My Gen 3 charger will be coming next week and I am going to get everything setup for it ahead of time.
I plan on doing this setup to charge at 48 amps.
60 amp breaker.
Running 4/2 and a ground in 1" EMT. I have read that #6 while it might be OK could get warm and possibly be an issue charging at 48 amps. Since I have a 50' run I am doing #4.
I will be using the bottom install so I guess I need to drill it out from 3/4 to 1" at a
1-3/8" to fit the 1" connector.
My main question is what size ground do I need??
I have seen #10 for a 60 amp.....but that is when you run #6. If I do #4 do I need to make the ground bigger?
Anyone see any issues with this plan or have any comments?