Code is 6awg thhn with60 amp breaker or 6awg romex nm-b with 50amp beaker so either 48amp continuous or 40 amp continuous.cable is clearly marked nm-b
I just need what is code, not what will work.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Code is 6awg thhn with60 amp breaker or 6awg romex nm-b with 50amp beaker so either 48amp continuous or 40 amp continuous.cable is clearly marked nm-b
I just need what is code, not what will work.
Yep, the engineering plans approved, and county, say 6awg thhn 3.4 conduit with 60 amp breakerCode is 6awg thhn with60 amp breaker or 6awg romex nm-b with 50amp beaker so either 48amp continuous or 40 amp continuous.
4. VW ID.4 (48A)Off the top of my head, I can think of:
1. All Teslas except the M3 SR+
2. Rivian EVs
3. Lucid EVs
In the future? Who knows. Better to just future proof your setup so that upgrading is easy. I suspect that most larger vehicles (anything using more than 300-400 Wh/mi) will be getting a > 32A OBC.
- Tesla Model Y: 52,051
- Tesla Model 3: 47,682
- Tesla Model S: 9,250
- Ford Mustang Mach-E: 6,957
- Hyundai Ioniq 5: 6,265
- Kia EV6: 4,901
- Tesla Model X: 4,899
- Nissan Leaf: 4,401
- Kia Niro Electric: 3,549
- Volkswagen ID.4: 2,926
Not really an issue. I've been charging my S for >5 years on a J1772 plug. I got an extra adapter that lives on the J-plug permanently. I leave another in the car for charging at workFor cars that aren't Teslas though, you'd need to put an adapter on it, which is just as annoying as having to fiddle with a J1772 adapter on the end of a Chargepoint Home or Juicebox.
Romex/NM-B cable is limited to the 60deg C rating which, for #6 is 55A. There is no 55A breaker, so code allows you to "round up" to the next largest standard size breaker. But that doesn't allow you to max out the breaker rating; you are limited to the min of wire rating and breaker rating (so 55A load on a 60A breaker w/ #6 romex).Just hearing one should not run #6 romex on a 60 amp breaker was interesting. Pretty sure that is what they ran, and was speced, on my inverters.
Lots of 6-50's, too, eg ClipperCreek. Pretty sure anything they sell with a 14-50 can be ordered with a 6-50 and vice versa.I only see some 14-50 ev plug charges but I assume this is just because if was already wired?
I do the same I have a chargpoint flex a simple press on the trigger releases the adapter and the J1772 handle from the car as one unit. I even printed a wall hanger that accepts the Tesla adapter in the J1772 handle. Haven't removed the adapter since I got the car. I ordered a spare adapter that I leave in the car.Not really an issue. I've been charging my S for >5 years on a J1772 plug. I got an extra adapter that lives on the J-plug permanently. I leave another in the car for charging at work
Nice. I keep meaning to print something like that. I'll also add that it's easy to use the adapter. Press and hold the trunk button on the fob to open the door/unlock the port to install. To remove, I just push the J plug's button/latch until the port unlocks, release it to physically lock the adapter to the plug, and IMMEDIATELY yank out the plug and adapter as a unit before the charge port's lock reengages. Easy-peasyI do the same I have a chargpoint flex a simple press on the trigger releases the adapter and the J1772 handle from the car as one unit. I even printed a wall hanger that accepts the Tesla adapter in the J1772 handle.
View attachment 805406
Lets see with my nm-b #6Not really an issue. I've been charging my S for >5 years on a J1772 plug. I got an extra adapter that lives on the J-plug permanently. I leave another in the car for charging at work
Romex/NM-B cable is limited to the 60deg C rating which, for #6 is 55A. There is no 55A breaker, so code allows you to "round up" to the next largest standard size breaker. But that doesn't allow you to max out the breaker rating; you are limited to the min of wire rating and breaker rating (so 55A load on a 60A breaker w/ #6 romex).
For a 10kw inverter - 10000W/240V = 42A. Add 25% for continuous load: 42A*1.25 = 52.5A, well within the limit for #6 romex. Round up breaker to 60A, which is safe and allowed, since you will never go beyond 42A continuous (equiv to 52.5A intermittent)
Lots of 6-50's, too, eg ClipperCreek. Pretty sure anything they sell with a 14-50 can be ordered with a 6-50 and vice versa.
If you need the file I used it's here Tesla J1772 Adapter Charger Plug Holder by grant10kNice. I keep meaning to print something like that. I'll also add that it's easy to use the adapter. Press and hold the trunk button on the fob to open the door/unlock the port to install. To remove, I just push the J plug's button/latch until the port unlocks, release it to physically lock the adapter to the plug, and IMMEDIATELY yank out the plug and adapter as a unit before the charge port's lock reengages. Easy-peasy
I didn't see the inverter specs in your sig. Solaredge specs 47.5A max output on the 11400, so that's a bit funky w/ #6 romex. But I think solar follows the normal continuous loading rules, ie must be >= 3hrs to be "continuous". AFAIK, EV charging is the only load that MUST be classified as continuous, regardless of duration. So if your inverters don't go above 55A/1.25=44A for more than 3 hours, I believe you aren't subject to the continuous loading requirements.Lets see with my nm-b #6
I have a 11.4kw inverter, which I am seeing putting out 11.7kw continuous, so thats 11700/240 = 48.75 add 25%, 48.75*1.25= 60.9375, which seems to be above #6 romex? So if you have a 10 kw inverter, great, by at 11.4kw spec, but the app shows going to 11.7kw, seems a no?
Even if 11400/240 = 47.5X1.25=59.375, still above 55amp, right?
(NEC 705.60.B)I didn't see the inverter specs in your sig. Solaredge specs 47.5A max output on the 11400, so that's a bit funky w/ #6 romex. But I think solar follows the normal continuous loading rules, ie must be >= 3hrs to be "continuous". AFAIK, EV charging is the only load that MUST be classified as continuous, regardless of duration. So if your inverters don't go above 55A/1.25=44A for more than 3 hours, I believe you aren't subject to the continuous loading requirements.
EDIT - I guess this is just an intellectual exercise, since the installer has said they will fix it. Personally, I'd rather see it done to code than "good enough", especially if your inverters are running at peak output for >3hrs.
I have yet to get in writing they will fix.I didn't see the inverter specs in your sig. Solaredge specs 47.5A max output on the 11400, so that's a bit funky w/ #6 romex. But I think solar follows the normal continuous loading rules, ie must be >= 3hrs to be "continuous". AFAIK, EV charging is the only load that MUST be classified as continuous, regardless of duration. So if your inverters don't go above 55A/1.25=44A for more than 3 hours, I believe you aren't subject to the continuous loading requirements.
EDIT - I guess this is just an intellectual exercise, since the installer has said they will fix it. Personally, I'd rather see it done to code than "good enough", especially if your inverters are running at peak output for >3hrs.
Thanks, that is what you folks have all been saying! I will make sure my 5 EV charges are wired correctly.(NEC 705.60.B)
(B) Ampacity and Overcurrent Device Ratings. Inverter
system currents shall be considered to be continuous. The
circuit conductors and overcurrent devices shall be sized to
carry not less than 125 percent of the maximum currents as
calculated in 705.60(A). The rating or setting of overcurrent
devices shall be permitted in accordance with 240.4(B)
and (C).
Therefore I suspect the #6 Romex is undersized for the load of a SE11400
See my response above. All inverters are continuous loads by NEC definition.I have yet to get in writing they will fix.
But the county inspector told them it was wrong.
So far the experts here also said it does not meet code. No one has said it has to be 3 hours, even though I am seeing my inverter this time of the year lasting for a while.
What they installed is also NOT what their engineer designed and approved, or the county. So at this point, its not what might be okay, it is
what their engineer and county signed off on, IMO.
Looks like I might be having an electrician coming this weekend to wire my 5 EV stations. I said we need #6 90C thhn wiring in conduit. This is
what the tesla Gen 3 says is needed on a 60 amp breaker.
So wayne on others, is what they installed not to code, or is there another 3 hour spec somewhere?
I saw after I wrote what I did. THANKS!!!!!!See my response above. All inverters are continuous loads by NEC definition.
It's in @Vines's post above. Normally loads are only considered "continuous" if they last for >= 3 hrs. EV charging is an exception, NEC 625 says all EV charging, regardless of duration, must be considered continuous. NEC 705.60.B apparently places the same restriction on the inverter output circuit. I'll edit my post.So wayne on others, is what they installed not to code, or is there another 3 hour spec somewhere?
Installers are constrained by field conditions. Could be that they didn't notice, couldn't get the correct material, and didn't think it was an issue.Thanks, that is what you folks have all been saying! I will make sure my 5 EV charges are wired correctly.
Now, with the difficulty of my install, this why I assume the first folks use RM #4/3, expensive stuff! So I expect the second installer now
gets to put in 2 long lines of RM #4/3 since no way I believe they could get conduit fulling in. This means cutting lots of sheet rock back out also.
Why would the installer part of a company not install what there engineers speced?
THanks!!!
Yep, no idea why, and 99.999999% of folks would never had found, let alone cared enough to get it fixed. I just know it is going to cost them a lot of money to fix. I sure know the county does not want me to file with the contractors board. I had to do this once. They are 100% black and white, it is either to code or not. I got all of his bond money.Installers are constrained by field conditions. Could be that they didn't notice, couldn't get the correct material, and didn't think it was an issue.
I had an issue where we had run a #10 THWN-2 in EMT for a 35A breaker and a Solar Edge 6000 inverter (25A @240vac)
We had to pull the #10 THWN-2 out (though the wire is rated 35A and install #8 THWN-2 to ensure the circuit was compliant with the NEC. (240.4.D.7)
CSLB reports are pretty serious, so hopefully, the contractor works this out proactively.Yep, no idea why, and 99.999999% of folks would never had found, let alone cared enough to get it fixed. I just know it is going to cost them a lot of money to fix. I sure know the county does not want me to file with the contractors board. I had to do this once. They are 100% black and white, it is either to code or not. I got all of his bond money.
Well you paid them to do the work to code. They screwed up. They should take this as a lesson to make sure they do things right, and in the future, they won't have to do the work over.Yep, no idea why, and 99.999999% of folks would never had found, let alone cared enough to get it fixed. I just know it is going to cost them a lot of money to fix. I sure know the county does not want me to file with the contractors board. I had to do this once. They are 100% black and white, it is either to code or not. I got all of his bond money.