You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
So I guess I didn't need the 60amp breaker?EVs are considered continuous loads, and are only allowed to take 80% of the circuit's rating.
AND
The onboard charging circuitry in the battery assembly can only convert 48 amps(on a long-range model) or 32 amps (on a short range model).
80% of 60 amps is 48 amps...you need the 60 amp breaker for sustained 48 amp charging.So I guess I didn't need the 60amp breaker?
Thank you80% of 60 amps is 48 amps...you need the 60 amp breaker for sustained 48 amp charging.
Thank you
36 mph on my 40 amp Clipper Creek. What a difference voltage makes.
Not stupid at all.Since we’re on the subject, I typically don’t run my garage charger at full 80% of rating, usually throttle it down to 32 (50A circuit). This is plenty fast enough for our driving. I Assumed this was better for the battery and less risk of catching my garage on fire. Am I being stupid?
It's crazy how much degradation varies.. After 9k miles I'm at 327 to 328 mile range when my original full range was 330 miles..View attachment 704957
Nope, if 32 amps meets yours needs there is ZERO reason to charge at a higher amperage. On the occasion when you need faster charging you can always bump it up. But at most you might save is an hour going up from 32 to 40, and from 40 to 48 amps. It’s really not that much of a gain when charging over night say. But bragging rights has its merits.Since we’re on the subject, I typically don’t run my garage charger at full 80% of rating, usually throttle it down to 32 (50A circuit). This is plenty fast enough for our driving. I Assumed this was better for the battery and less risk of catching my garage on fire. Am I being stupid?
Charging at 32A instead of 40A is not "way better" for the battery. Even the maximum Level 2 (240V) charging rate for the Model Y of 48A (11.5kW) is no more than 1/7th of C (14% of C) where C is the capacity of the battery in kWh/1hr. An 82kWh battery can be charged at a rate of 80kW or less per hour without stressing the battery. As to whether the lower charging amperage (32A versus 40A) is better for the house wiring it would depend on the age of the wire, the type of wire and the highest temperature experienced while charging.Since we’re on the subject, I typically don’t run my garage charger at full 80% of rating, usually throttle it down to 32 (50A circuit). This is plenty fast enough for our driving. I Assumed this was better for the battery and less risk of catching my garage on fire. Am I being stupid?
Hi folks; so I've joined "the club" and have my first Y-P sitting in my garage. It's on an [electrician installed] ClipperCreek HCS80 (80A rating so 64A/15.4kW max flow) and connected to the Y using a J1772 adapter. The dashboard shows it's getting 48A (which I believe is the maximum), so no surprise there...but why am I seeing 39mi/hr vs. advertised 44mi/hr? Both the CC website claim 44, and a friend of mine with his Tesla wall unit sees 44mi/hr at 48A. Obviously it's not a huge diff, but curious why the 10% less flow rate and is there some setting I need to adjust in the car? (there are none I'm aware of on the HCS80)
The size (gauge) of the wire establishes the nominal electrical load (55amps let’s say) allowed on that circuit.So I guess I didn't need the 60amp breaker?
Makes perfect sense, thanks!Your voltage (232V) on that circuit is lower than their voltage. I bet your Neighbor shows over 240V.
Could be how far your EVSE is from the breaker panel, or maybe other loads (dryer?) or maybe the grid were reducing your overall house voltage.
Different time of day also results in different house voltage.
Remember V(volts) x A(amps) = W(watts) (or mph charge rate) W/1000 is kW.
increase the V or the A and get more W.
decrease the V or the A get less W.
My MY takes the full 48 amps until it shows 100%, and for several minutes after that. If the heat pump isn't running, it'll show 43 to 45 MPH charge rate, with my voltage between 232 and 238.The speed at which you can charge the battery will slow as the battery state of charge increases. Expect the fastest charging from 10% (or less) to 40%, then from 40% to 70%, with much slower charging from 70% to 100%. You will see this when Supercharging too but it is more noticeable because when Supercharging the maximum power provided to the Tesla vehicle will be tapering and the charging speed is also slowing at the same time.