    Everyone is having 14-50's installed and prices seem to vary allot. My electrician asked me to provide the outlet so as to ensure a good price.

    Cheapest I have found so far is the Cooper

    Cooper Wiring 5754N - Buy Now | Westway Electric Supply
    $59.44 after tax and shipping.

    For a little more I can prime the hubbell
    https://www.amazon.com/Hubbell-Wiring-Systems-HBL9450A-Specification/dp/B00IPBMUKY/ref=sr_1_3?ie=UTF8&qid=1532722760&sr=8-3&keywords=cooper+5754n
    $79.98

    Is the Hubbell better than the Cooper?

    Also off topic, I asked the electrician about running 100feet 4awg instead 6awg, he said it would be an extra $150.
    Would this be a good idea in case I want to install the Tesla Wall Connector later?
     
  2. P85_DA

    P85_DA Supporting Member

    Joined:
    Apr 25, 2015
    Messages:
    2,547
    Location:
    Chula Vista, CA
    The stabdard Leviton 14-50 works fine ..have had one as backup over 4yrs no issue ..I would run #4 and buy materials myself ..as the price differential isn’t that much from the bulk roll than u are set for WC in future

    Btw what do those expensive 14-50 plugs get you ?
     
  3. Glamisduner

    Glamisduner Member

    Joined:
    Aug 2, 2017
    Messages:
    687
    Location:
    Escondido, CA
    More plug / unplug cycles and they supposedly stand up to high constant current better.

    I was just reading the WC would need #3 or maybe even #2 wires.

    I'm thinking I might just have him run an extra 6awg instead so a second 14-50 could be installed at a later time?
     
  4. P85_DA

    P85_DA Supporting Member

    Joined:
    Apr 25, 2015
    Messages:
    2,547
    Location:
    Chula Vista, CA
    The WC needs larger wires if you are going to use max 100a or 90a breaker ...not sure what car u are getting but normally 48a is good and #4 will be good ...if u plan on keeping the car I would build this as if u were getting the WC and the 14-50 being temporary ..my situation was easy as I did a back to back run of less than 3ft ..the 14-50 actually was used a lot recently when Tesla broke my gen 1 HPWC with software ...in terms of plug/unplug cycles the Leviton costs like $10 I have easily in four years done a hundred plus and plug is still fine ...I was just curious as the cost differential was so much from the stuff u get at Home Depot and was looking at pic and nothing jumped out in terms of build
     
  5. Glamisduner

    Glamisduner Member

    Joined:
    Aug 2, 2017
    Messages:
    687
    Location:
    Escondido, CA
    I honestly don't know, just going with tesla recommendation. I heard they are heavier though. Guess that answered my questions about Hubbell vs Cooper.. Sounds like the Cooper is already above and beyond.

    For the wires, I was trying to future proof for having 2 EV's someday. But it sounds like I should just worry about the one I have for now and get the 4awg. HPWC later would still allow 48 with 4awg which is good enough for the car I have now.
     
  6. P85_DA

    P85_DA Supporting Member

    Joined:
    Apr 25, 2015
    Messages:
    2,547
    Location:
    Chula Vista, CA
    For load sharing another EV with two WCs best is get the #3 ...problem in future is if u go this route(14-50) and ur electrician runs conduit ..u most likely will need to upsize conduit due to heat issues ..with WC u would run 2 #3s and maybe a 6 or 8 for ground ...with the 14-50 u need to run four wires ..3 6s and an 8 ground ...THHN/THWN is not too much if u buy from bulk roll at Home Depot
     
  7. Glamisduner

    Glamisduner Member

    Joined:
    Aug 2, 2017
    Messages:
    687
    Location:
    Escondido, CA
    He said he can do 1.25" pipe to the box in the garage which will allow for larger conduit in the future to be pulled. Then he will run #4 wire into a smaller conduit to my outlet.
    With #4 I can still upgrade to WC later to charge at 48 amps?

    This way I can easily fish wire (probably #6) through the larger 1.25" conduit later for a 14-50 outlet for another ev.
     
  8. P85_DA

    P85_DA Supporting Member

    Joined:
    Apr 25, 2015
    Messages:
    2,547
    Location:
    Chula Vista, CA

    Yes number #4 u can use a 60a breaker and get 48a on WC looks like u will have nice setup !
     
    • Informative x 1
  9. Glamisduner

    Glamisduner Member

    Joined:
    Aug 2, 2017
    Messages:
    687
    Location:
    Escondido, CA
    I hope so. I ordered the cooper, came out to $69 shipped with tax. Still beats amazon's $80 + tax and I don't need it in 2 days (no car yet)...
     
  10. tga

    tga Supporting Member

    Joined:
    Apr 8, 2014
    Messages:
    3,003
    Location:
    New Hampshire
    #10 tga, Jul 28, 2018
    Last edited: Jul 28, 2018
    If he's pulling THHN in conduit, you can use the 75 deg column and get a 60A circuit. 100ft will give you a voltage drop of <2% (<4V). #4 cu @ 75 deg is good for 85A (64A HPWC setting).

    You could also save money by not pulling a neutral and installing a 6-50, especially if you are planning to install a HPWC later. You'll probably save enough on installation to cover the cost of the 6-50 adapter.

    IMHO, it's stupid that Tesla standardized on the 14-50 and had all that wasted copper installed for 50A neutrals that will never be used...
     
    • Informative x 1
  11. kelly

    kelly Member

    Joined:
    Nov 22, 2015
    Messages:
    101
    Location:
    phoenix, Arizona
    I bought my Hubbell on ebay for $59.99. Don't know if the seller is still selling them. He had a bunch of new ones in boxes.
     
  12. P85_DA

    P85_DA Supporting Member

    Joined:
    Apr 25, 2015
    Messages:
    2,547
    Location:
    Chula Vista, CA

    Good point ...there was another thread that discussed this same issue ...for short runs going from 14-50 to WC not a big deal to pull out cable later ...but for a long run if u know you will do WC than run wiring that way ...the 6-50 fits this scenario perfectly
     
  13. eprosenx

    eprosenx Member

    Joined:
    May 30, 2018
    Messages:
    688
    Location:
    Beaverton, OR
    Yeah, I think Tesla includes the 14-50 by default since it is a lot more common in the wild than a 6-50. RV parks everywhere, plus a lot of folks have installed them at their houses to support their RV’s. Not to mention ovens of course...

    But yeah, neutrals are a waste of wire for EVSE applications.
     
    • Like x 1
  14. alpinebum1

    alpinebum1 Member

    Joined:
    Apr 22, 2017
    Messages:
    350
    Location:
    Maryland
    I am doing this right now. I have 6awg running to a junction box where it splits to a 14-50 and a Wall charger. If I ever need to add another wall charger, the wiring is already there (including conduit for the data link. They will then share/load balance the 50amp circuit.
     
    • Informative x 1
    • Like x 1
  15. eprosenx

    eprosenx Member

    Joined:
    May 30, 2018
    Messages:
    688
    Location:
    Beaverton, OR
    Hrm, I don’t know if this is code compliant.

    There are a bunch of code sections that don’t apply if you have a single 14-50 on a given circuit. If it has more than one receptacle on a circuit I know other rules apply. Not sure what happens if a Wall Connector and a receptacles are on a circuit. I would have to go research.

    Now from a practical standpoint, as long as only one in use at a time this would clearly be fine as long as it is a 50a breaker and the wall connnector is limited to 40a. Just I am not sure if it is code compliant.
     
  16. alpinebum1

    alpinebum1 Member

    Joined:
    Apr 22, 2017
    Messages:
    350
    Location:
    Maryland
    It’s wired exactly per instructions in the wall connector manual
    The electrician wired everything per the Tesla manual for a load sharing setup. If the inspector has a problem with having the 14-50 there for a future load-sharing Wall Charger, then I’ll pull it off, cap the wires, and put a blank face plate on the box. The key is to get all the wires pre-positioned before the drywall goes up.
     

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.


    SUPPORT TMC