My HPWC was installed yesterday in my garage with roughly 150 ft of #2 Aluminum 4 conductor cable from my 200 Amp breaker panel in my basement. I decided to use a Tesla recommended electrician and am very glad that I did. I have a 125 amp sub panel in my garage. Although a 100 amp sub panel was in the estimate I guess they were out of stock so I ended up with a 125 amp 12 slot sub panel with a double 60 amp breaker. A permit was applied for and I'm sure their excellent neat and professional work that they did will pass inspection.
As someone pointed out in another thread if those that do the work themselves with no permit, no licensed electrician, and if there is ever a fire the insurance company will most likely deny a claim?
I decided that I was unwilling to take any chances. My nephew will be stopping by next week with his 2021 MY so I can test out my wall charger to confirm the promised 48 amp charge rate prior to my Delivery DD.
Looks just like my install (I’m in central NJ). I’m guessing it’s the same installer - RF Electric. They were awesome to deal with and the install is very clean. No issues so far and definitely getting the full 48 amps.
 
I suggest you consider the Wall Connector instead, the 14-50 is not as cheap was you might think. A quality outlet will run you about $80, you need a GFIC breaker that adds $100+, and you need to order a 14-50 adpater for the mobile connector, another $45. Add in some sort of cable management system for say $30 and your total is $255. The Wall Connector is $550 + a $10 breaker, which makes the total just $300 more. What do you get for that extra $300

  1. The ability to charge at 48A (on a 60-amp circuit) instead of 32A
  2. You get to keep the mobile connector in the car so it is not forgotten when needed
  3. If you add a 2nd Wall Connector at a later date, power sharing is already built in
  4. Firmware updates to the connector, power sharing was recently added via a firmware update
And I would definatly replace the wire with copper!

If you stay with your plan to run 40-amps to a 14-50 outlet, be sure to lable the outlet as 40-amps
You made a good point with respect to teh advantages of a wall conector vs UMC, however, the cost of upsizing the wire from a gauge that can handle 40A to a gauge that can handle 60A is not insignificant,
If 32A is enough to cover your day to day use, using that $300 saved on the install to instead buy a second Mobile Connector might be worth while, and the money saved on the wire could go toward a set of adapters to go with that second UMC for every possible plug you might encounter on the road.
 
You made a good point with respect to teh advantages of a wall conector vs UMC, however, the cost of upsizing the wire from a gauge that can handle 40A to a gauge that can handle 60A is not insignificant,
If 32A is enough to cover your day to day use, using that $300 saved on the install to instead buy a second Mobile Connector might be worth while, and the money saved on the wire could go toward a set of adapters to go with that second UMC for every possible plug you might encounter on the road.
I suggest it is still better off with the WC then buying a 2nd UMC. The WC will deliver a 40A charge rate on a 50A circuit. Also, if you install a 14-50 outlet you need 6/3 wire, whereas the WC requires only 6/2 wire, so you can save on wiring as well.

But…from what I have seen the cost of 4/2 wire is about the same as 6/3, so going to 60-amps is not a significant increase in wire cost. Your mileage, will of course, vary. 😉 Definitely worth getting quotes.
 
Last edited:
  • Love
Reactions: Rocky_H
This is refreshing to see mostly correct answers on an electrical installation thread for once :).

You should be able to tell rather easily if you can use the existing wire to pull in copper instead. Give it a tug on one end and see how easily it moves. If it was actually installed to code, it won't. Romex requires staples near junction boxes/panels, plus strain reliefs when going in and out of boxes (that part can be overcome but it's sometimes a pain). So likely the answer is no, you will need to open the drywall.

If you leave the Aluminum wire, yes you need the anti-oxidizing goo. Also, you will need to occasionally (1-2x per year) go check and re-tighten all terminal screws. Aluminum softens over time. I have had to do this with an outlet used at a family member's house (it overheated once rather significantly, tipping me off to this).

Yes, you need a receptacle that is rated for Al wire if you keep that. If it isn't, you can make a copper jumper and splice it (recommend Polaris connectors if you want some something small, or an outboard 60A non-fused disconnect (like those used for A/C units) if you want something cheap). The same is true if you put in an HPWC -- Gen 3 units are rated for copper only.

Make sure you use a GFCI breaker if your locale uses NEC 2017 or newer (most do). Not needed for HPWC. 40A is a fine choice for UMC usage. Agree that 60A is not going to be a good choice on a 125A service unless you do a load calc.

Finally, get it permitted and inspected per your AHJ.
 
Kevin
My MY is on order with a EDD now May 31st to June 28th 2022.
My HPWC was installed yesterday in my garage with roughly 150 ft of #2 Aluminum 4 conductor cable from my 200 Amp breaker panel in my basement. I decided to use a Tesla recommended electrician and am very glad that I did. I have a 125 amp sub panel in my garage. Although a 100 amp sub panel was in the estimate I guess they were out of stock so I ended up with a 125 amp 12 slot sub panel with a double 60 amp breaker. A permit was applied for and I'm sure their excellent neat and professional work that they did will pass inspection.
As someone pointed out in another thread if those that do the work themselves with no permit, no licensed electrician, and if there is ever a fire the insurance company will most likely deny a claim?
I decided that I was unwilling to take any chances. My nephew will be stopping by next week with his 2021 MY so I can test out my wall charger to confirm the promised 48 amp charge rate prior to my Delivery DD.
I thought that I read in the Tesla Wall Connector installation instructions: "Copper Wire Terminations Only"❓
 
I thought that I read in the Tesla Wall Connector installation instructions: "Copper Wire Terminations Only"❓
My Gen 3 HPWC has copper wire terminations from the 100 Amp garage sub panel. The sub panel is fed with #2 aluminum four conductor cable from the 200 Amp basement panel that is roughly 150 feet away from my garage.
#2 aluminum cable is cheaper, lighter, easier to work with, perfectly acceptable to local electrical codes when properly terminated and torqued by qualified electricians.
 

Attachments

  • Tesla Garage Charger IMG_7806.JPG
    Tesla Garage Charger IMG_7806.JPG
    45.1 KB · Views: 133
  • Aluminum IMG_7824.JPG
    Aluminum IMG_7824.JPG
    23.1 KB · Views: 76
  • Like
Reactions: cmy4x4 and Rocky_H
The use of Aluminum wire is OK provided if is terminated with Copper Wire, which is what the Wall Connector manual says.

Note:
  • Aluminum has different coefficients of thermal expansion than copper – Termination systems need to take this difference into account. Thermal cycling of a termination can create voids leading to loose connections, which cause high-resistance terminations that get progressively worse over time.
Since the system in the wall connector is copper, the aluminum wire needs to be connected to copper wire by a compression fitting (or another acceptable means) with the copper wire then terminating the connection at the wall connector.

This was also mentioned in post #25 above by @iluvmacs
 
  • Like
  • Informative