    Looks like I-25 south may be next, perhaps Castle Rock and then Trinidad or thereabouts.... Then Sterling on I-76 and Burlington on I-70 east in 2015. Something south of Denver asap would be great.
     

    Attached Files:

  2. emupilot

    emupilot Member

    Joined:
    May 23, 2013
    Messages:
    926
    Location:
    Northern California
    I-70 eastbound is on the 2014 map, but I don't think the dots on I-70 can be believed - it would be 234 miles from Silverthorne to Burlington.
     
  3. slipdrive

    slipdrive Member

    Joined:
    Aug 30, 2013
    Messages:
    196
    Location:
    Colorado
    Good point. Westbound is the constraint. Maybe Limon, CO at about 145 to the top of the Continental Divide, but probably at least 55Kwh in winter due to the climb. We can mingle with the 18 wheeler rigs out there in Limon....
     
  4. everman

    everman Member

    Joined:
    Aug 7, 2013
    Messages:
    291
    Location:
    Colorado Springs
    Here's hoping it's close to Colorado Springs! It will be exciting to have a Tesla gathering site so close!
     
  5. Sgt Barone

    Sgt Barone Member

    Joined:
    Sep 6, 2013
    Messages:
    767
    Location:
    Cleveland, OH
    4 mobile superchargers coming to Park Meadows Mall in south metro Denver. Should be operational within a week!

    Thanks to brdunton on the TM forums.
     
  6. Zaxxon

    Zaxxon Member

    Joined:
    Dec 11, 2012
    Messages:
    896
    Location:
    USA
    Hey! Look! I finally get to participate in the reconnaissance. Here's a shot of the Park Meadows Superchargers going in. They were working hard at 10 am on Saturday morning.

    uploadfromtaptalk1391880411150.jpg
     
  7. stevezzzz

    stevezzzz R;SigS;P85D;SigX

    Joined:
    Nov 13, 2009
    Messages:
    6,062
    Location:
    Colorado
    Excellent news! I hope Tesla's directions are good when they finally post this one, because it's not easy to find if you don't know where to look. I like the palletized arrangement of two pedestals and the associated Supercharger cabinet: neat and compact. But where's the transformer and distribution cabinet we've gotten used to looking for? Or does this design obviate them?

    I predict there will be a lot of local owners charging at this location in addition to the gallery's test drive cars, with transient charging at the bottom of the list. For now.
     
  8. Zaxxon

    Zaxxon Member

    Joined:
    Dec 11, 2012
    Messages:
    896
    Location:
    USA
    The folks in the gallery said the intent is for this one to mainly be used by the Gallery's cars. But four stalls is overkill if that's the case.
     
  9. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    If it is like the Bethesda install, they just pulled a 480-Volt, 3-phase+neutral connection from a panel on site through a large conduit. With conventional breakers, 200 Amp service is needed; with the more modern, electronic breakers used in the Supercharger sites, 175 Amp service is needed.

    Each pallet/stall-pair needs a connection of this size.
     
  10. bluetinc

    bluetinc Member

    Joined:
    May 11, 2009
    Messages:
    682
    Location:
    MD
    From talking to the store and looking at the wire they ran at Bethesda, it looks like they ran 240V (their words I'm guessing they really mean 208V). They ran 500 mcm Cu cable, and have the Supercharger turned down to 90kW and the fuses in the disconnect box looked like they were 500A fuses, not 200A. I wish I had my meter to really verify that when I was there...


    Peter

     
  11. AudubonB

    AudubonB Mild-mannered Moderator Lord Vetinari*

    Joined:
    Mar 24, 2013
    Messages:
    4,222
    Location:
    Denali Highway, Alaska
    So, do I undertand this correctly? SpCs like those at Park Meadows, and in Maryland somewhere, are being called "mobile"...but really, they're no more, or even less, mobile than those firmly planted homes at a "Mobile Home" Park. They're firmly tied to the local grid - not being supplied by juice from an associated generator, that is - and there's no expectation of their being transported at a moment's notice to some other location.
    Rather, the only distinction to these is that there is no u/g wiring or affixing the charging posts themselves to the ground.

    Am I missing something? Might local codes and some such restrictions come into play here?
     
  12. Cottonwood

    Cottonwood Roadster#433, Model S#S37

    Joined:
    Feb 27, 2009
    Messages:
    5,062
    Location:
    Colorado
    #12 Cottonwood, Feb 8, 2014
    Last edited: Feb 12, 2014
    Good to know. I had just assumed 480V for efficiency. 208V would work...

    As you can see from the label on a Supercharger, it can take in 160A at 480V, or 280A at 208V, both 3-phase. Here are some AC power calculations:
    1. 160A*480V*sqrt(3) = 133 KW
    2. 280A*208V*sqrt(3) = 101 kW
    With AC to DC, charger inefficiency, maybe 10% or so, that is completely consistent with 120 kW at 480Volts and 90kW at 208 Volts. Also, with conventional circuit breakers, the install would require 280A/0.8 or 350A breakers. Finally, 500 MCM Cu THWN-2 (what Tesla has specified in the past) is rated for up to 430 Amps, so everything is consistent.

    This is still a pretty heavy load on a panel somewhere; it makes putting an HPWC in your home look simple. :wink:

    Supercharger Plate.JPG

    - - - Updated - - -

    I think that your analogy is perfect. Normal Superchargers are like normal, detached homes, and mobile Superchargers are like mobile homes. Mobile homes may come in on wheels, but normally get (semi-)permanent connections to power, water, and sewer. Also, like mobile homes, mobile Superchargers are factory built, and the build-out/install is a lot quicker.
     
  13. slipdrive

    slipdrive Member

    Joined:
    Aug 30, 2013
    Messages:
    196
    Location:
    Colorado
    Friday afternoon TMC staff in the store told me they thought they would be live by Wednesday latest. They also said they would "not be on the Supercharger map". Probably due to the permanent demo parking which usually is 2-3 cars. It would be great if they left the HPWC up where they are, and the two spaces on either side . In the past they had told me the mall would not give them more Tesla space. That's a touchy subject with other stores, etc. I'm sure. Anyway, good surprise news.. I'll go by this week. I'm 15 minutes away.
     
  14. Zaxxon

    Zaxxon Member

    Joined:
    Dec 11, 2012
    Messages:
    896
    Location:
    USA
    No workers onsite when I went by this afternoon. Here are some more pics.

    e6ate4eq.jpg

    yvepu8yv.jpg

    duburase.jpg

    u7y4e9yg.jpg

    ybesyneq.jpg

    u2amama9.jpg
     
  15. slipdrive

    slipdrive Member

    Joined:
    Aug 30, 2013
    Messages:
    196
    Location:
    Colorado
    At noon today three contractors were pulling conduit through the overhead runs.
     
  16. Lloyd

    Lloyd Active Member

    Joined:
    Jan 12, 2011
    Messages:
    4,885
    Location:
    San Luis Obispo, CA
    The Leviton 2000 is interesting, that is a 200 amp power meter. Perhaps they had to account for power to lighting or ??? I have not seen that at any other supercharger.

    http://www.grainger.com/product/19C697?gclid=CL2EsMe4x7wCFUQRpAodBzYAYw&cm_mmc=PPC:GooglePLA-_-Electrical-_-Distribution-_-19C697&ci_src=17588969&ci_sku=19C697&ef_id=UvVD9AAABcPsqlGT:20140212203701:s

    Meter,Three Phase,120/208 Volt,200 Amp








    Meter, Three Phase, 120/208 Volt, 200 Amp

    LEVITON




    Price: $789.00 / each




    Qty:



    +Add to list



    Deliver one time only

    Auto-Reorder Every 1 2 3 4 5 6 Month(s)

    Product ships within 5 business days from supplier
    AddRepair & Replacement Coverage for $129.00 each.







    0 Stars

    Be the first to write a review | Ask & Answer

    Item # 19C697
    Mfr. Model # 2K208-2W
    UNSPSC # 41113708
    Catalog Page # 439
    Shipping Weight 8.0 lbs.

    Country of Origin United States Of AmericaCountry of Origin is subject to change.












    Technical Specs

    ItemEnergy Meter
    TypeThree Phase
    Voltage120/208
    Amps200
    Accuracy+/- 1%
    Size6 ft. X 6" X 4"
    Description/Special Features10 Year Warranty
    StandardsUL and CSA
     
  17. Zaxxon

    Zaxxon Member

    Joined:
    Dec 11, 2012
    Messages:
    896
    Location:
    USA
    There was one Leviton on each set of two Supercharger stalls.
     
  18. bluetinc

    bluetinc Member

    Joined:
    May 11, 2009
    Messages:
    682
    Location:
    MD
    Lloyd,

    It looks like the 2000 series has multiple CTs that will measure up to 1200A, so they should be able to measure the power the Superchargers use that way.
     
  19. slipdrive

    slipdrive Member

    Joined:
    Aug 30, 2013
    Messages:
    196
    Location:
    Colorado
    Yesterday it appeared all construction complete, but the pedestals were still covered in plastic. Probably waiting for inspection/testing most likely. Will be interesting to see how they manage the use and parking there.
    Looks great. Nice upgrade.
     
  20. BP_Tesl@

    BP_Tesl@ Member

    Joined:
    Dec 27, 2013
    Messages:
    20
    Location:
    Colorado Springs
    I'll keep an eye out for one in Colorado Springs, I figured Meadows would get one soon because of the dealer there. I've only seen a handful of owners here in the springs and it seems a bit off the beaten path to see one anytime soon though. :wink:
     