Hi All.

Recently we had a power outage and the Powerwall took the load on backup. However the UPS’s in the house continued to complain re power quality even once the PW was delivering power to the house. This was new as previous outages left the UPS’s happy once he PW had taken the load.

On closer investigation the frequency from the grid is 50Hz. But when the PW takes the load on backup the frequency goes up to 55Hz. Which is outside the UPS spec.

I have read about the frequency shifting to control the solar however it would appear the 55Hz is out of the normal spec. I have heard the PW lifts the frequency to 53Hz max to throttle back / drop out the Solar.

Any observations or advice on how I can get some technical input? I have emailed the installer but wanted to get a forum perspective.

Thanks

Some context. I have a PW2 with Gateway 2 installed. I also have solar via a SolarEdge Inverter with Panels. Powerwall version is 1.47.0. Installation is in Johannesburg, South Africa. Grid frequency is 50Hz. 230 volts.

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.