Not much I can add I’m afraid, other than trying the UMC at a neighbour or relative’s house to rule out a faulty UMC. You could also try reducing the charging current in the car, say down to 5A, and see if that affects anything.APologies for cross posting but this seems a more active charging thread..
I've got similar RCD problems with new (2 weeks old..) M3.
I'm waiting on Zappi installation, so I'm hoping this may not be a long term problem, but I'd like to know what's going on! Apologies if I'm not using the correct electrical terminology.
I've had a Nissan leaf which has charged via 10A 3 pin ESVE or a specific Rolec 3KW J1772 (Type1) - both in the garage - for the last 9 years with no problems.
It's a 10 year old house/charging via garage, which has it's own 'box' for circuits etc. The Rolec installation has some earthing next to driveway (although I can't remember details).
I've not had any problems charging M3 away from house on SC/CCS or 7Kw or 22Kw type 2 chargers.
I've been using Rolec with a type 1/Type 2 adaptor as the main way to charge at home. This seems to generally work ok. It's limted to the rolec 3Kw.
However, I've had the RCD trip overnight a few times (even when 80% has been reached, although it might have been topping up for sentry mode after this? - ). I don't know exactly what time the RCD tripped, but the car seems to have charged to 80% ok, from 1Am, so it seems a few hours after this.
As I was using a Type 1 to type 2 adaptor, so I wondered if this might be the problems.
However, today I tried UMC for the first time via the garage 3 pin (no extension etc), and it tripped RCD immediately. When I plugged it in, but with a schedule set for the future, it did not 'trip' the RCD
Most of the time it charges fine using the rolec J1772Type1/Type 2 adaptor at 3-4Kw, although it did trip the RCD once today, just after the UMC had.
When I look at the main board, one of the switches (breakers?) has also tripped (the one for 'upstairs sockets') when I turn RCD back on, but the garage one never 'trips'.
I've got so many variations here I'm a bit confuddled. The only constant common participants are the M3 and my house.
Update - If I turn off all the other house circuits it seems to charge ok on UMC so I must have one of the 'overall' house leak problems?
Any suggestions welcome!
Thanks
Ian
I've just turned the house circuits all back on, and nothing has tripped so far...car is charging, house is alive!
I've a feeling this could be one of those problems that is so elusive it slowly drives me mad!
It’s been charging every time at 32A for over a fortnight, then last night it decides to charge at 16A.
A couple of times it has charged at 16A on subsequent nights, but usually it does it one night, then the following night it’s back to 32A. All without me altering anythingJust curious : When this happens does it ever revert to 32AMP by itself (that session, or following night(s) ), or is it "stuck" at 16A until you manually put it back up again?
A couple of times it has charged at 16A on subsequent nights, but usually it does it one night, then the following night it’s back to 32A. All without me altering anything
That was my understanding too, a bit like it remembers the location for scheduled charging.This sounds like a weird one. My understanding is that if car fell back to 16A thinking there was a fault on the line for example, low voltage, it would remember if for that charger next time. But you then say, without altering anything, its back to 32A next time.
I've done another variation...If I use the Leaf ESVE 3 pin, and use the T1 T2 adaptor into the tesla..it also trips, so it must be something to do with the M3 being different in some way to the Leaf. I think the new install of 7KW Zappi plans an RCD in garage, so hopefully, I can avoid resetting the clocks and wifi every time I try and charge..APologies for cross posting but this seems a more active charging thread..
I've got similar RCD problems with new (2 weeks old..) M3.
I'm waiting on Zappi installation, so I'm hoping this may not be a long term problem, but I'd like to know what's going on! Apologies if I'm not using the correct electrical terminology.
I've had a Nissan leaf which has charged via 10A 3 pin ESVE or a specific Rolec 3KW J1772 (Type1) - both in the garage - for the last 9 years with no problems.
It's a 10 year old house/charging via garage, which has it's own 'box' for circuits etc. The Rolec installation has some earthing next to driveway (although I can't remember details).
I've not had any problems charging M3 away from house on SC/CCS or 7Kw or 22Kw type 2 chargers.
I've been using Rolec with a type 1/Type 2 adaptor as the main way to charge at home. This seems to generally work ok. It's limted to the rolec 3Kw.
However, I've had the RCD trip overnight a few times (even when 80% has been reached, although it might have been topping up for sentry mode after this? - ). I don't know exactly what time the RCD tripped, but the car seems to have charged to 80% ok, from 1Am, so it seems a few hours after this.
As I was using a Type 1 to type 2 adaptor, so I wondered if this might be the problems.
However, today I tried UMC for the first time via the garage 3 pin (no extension etc), and it tripped RCD immediately. When I plugged it in, but with a schedule set for the future, it did not 'trip' the RCD
Most of the time it charges fine using the rolec J1772Type1/Type 2 adaptor at 3-4Kw, although it did trip the RCD once today, just after the UMC had.
When I look at the main board, one of the switches (breakers?) has also tripped (the one for 'upstairs sockets') when I turn RCD back on, but the garage one never 'trips'.
I've got so many variations here I'm a bit confuddled. The only constant common participants are the M3 and my house.
Update - If I turn off all the other house circuits it seems to charge ok on UMC so I must have one of the 'overall' house leak problems?
Any suggestions welcome!
Thanks
Ian
"Wattson" is back with me after nearly 2.5 weeks - and all appears to be sorted....
Had Model 3 for 3 weeks now and love the car....however my charging issues continue to plague my overall experience of the Tesla.
I had Rolec unit installed at home.....all checked out fine upon install. However upon getting car home 1st day and trying to charge the charger would start/stop go up to 32A, then drop to 0, then back to 16A - stay there, then cut off after about 10 minutes. Tried for a few days and this continued.
Installers agreed to swap the unit out as they couldn't find any initial faults so thought it might be a faulty unit.
Just had my Rolec swapped out for a new one Rolec.
New unit (Rolec) - same issues happening.
Electrician is stumped as everything is fine, earth readings are very low and under tolerance etc.
So trying to narrow down the issues.
I have booked a provisional service appointment in Edinburgh but first appointment isn't till the 29th October....
- Charging on rapid CCS chargers 50kw DC (one Insta volt and one public chargeplace scotland) - Zero issues, full speed no interruptions - 2 separate places.
- Public chargeplace scotland Type 2 cables - 2 separate locations - they start a full speed but then I get a warning saying "charging speed reduced - contact Tesla ". It continues to charge uninterrupted but slower than standard speeds
- Home 3 pin 13A Telsa charger - charges for about 20/25 minutes at a time - then suddenly stops, I need to then restart via app, same thing - rinse and repeat. So I can't leave it overnight charging as it stops after 20 minutes or so.
- Rolec - both units (one tethered, one untethered) start charging up to 32A, then stop and drop to 0A, then go up to 16A or so, but again after 5/10 minutes stop charging
I have spoke via text to Servicing/Techinical team. However, they wanted response via text..... They asked for times/date for charging, which units I've tried and used, whether AC/DC etc, along with other details of how long it charges for, what happens etc.
Hard work trying to put that all into a text message and send it over. Email would be easier, speaking to someone would be a novel idea as well!!
Anyway - Sent all the details to them, and despite using 4 different public chargers, they are blaming a "power surge" at my home address for the issues.
Clearly that's not the case as I have issues with public charging on AC as well.....
They are suggesting I need to call an electrician out to review my home wiring - They are utterly ignoring the fact I have similar charging issues on public chargers!!!
All the text messages back and forward are ridiculous way of trying to solve the problems.
Anyone any ideas??
I'm off to try another public chargers and a friends Rolec at his home just now - if it's the same problems still then CLEARLY it's not my home that's the issue!!
I am having very similar issues with my Rolec tethered home charging unit.
when connected to a 32 amp supply it is not uncommon for the Tesla to show a 16amp supply and the + sign to increase is greyed out and does not function.
I have yet to work out a full proof method of getting to 32 amp input. It seems that pressing the boost button on the EV.charge app the amp went up to 32 and then I was able to stop the charge and re schedule for off peak charging and the setting remained.
Still waiting for any response from Tesla
I certainly have the same frustration with trying to talk or email Tesla about the issue.
Two things to reset the Rolec:I am having very similar issues with my Rolec tethered home charging unit.
when connected to a 32 amp supply it is not uncommon for the Tesla to show a 16amp supply and the + sign to increase is greyed out and does not function.
I have yet to work out a full proof method of getting to 32 amp input. It seems that pressing the boost button on the EV.charge app the amp went up to 32 and then I was able to stop the charge and re schedule for off peak charging and the setting remained.
Still waiting for any response from Tesla
I certainly have the same frustration with trying to talk or email Tesla about the issue.
Two things to reset the Rolec:
- Turn off the smartness of the Rolec and don’t give it your Tesla credentials
- Reboot the Rolec by briefly turning off the breaker inside the house
Test by setting a scheduled charge 2 minutes in the future, plug it in, lock the car, and wait.
You mentioned the boost button in the app, so I assume you have the “smart” aspect of the Rolec enabled?Thanks for idea however the Rolec never had my Tesla credentials and the problem existed when I connected to a Tesla home charger, so this suggestion will not solve the problem.
Yes I have the Boost button but I withdrew the Tesla credentials to simplify the task. The app still works without the credentials and therefore I can Boost which has forced the Tesla to see 32amp. Before the boost I was unable to force the amperage up on the TESLA display.You mentioned the boost button in the app, so I assume you have the “smart” aspect of the Rolec enabled?