Clarify Ontario Electrical Requirements for UMC / HPWC

Discussion in 'Canada' started by hingisfan, Jan 19, 2015.

  1. hingisfan

    hingisfan hingisfan_Mark_V

    Joined:
    Oct 19, 2013
    Messages:
    760
    Location:
    Kingston, Ontario
    Hi guys,
    I was just getting a quote done for my future outdoor nema 14-50, which will be enclosed outside my garage (see below).
    The electrician that is giving me the quote seemed to think that 8 gauge wire was fine (I was thinking 6), and that a shutoff with arms reach of the recepticle was required. (I was hoping to not have to do this)
    Is the electrician correct?
    My panel is about 100 feet away and inside the house.
    cMEkrHA.jpg
     
  2. andyro

    andyro Member

    Joined:
    Aug 19, 2011
    Messages:
    58
    Location:
    Toronto
    Electrician here (QC) put the 14-50 outlet inside a nice RV enclosure - hangs nicely (no cord kink). Made by company called Midwest Electric Products, Inc. (Rainproof box, lockable). 8 wire OK for stoves but I used 6 for both outlets. You might need better than 6 for 100' though, that's far - what does a chart say?
     
  3. hingisfan

    hingisfan hingisfan_Mark_V

    Joined:
    Oct 19, 2013
    Messages:
    760
    Location:
    Kingston, Ontario
    Link for that enclosure you used?
    I like the style in the picture above as I can leave the umc locked in the box and then just grab the wand to use. Works just like a dedicated EVSE and then I can disconnect and take on a trip if I need to.
     
  4. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,851
    Location:
    Ottawa, Canada
    The cutoff switch thing is due to a misinterpretation of the electrical code, IMHO, but if the inspectors says you gotta have it, then you gotta have it.

    Here's a picture of my ridiculous installation. A switch in series with a plug. Makes no sense whatsoever. But I did find it came in handy as a cord holder.

    IMG_2697.JPG
     
  5. miimura

    miimura Active Member

    Joined:
    Aug 21, 2013
    Messages:
    1,243
    Location:
    Los Altos, CA
    Many inspectors in USA initially misinterpreted the NEC to require disconnect for hard wired EVSE installations. The actual requirement in the NEC is to require disconnect if over 150 Volts above ground or over 60 Amps. A NEMA 14-50 on North American 240V split phase is only 120V above ground and only up to 50A, so it is not required in the States. In addition, any plug-in appliance (EVSE) that has an accessible plug should not need a disconnect since the plug IS the disconnect? A HPWC on a circuit greater than 60 Amps does need a disconnect though.
     
  6. Cosmacelf

    Cosmacelf Active Member

    Joined:
    Mar 6, 2013
    Messages:
    3,399
    Location:
    San Diego
    8 gauge wire for 50 amps can be fine if it has a high enough temperature rating. Don't quote me, but I seem to remember that 8 gauge THHN in conduit works, but typical 8 gauge romex does not.

    You shouldn't need a cutoff switch for a NEMA 14-50 outlet.
     
  7. wayner

    wayner Active Member

    Joined:
    Oct 29, 2014
    Messages:
    1,586
    Location:
    Toronto
    But do you need one for an HPWC? I had mine installed a month ago but my inspector is coming tomorrow and I hope I don't get dinged by this.
     
  8. kizagjo

    kizagjo Member

    Joined:
    Jan 16, 2014
    Messages:
    73
    Location:
    Toronto, Ontario
    Mine looks like this:
    IMG_20140226_181320.jpg

    I'm in Markham. Installed ~March 2014, and got my rebate.
     
  9. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,851
    Location:
    Ottawa, Canada
    I've had that argument with the inspector. Their line is, "no that's obviously an error in the way they wrote it, everything in the standard is phase to phase, not phase to ground."

    - - - Updated - - -

    LOL that's bad. I didn't show you my Roadster HPC installation. Considering that the Roadster HPC is about 5X larger than the Model S HPWC... the switch box is even bigger:

    charger.JPG
     
  10. Cosmacelf

    Cosmacelf Active Member

    Joined:
    Mar 6, 2013
    Messages:
    3,399
    Location:
    San Diego
    Well, first it all depends where in the world you are. But my understanding of the US NEC is that a dedicated hardwired HPWC does need a cutoff switch (similar to what an outside AC condenser needs). That's assuming the HPWC is hardwired (not via a plug). Also, some inspectors will allow the cutoff switch to be the breaker panel breaker if the panel is within visual distance of the HPWC. Good luck!
     
  11. wayner

    wayner Active Member

    Joined:
    Oct 29, 2014
    Messages:
    1,586
    Location:
    Toronto
    Um, I am in Ontario of course!

    Isn't this thread entitled "Clarify Ontario Electrical Requirements for UMC / HPWC". I am pretty sure that Ontario is referring to Canada's most populous province rather than the city in SoCal, especially since this is in the Canadian sub-forum and the OP live in Kingston, Ontario.
     
  12. RAM_Eh

    RAM_Eh Member

    Joined:
    Dec 10, 2013
    Messages:
    307
    Location:
    Toronto ON
    For the HPWC you need a disconnecting means.

    For a 14-50 outlet you do not, but if the inspector says you do he rules. A lot of the inspectors will play it safe.
     
  13. wayner

    wayner Active Member

    Joined:
    Oct 29, 2014
    Messages:
    1,586
    Location:
    Toronto
    I guess I need my electrician to come back - the inspector is coming tomorrow. Is a circuit breaker box sufficient? I could use one in my garage anyhow so this could kill two birds with one stone.
     
  14. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,851
    Location:
    Ottawa, Canada
    At 40A the code is pretty clear - you don't need the disconnecting means. The PLUG is the disconnecting means.

    Plugs aren't allowed above 40A, due to the risk of arc flash if you pull the plug at full power. So the disconnecting means within sight of the load is a good idea - and required in most jurisdictions.

    And yes, if the inspector says you need it, then you need it. The reason my inspector gave is hilarious. He said that if they forget to unplug the car before pulling the plug out of the wall, then they could get a big arc. I pointed out that if they weren't smart enough to unplug the car first, they weren't going to pull that switch either. Didn't convince him of course, but it is complete idiocy.

    The "Electric Vehicle Only" sign on my outlet - also required - makes no sense whatsoever. So I can't plug a welder into the outlet? Adding a safety switch makes that illegal? Don't get it.
     
  15. hingisfan

    hingisfan hingisfan_Mark_V

    Joined:
    Oct 19, 2013
    Messages:
    760
    Location:
    Kingston, Ontario
    For guys that are doing an outdoor Nema 14-50, are they putting in a GFI breaker? or just normal? Does GFI cause issues with the UMC?
     
  16. Cosmacelf

    Cosmacelf Active Member

    Joined:
    Mar 6, 2013
    Messages:
    3,399
    Location:
    San Diego
    I don't think anyone makes a 50A GFCI breaker. As it happens, the Tesla UMC has a built in GFCI anyways.
     
  17. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,851
    Location:
    Ottawa, Canada
    Personally I'd install the HPWC outdoors, and dial it back to 40A if that's what your circuit can hack.
     
  18. hingisfan

    hingisfan hingisfan_Mark_V

    Joined:
    Oct 19, 2013
    Messages:
    760
    Location:
    Kingston, Ontario
    I have one right now on my hot tub circuit!

    - - - Updated - - -

    If you didn't buy new though you could save $800+tax by using the UMC though. (no Ontario EVSE rebate on used)
     
  19. Doug_G

    Doug_G Lead Moderator

    Joined:
    Apr 2, 2010
    Messages:
    15,851
    Location:
    Ottawa, Canada
    Well sure, you can save some money by using what comes with the car. But it's nice to have the UMC in the car with you all the time, in case you ever need it. These days buying a second UMC is only slightly less than buying an HPWC.
     
  20. hingisfan

    hingisfan hingisfan_Mark_V

    Joined:
    Oct 19, 2013
    Messages:
    760
    Location:
    Kingston, Ontario
    Is anyone running the UMC with a 50 amp GCFI breaker? I saw some posts from way back saying that there could be issues in doing this, but nothing lately about it.
    Thanks
     