement that one or more padlocks be in place on a lockable disconnect with the key(s) in the possession of appropriate personnel before any work can be done on a machine connected to that disconnect. This makes a lot of sense in an industrial setting but my garage is not an industrial setting and it does seem a little silly there but it is in the code and had it installed. Before leaving for the summer I flipped it off (thus assuring myself that the HPWC won't burst into flames while we're gone) but I didn't lock it.
 

Phlier

Bluebird
Jun 12, 2019
1,374
1,701
Utah
I had an electrician install my Wall Connector. I asked him to install a 100 amp breaker and the wiring to support it, as I'm hoping to add another Tesla to the household "soon". He did put in a disconnect, stating that it would make it easier to add the second charger.

He also did the actual installation of the Wall Connector itself. After he read the Wall Connector manual, he said that he didn't need to install a GFI breaker, as the Wall Connector itself acted as a GFI.
 

Phlier

Bluebird
Jun 12, 2019
1,374
1,701
Utah
Over 60A it is not an option. It is required by the NEC. But it will make installation of a second HPWC easier both because the lugs will be convenient and because he can turn it off when he connects to them.
Thanks for that. Not being a sparky, I didn't understand what he was talking about, but I trust both him and his company completely. I've used his company for electrician services for 25 years. Not the cheapest in the business, but I'll pay for the best... every time.

Even though I told him he didn't need to stay, he insisted on making sure the car would actually charge. I told him that the computer in the HPWC would diagnose any issues, and the green light on the face of it meant everything was fine. He waited 20 extra minutes at no charge for my wife to get home with the car so he could make sure that it charged OK.
 

ajdelange

Active Member
Dec 10, 2018
1,077
540
Virginia/Quebec
Individual cities/counties/townships may have their own regulations which require a separate disconnect when the circuit is less than 60 A and/or impose other requirements such as where it must be located. The national requirement is only that it be readily accessible.
 
  • Informative
Reactions: Rocky_H

ajdelange

Active Member
Dec 10, 2018
1,077
540
Virginia/Quebec
I'll point out again that
1)No disconnect is required by the NEC anywhere for a 60 amp or smaller installation but your local jurisdiction may require one
2)It isn't just a disconnect that is required. It is a lockable disconnect. Whether a circuit breaker is deemed lockable or not is between you and the inspecting authority.
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.