Whatever you do, make sure you pull wire thick enough for 100A service through that conduit. You'd hate to have to redo anything related to this trench in the future!
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Alright, FINAL UPDATE!! WOOOO
A saga ends.:love:
No I did not, I offered it as "hey I'd like to do this what do you think" and the ele said it probably wasnt needed, and I took it at that. He ran one line for all the 120v stuff (lights and garage door) and one line for the NEMA. The conduit is massive, and could easily run more power through if needed in the future... Long run it probably would have been better to force the issue, but at this point I just wanted to charge my damn car :crying:
First, if you require 120V circuits and the 14-50 in the garage, you *require* a subpanel in the garage... only one branch circuit may be run to a detached building without a subpanel. So plan to install one.
Congratulations on all of your hard work! Looks great!
What is that box on the roof of your car?
No I did not, I offered it as "hey I'd like to do this what do you think" and the ele said it probably wasnt needed, and I took it at that. He ran one line for all the 120v stuff (lights and garage door) and one line for the NEMA. The conduit is massive, and could easily run more power through if needed in the future... Long run it probably would have been better to force the issue, but at this point I just wanted to charge my damn car :crying:
Unfortunately, it's an illegal install. 225.30: "A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E)." (A) through (E) list special conditions such as power requirements greater than 2000 amps, documented safe switching procedures, different secondary transformer voltages, etc.
You might be able to con an inspector into letting you use 225.30(D), where it is stated that "Additional feeders or branch circuits shall be permitted for different voltages, frequencies, or phases or for different uses, such as control of outside lighting from multiple locations." I tried it once and the AHJ didn't agree, because it wasn't a different secondary voltage. However, even if you do that, you probably still fall afoul of the disconnect requirement of 225.31/225.32, which requires a means of disconnect at the building. 225.31/225.32 require that your detached garage have an accessible disconnect as near to the point of entry into the building as possible.
The reason you'll likely want a subpanel is that if you require a disconnect anyway, you may as well just run a single feeder and put a subpanel in there. You could get away with a 60A disconnect for the NEMA 14-50 and a simple snap-switch (listed for disconnect), but at that point you may as well just look at a subpanel.
Your electrician never said anything about a disconnect or a subpanel requirement? This is kinda basic stuff.
Hm, very interesting. No he didn't, but of course I wasn't able to cite code to conversate the matter further. Indeed it might fall under the 225.30(D) definition as you have quoted it, but I guess it depends on the inspector. The 20a is on a separate breaker from the 40a, and both are strung through to the dwelling and then they split off to their final destinations. I will call him and ask if we're in violation of 225.30. My MAIN concern is insurance coverage on a catastrophe. When I buried the cable I laid red aluminum caution tape over the trenches about 2 inches into the fill. I feel that's all I can do from a precaution standpoint for any future owners, or myself if I randomly forget.
I'll post an update later.
I wonder if this would qualify as a sub-panel?Unfortunately, it's an illegal install. 225.30: "A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E)." (A) through (E) list special conditions such as power requirements greater than 2000 amps, documented safe switching procedures, different secondary transformer voltages, etc.
You might be able to con an inspector into letting you use 225.30(D), where it is stated that "Additional feeders or branch circuits shall be permitted for different voltages, frequencies, or phases or for different uses, such as control of outside lighting from multiple locations." I tried it once and the AHJ didn't agree, because it wasn't a different secondary voltage. However, even if you do that, you probably still fall afoul of the disconnect requirement of 225.31/225.32, which requires a means of disconnect at the building. 225.31/225.32 require that your detached garage have an accessible disconnect as near to the point of entry into the building as possible.
The reason you'll likely want a subpanel is that if you require a disconnect anyway, you may as well just run a single feeder and put a subpanel in there. You could get away with a 60A disconnect for the NEMA 14-50 and a simple snap-switch (listed for disconnect), but at that point you may as well just look at a subpanel.
Your electrician never said anything about a disconnect or a subpanel requirement? This is kinda basic stuff.
I wonder if this would qualify as a sub-panel?
GE 70 Amp 2-Space 2-Circuit 240 Volt Unmetered RV Outlet Box with 50 Amp and 20 Amp GCFI Circuit Protected Receptacles-GE1LU502SS - The Home Depot
Hm, very interesting. No he didn't, but of course I wasn't able to cite code to conversate the matter further. Indeed it might fall under the 225.30(D) definition as you have quoted it, but I guess it depends on the inspector. The 20a is on a separate breaker from the 40a, and both are strung through to the dwelling and then they split off to their final destinations. I will call him and ask if we're in violation of 225.30. My MAIN concern is insurance coverage on a catastrophe. When I buried the cable I laid red aluminum caution tape over the trenches about 2 inches into the fill. I feel that's all I can do from a precaution standpoint for any future owners, or myself if I randomly forget.
I'll post an update later.
I think it should be pretty obvious where the conduit is, given that is comes out of the ground on either end. If someone is so clueless as to dig without first considering where that conduit goes, it's on them.
-Mark
Totally agree, but life has taught me (thus far) that not everyone is as smart as we give them credit for ... anyway it was only like 5 bucks!
As long as it was properly permitted and inspected, you should be able to rest easy on that score. If the inspector passed it, it's on the city/county's head if it's wrong. Had it been my install, I would have wanted a 60 or 80a feeder and a subpanel. Leaves room for changing or adding circuits in the future. Also nice not to have to trudge back to the house to access the breaker.... My MAIN concern is insurance coverage on a catastrophe. ...
I understood all that. My point was that so long as a permit was gotten and the inspection was passed, your responsibility for code compliance is satisfied. Your insurance would have to pay.@davewill
Based on what has been identified by FlasherZ, i am probably not to code due to the double cable run in same conduit. There is some potential wiggle room for dissimilar voltage, mainly my 240v is very obviously not my 120v by size and usage. Even if they passed me there, I might be in trouble with no cutoff near the point of entry (this is probably an easy fix for me to do). I am exploring my options to "ensure my insure", including taking a walk to talk to my local city engineer, whom I have a history with (retention wall ingress ). This is lower on my list of priorities at the moment, but will get done.