Cross-posting this from my
other thread...
According to PG&E, molded case circuit breakers are not allowed for the disconnect between the Grid and the distributed energy generation system (which I think includes both solar and ESS). So for the grid disconnect, you need that big box like what
@adspguy posted.
https://www.pge.com/includes/docs/p...lity/electrictransmission/handbook/060559.pdf
#11: Molded case circuit breakers, pull-out type disconnects, or any other similar device are
not acceptable as an approved disconnect switch.
That means Sunrun did put the bladed AC disconnect in the right location; since they wanted the bladed disconnect to work with PG&E's requirement. But their disconnect wouldn't work for a fire-safety requirement since the house itself would still be energized and potentially unsafe for emergency workers in my home.
As
@Vines pointed out, if you use the same disconnect to keep both PG&E safe and firemen safe... then PG&E would disable your home backup solution if they ever had to work on services near your home. I guess the "safest possible answer" is to provide firemen access to shut off your PV and batteries that is a separate item than the big lever box that PG&E requires.
I'm trying to see if fire-safety requirements also deny the use of molded case breakers...
Seems like overkill to do this, but then the inspectors can't poo poo on anything.