Charger install 80' away from panel

bv2925

New Member
Jan 28, 2021
2
0
USA
I am trying to install a wall charger that is 80' away from the panel since the panel is located just on the oppsite side of the house. Planning on using 3/4 conduit and individual #6 THNN black & red along with #10 green for the ground on a 60amp breaker.
Considering the run of the cable will i be able to achieve the full capacity of the charger for a model or should i anticipate a drop due to the lengthy run.
Please advice.
 

Rocky_H

Well-Known Member
Feb 19, 2015
7,297
8,990
Boise, ID
Yes, that sounds like a good setup. #6 copper in conduit has good capacity for that. It's rated generally for 65A circuits at the 75 degree C rating.
I checked with a voltage drop calculator, and it shouldn't have much for 80 feet.
Voltage Drop Calculator | Southwire.com
It's showing only about 1.41% drop for running 48A on 6 gauge copper for 80 feet.
 
  • Helpful
Reactions: pilotSteve

bv2925

New Member
Jan 28, 2021
2
0
USA
Thanks Rocky, appreciate your response.
I am planning to use 3/4 flexible metal conduit from the panel to the exit of the garage wall from where it would be a 90 degree turn and from there on use rigid conduit which would have 2 90 degree bends and enters into the charger.
Any advice on what kind of fittings to use for the conversion, advice to use a 3/4 LB?
And another question is that i dont have a bender nor a threading tool to thread the metal conduit. are there any coupling other than threaded out there that can make my life easier with the job and at the same time pass inspection.

Thanks
 

Rocky_H

Well-Known Member
Feb 19, 2015
7,297
8,990
Boise, ID
Ah, sorry, you're getting into questions about actually doing, which is not my thing. I'm just about the knowing of numbers as an "internet electrician". ;) I am an electrical engineer, but it's for layout design of computer chips, so I don't have experience with the mechanical fittings of conduits and such.
 

iluvmacs

Member
Jan 27, 2014
519
899
Madison, WI
I only have slightly more input, based on experience of installing several units... coincidentally I am also an electrical engineer but I work on circuit board design... My first question is why you've chosen rigid conduit instead of EMT. EMT is way easier, but obviously certain situations call for RMC. RMC does, I believe, have to be threaded; it's kinda part of the point to make very solid coupling connections. For the transition point from flex, I usually use a junction box, as there are fittings from literally everything to fit KO's. An LB is probably fine, depending on the exact installation details.

One other note, you can use the conduit as the grounding means, if you don't want to buy and pull the long ground wire. You do, however, have to bond the ground into the HPWC, which is pretty easily done with a j-box mounted a few inches away from it and a #10 ground wire connected from the box to the HPWC ground terminal. It's admittedly not quite as clean, and I guess if you're doing a fully outdoor installation it wouldn't work well, but I figured I'd throw it out there if it's an option for you.
 
  • Helpful
Reactions: Rocky_H

Products we're discussing on TMC...

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.