solarAddict

Member
Jan 26, 2020
95
40
MA
Hi,

Mi installer informed me (informally though) that we might need to build an fire proof enclosure around PWs as a new requirement in MA for 2020. Anyone have any info on this? One PW would be OK without the fire box, but 2+ installation would need it.

Honestly I'm confused - for me the chance of overheating and all consequences is much higher for device installed in enclosure vs in open space...



Thanks
 

Vines

Active Member
Jul 20, 2018
1,783
2,062
Silicon Valley, CA
Likely until the Powerwall passes UL9540a fire testing we will continue to see these requirements pop up.

I wouldn't be surprised if this is a similar issue to the Santa Clara County Fire department issue. Basically, here they want to enforce the 2019 CFC 1206 (2018 ICC) if the storage quantity is over 20kWh.

In actuality, the intention is that 1206.2.1 section is intended that permits are required for battery installations above a certain size. Those battery installations requirements are per CRC R327 or CFC 1206 according to the occupancy category.
 

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.