My powerwall is not discharging during peak time (cost saving mode, 20% reserved), so today I logged into the gateway installer mode and see if I can find anything wrong.
When I got to the metering page, I see Meter 1 CT1 and CT2 are both reading negative W, when I click on the Flip check box, a info screen pops up and say "A negative power reading may indicate the CT is installed backwards or on the wrong phase."
on the gateway installation manual pg 34, it says "– This Site meter may be used when the Grid connection is at the Supply terminals." Does this mean my gateway is wired wrong? (either the 2 incoming wires or the CT)
could that cause my powerwall to not discharge during peak hours because they are reading negative value?