Wondering if anyone has used a Tesla PV/ESS setup with on-demand / tankless (specifically electric) water heaters?
TL;DR...could you split a 36kW tankless electric water heater across both your backed up load center and non-backed up (main panel) to have some hot water in the event of a power outage...but not sacrifice a majority of your backed up load center to heating water (or have to get an excessive amount of ESS).
Looking at specs…PW+ is
And Powerwall2 is
So for a Rheem 36kW (Find product information, documents, videos, and installation assistance for the Rheem Professional Classic Series: RTEX-36), which requires 4x40A (36kW) when operating at 8gpm flow it would seem powewalls cannot cut it.
First, based on above specs...you'd need like 2xPW+ (2x9.6kW) and 4xPW2 (4x5kW) in parallel giving you 39.2kW output if you were off-grid (and that appears it would also require full sun from the PV)...if I'm doing this correctly.
Additionally, it would seem impractical in that I think Tesla limits the backed up Load Center for your house to either 200A or 225A. This would mean taking 160A out of your load calc for backing up the house, leaving you with not very much headroom for all other electrical lightning, appliances, EVSE, etc. Also, does this get considered a "continuous" load by the NEC? In which case wouldn't you have to uprate by 125%, so actually you would need to use 200A for the load calc on the back'd up load center? So there goes all your power!
It got me thinking...since the tankless 36kW is really just 4 parallel heating elements, 9kW each...could you in theory run 3x of the 40A breakers off your main panel which is not backed up and will only get power from the grid and not your PV or ESS (lets assume in this case you have a 300A or 400A service from utility)...and then only run a single 40A breaker off the backed up load center, running a 9kW element.
1) is this an acceptable config? Do the 4x breakers and circuits for the 4 heating elements have to run off the same load center for any reason? Or can you split them 3 and 1?
2) will a tankless electric water heater function should only one of the circuits (40A, 9kW) be operational? Thinking the power goes out, so you lose grid power (and 3x40A, three of the four heating elements)? Will it just basically downgrade the WH to a single 40A/9kW heater...which should be able to handle ~2.0gpm with a decent temperature rise...which is enough to take a hot shower.
This would see like a reasonable compromise. Most of the time you'll have the full 160A / 36kW available, but without having to sacrifice a major amount of Amps for your backed up load center. But, you will still have a hot shower should you lose power.
Havent done any of the financial calcs to see if this is even worth it (natural gas is pretty cheap). But in an earthquake, you might lose case...with a limp along tankless electric + ESS + PV, you could manage indefinitely. Also, I believe electric tankless have a the least maintenance and highest efficiency.
TL;DR...could you split a 36kW tankless electric water heater across both your backed up load center and non-backed up (main panel) to have some hot water in the event of a power outage...but not sacrifice a majority of your backed up load center to heating water (or have to get an excessive amount of ESS).
Looking at specs…PW+ is
And Powerwall2 is
So for a Rheem 36kW (Find product information, documents, videos, and installation assistance for the Rheem Professional Classic Series: RTEX-36), which requires 4x40A (36kW) when operating at 8gpm flow it would seem powewalls cannot cut it.
First, based on above specs...you'd need like 2xPW+ (2x9.6kW) and 4xPW2 (4x5kW) in parallel giving you 39.2kW output if you were off-grid (and that appears it would also require full sun from the PV)...if I'm doing this correctly.
Additionally, it would seem impractical in that I think Tesla limits the backed up Load Center for your house to either 200A or 225A. This would mean taking 160A out of your load calc for backing up the house, leaving you with not very much headroom for all other electrical lightning, appliances, EVSE, etc. Also, does this get considered a "continuous" load by the NEC? In which case wouldn't you have to uprate by 125%, so actually you would need to use 200A for the load calc on the back'd up load center? So there goes all your power!
It got me thinking...since the tankless 36kW is really just 4 parallel heating elements, 9kW each...could you in theory run 3x of the 40A breakers off your main panel which is not backed up and will only get power from the grid and not your PV or ESS (lets assume in this case you have a 300A or 400A service from utility)...and then only run a single 40A breaker off the backed up load center, running a 9kW element.
1) is this an acceptable config? Do the 4x breakers and circuits for the 4 heating elements have to run off the same load center for any reason? Or can you split them 3 and 1?
2) will a tankless electric water heater function should only one of the circuits (40A, 9kW) be operational? Thinking the power goes out, so you lose grid power (and 3x40A, three of the four heating elements)? Will it just basically downgrade the WH to a single 40A/9kW heater...which should be able to handle ~2.0gpm with a decent temperature rise...which is enough to take a hot shower.
This would see like a reasonable compromise. Most of the time you'll have the full 160A / 36kW available, but without having to sacrifice a major amount of Amps for your backed up load center. But, you will still have a hot shower should you lose power.
Havent done any of the financial calcs to see if this is even worth it (natural gas is pretty cheap). But in an earthquake, you might lose case...with a limp along tankless electric + ESS + PV, you could manage indefinitely. Also, I believe electric tankless have a the least maintenance and highest efficiency.