This thread has me wondering.
In a grid outage, if my system is putting out let's say 10kw, and my house is drawing only 2kw, and the PW is charging at 5kw, will I have a problem because of the excess not being "absorbed" by the grid?
In essence that is the issue, and it is complicated by some things:
1. Battery temperature - They cant always charge at 5 kW
2. Battery SOC, they cant always take a 5 kW charge
3. Inverter compliance with partial curtailment - Do your inverters support this? Does your house work fine with the final frequency shift?
4. House load of 2 kW will naturally surge up and down
5. PV generation will vary with irradiance and weather, so can jump up and down quite a bit on a cloudy and sunny day. My PV array typically maxes at 6.8 kW but today we saw brief spikes up to 7.8 kW as the sun reflected off the clouds, with cool PV panels due to the rainy weather. This effect is smaller if your DC/AC ratio is significantly larger than 1.0, since the inverter will be clipping already.
In this backup scenario, the PW and TEG will start pushing the microgrid frequency towards 62-65 hz, depending on the settings and your current PV inverters. This either takes the PV totally offline, or reduces their output, based on partial curtailment.