I just took delivery of my M3 LR AWD and I'm trying to figure out my home charging situation. I live in a recently built house which came with a 220V circuit wired in the garage but with no receptacle installed. So I figured I could use the Mobile Connector and buy the appropriate NEMA adapter and receptacle. Checking my panel, I realized the circuit is connected to a 35A breaker which I quickly realized is not very common, or at least doesn't easily fit into any of the adapter categories.

I'm at a bit of a loss of what to do, but I figured I would go the 30A route and get a NEMA 14-30 adapter and install the appropriate receptacle. I'm not an electrician by any means, but in my train of thought it seems safe since I'm using the adapter that the car knows to only draw 24A and I'm using a receptacle that is rated for 30A. I'm wondering if there is any other potential risks I'm not seeing...

Has anyone else run into this dilemma while trying to setup charging at home?
 
If everything (receptacle, wiring, breaker) is rated for at least 30A and you'll only be drawing a 24A continuous load, you should be good as long as it is wired up properly.

35A is odd. Wiring support more by chance? If it did and you had capacity, you could bump up the breaker and receptacle.

Of course, you should probably also consult an electrician to be sure.
 
  • Like
Reactions: MichaelP90DL
Hi, This is what I did, similar setup at home. My house has a 150 amp entry, I installed a 60 amp set of breakers in the panel and installed a NEMA 1450 female flush mounted receptacle. This gives me 32 amps to charge my new model 3P. But since I can regulate the charging amps from 1 to 32 amps, what is the optimal charge rate for battery health? I have unlimited time to charge the battery, so I don't need to charge at the full 32 amp rate. I'm trying to learn what it the best rate of charge to bring the battery to 100% charge without harming it.
 
  • Disagree
Reactions: Rocky_H
Hi, This is what I did, similar setup at home. My house has a 150 amp entry, I installed a 60 amp set of breakers in the panel and installed a NEMA 1450 female flush mounted receptacle. This gives me 32 amps to charge my new model 3P. But since I can regulate the charging amps from 1 to 32 amps, what is the optimal charge rate for battery health? I have unlimited time to charge the battery, so I don't need to charge at the full 32 amp rate. I'm trying to learn what it the best rate of charge to bring the battery to 100% charge without harming it.

Well, for battery health, you don't want the battery sitting at a high level of charge. The car will warn you if you charge at 90% or greater repeatedly. I set mine at 80% and only increase if needed on a trip.

Regarding the speed of charge, I don't know that I'd be concerned. A Model 3 charging at a V3 Supercharger would be dealing with more than 30X the power. There could be some argument on whether it is better to charge faster and finish sooner vs charging slower and letting the car be in a charging state for longer, but with the relatively small amount of energy in use, the difference is likely negligible. I will bump the amps down a bit on my EVSE if I'm charging to a high percentage and want the charging to finish closer to my departure time so that the battery is warm, but generally I feel that it's better to finish charging sooner so that auxillary systems (cooling, BMS, etc.) are running the least amount of time.
 
Hi, This is what I did, similar setup at home. My house has a 150 amp entry, I installed a 60 amp set of breakers in the panel and installed a NEMA 1450 female flush mounted receptacle. This gives me 32 amps to charge my new model 3P. But since I can regulate the charging amps from 1 to 32 amps, what is the optimal charge rate for battery health? I have unlimited time to charge the battery, so I don't need to charge at the full 32 amp rate. I'm trying to learn what it the best rate of charge to bring the battery to 100% charge without harming it.
You're really overthinking it. 32amps is fine at 240v. No need to worry at all.
 
Last edited:
Well, for battery health, you don't want the battery sitting at a high level of charge. The car will warn you if you charge at 90% or greater repeatedly. I set mine at 80% and only increase if needed on a trip.

The car does NOT warn you if you charge to 90% repeatedly. There's nothing wrong with charging to 90% regularly, and in fact people have posted service notes from Tesla recently recommending exacly that.
 
The car does NOT warn you if you charge to 90% repeatedly. There's nothing wrong with charging to 90% regularly, and in fact people have posted service notes from Tesla recently recommending exacly that.
This. I charge to 90% daily. There's literally no reason not to. Simple as that. This charging debate is kinda out of hand. Just drive it. Charge it to what you feel comfortable for. That's really all anyone needs to do.

Even if you charge to 100% occasionally is no biggie. Hell, so long as it doesn't sit for months and months at full charge you won't damage the battery.

Just drive it.
 
  • Like
Reactions: focher
The car does NOT warn you if you charge to 90% repeatedly. There's nothing wrong with charging to 90% regularly, and in fact people have posted service notes from Tesla recently recommending exacly that.

Uh, my car warned me specifically about charging to 90% after a couple times, so at least my LR Model 3 built in Sep 2018 did in fact display a warning not too long ago. Maybe it has changed, but there you have it. I believe what the car displayed on its screen more than someone on the internet, but do what you like.

I do agree that most charging discussions are overthinking it, especially L2 charging.
 
Last edited:
I just took delivery of my M3 LR AWD and I'm trying to figure out my home charging situation. I live in a recently built house which came with a 220V circuit wired in the garage but with no receptacle installed. So I figured I could use the Mobile Connector and buy the appropriate NEMA adapter and receptacle. Checking my panel, I realized the circuit is connected to a 35A breaker which I quickly realized is not very common, or at least doesn't easily fit into any of the adapter categories.

I'm at a bit of a loss of what to do, but I figured I would go the 30A route and get a NEMA 14-30 adapter and install the appropriate receptacle. I'm not an electrician by any means, but in my train of thought it seems safe since I'm using the adapter that the car knows to only draw 24A and I'm using a receptacle that is rated for 30A. I'm wondering if there is any other potential risks I'm not seeing...

Has anyone else run into this dilemma while trying to setup charging at home?
Definitely the easy/safe choice. Technically, per code, you could “round up” to a 50A outlet, but you would have to make sure you limit the car to 28A (80% of 35A). The extra 4A isn’t worth the hassle, so just go with a 30A setup. Though, you will need to change the breaker to 30A.
 
Last edited:
I just took delivery of my M3 LR AWD and I'm trying to figure out my home charging situation. I live in a recently built house which came with a 220V circuit wired in the garage but with no receptacle installed. So I figured I could use the Mobile Connector and buy the appropriate NEMA adapter and receptacle. Checking my panel, I realized the circuit is connected to a 35A breaker which I quickly realized is not very common, or at least doesn't easily fit into any of the adapter categories.

I'm at a bit of a loss of what to do, but I figured I would go the 30A route and get a NEMA 14-30 adapter and install the appropriate receptacle. I'm not an electrician by any means, but in my train of thought it seems safe since I'm using the adapter that the car knows to only draw 24A and I'm using a receptacle that is rated for 30A. I'm wondering if there is any other potential risks I'm not seeing...

Has anyone else run into this dilemma while trying to setup charging at home?

We need to figure out what kind of wire is installed to give proper advice. A 35a breaker is a bit odd. This makes me think it might have been for an AC unit and AC units can be breakered higher than the ampacity of the wire in some cases.

So we need to know what wire gauge it is, whether it is copper or aluminum (likely copper), how many conductors there are, whether it is NM cable (romex) or something else.

Most likely it is 10 awg copper Romex (or even #8), and hopefully it has two hots, a neutral, and a ground. If it is #10 as described, then I would do a NEMA 14-30, swap to a 30a breaker, get the 14-30 adapter and call it a day! If you are lucky enough to have #8 awg then you could do a 6-50 or 14-50 on a 40a breaker and charge at 8 amps. I would not install that in a new install since it is best to have a 50a circuit on those two receptacle types, but if you have the wire in the wall this is fully code legal and I would have no issues doing it (I might label this on the receptacle as a 40a circuit).

If you are unlucky and you have #10 awg copper and only two hots and a ground, then things get a little more difficult. There are solutions, but no obvious slam dunk.

Feel free to post pictures of the wire and breaker panel and stuff (inside too if you can safely remove it) and we can provide advice. Sometimes running a new line is easier in general.

Good luck!
 
Hi, This is what I did, similar setup at home. My house has a 150 amp entry, I installed a 60 amp set of breakers in the panel and installed a NEMA 1450 female flush mounted receptacle. This gives me 32 amps to charge my new model 3P. But since I can regulate the charging amps from 1 to 32 amps, what is the optimal charge rate for battery health? I have unlimited time to charge the battery, so I don't need to charge at the full 32 amp rate. I'm trying to learn what it the best rate of charge to bring the battery to 100% charge without harming it.

My neighbor drives his Model S to/from his office 2 miles away. I convinced him to crank it all the way down. He has it set to 5A with a wall charger. On another post, owner mentioned running his at 40A and seeing burn marks on NEMA 14-50 receptacle and smelling slow burn. Best advice is to set it to the lowest amp based on the range you need. The lower the better. On another post, owner is having problem of the charger connecting properly and the car limits charging to 16A instead of 32A. So 16A seems to be Tesla's recommended highest safe charging rate.
 
Uh, my car warned me specifically about charging to 90% after a couple times, so at least my LR Model 3 built in Sep 2018 did in fact display a warning not too long ago. Maybe it has changed, but there you have it. I believe what the car displayed on its screen more than someone on the internet, but do what you like.

I do agree that most charging discussions are overthinking it, especially L2 charging.
Tesla software, in any of their vehicles, has never issued any warning when charging to 90% repeatedly. I’ve done so approximately 1,000 times in the last 3 years.

You must have had your slider set higher than 90%.
 
  • Like
Reactions: Rocky_H and mrau
Tesla software, in any of their vehicles, has never issued any warning when charging to 90% repeatedly. I’ve done so approximately 1,000 times in the last 3 years.

You must have had your slider set higher than 90%.

It's possible since the slider wasn't very precise in previous app versions even though I was aiming at the 90% mark. Could have been 91% I suppose. But warning you at 91% and not 90% doesn't give me warm fuzzies and the car can sit without driving for days at times, so I err on lower is better for me.
 
My neighbor drives his Model S to/from his office 2 miles away. I convinced him to crank it all the way down. He has it set to 5A with a wall charger. On another post, owner mentioned running his at 40A and seeing burn marks on NEMA 14-50 receptacle and smelling slow burn. Best advice is to set it to the lowest amp based on the range you need. The lower the better. On another post, owner is having problem of the charger connecting properly and the car limits charging to 16A instead of 32A. So 16A seems to be Tesla's recommended highest safe charging rate.

Hrm, I disagree with this. Properly installed receptacles/circuits should be perfectly safe up to their rated capacity. The issues with melted receptacles are all with bad installs coupled with low quality receptacles. I charge my M3 L3 at the full 48 amps every single day with zero issues.

Turning your charge rate all the way down to five amps will run your cooling pumps and computers a lot more than is necessary. I could see some argument for turning down a bit perhaps to stress things less, but 5 amps is crazy.

The issue in the other thread surrounding 16 amps is purely around the marching mechanism failing to work. Without it latched it is an arc flash hazard if you unplug it under load. The car detects this and limited the charge current. With a working charge latch I would have zero issues running at full charge speeds.

Any level 2 charging is so much hilariously slower than a supercharger that it does not stress the battery at all. The only thing it could stress is the rectifiers and the site wiring for the EVSE.
 
Hrm, I disagree with this. Properly installed receptacles/circuits should be perfectly safe up to their rated capacity. The issues with melted receptacles are all with bad installs coupled with low quality receptacles. I charge my M3 L3 at the full 48 amps every single day with zero issues.

Turning your charge rate all the way down to five amps will run your cooling pumps and computers a lot more than is necessary. I could see some argument for turning down a bit perhaps to stress things less, but 5 amps is crazy.

The issue in the other thread surrounding 16 amps is purely around the marching mechanism failing to work. Without it latched it is an arc flash hazard if you unplug it under load. The car detects this and limited the charge current. With a working charge latch I would have zero issues running at full charge speeds.

Any level 2 charging is so much hilariously slower than a supercharger that it does not stress the battery at all. The only thing it could stress is the rectifiers and the site wiring for the EVSE.

If you believe there's any cooling needed when charging the EV battery at 5A or the rectifier running at 5/40 of its capacity reduces useful life, I guess then your argument would make sense. It's like saying zooming from stop light to stop light then slamming on the brakes is better for your car vs accelerating slowly and letting it regen to a stop. :)

Lower amp, longer draw, benefits both the electronics in the EV and the power company would appreciate it too.
 
If you believe there's any cooling needed when charging the EV battery at 5A or the rectifier running at 5/40 of its capacity reduces useful life, I guess then your argument would make sense. It's like saying zooming from stop light to stop light then slamming on the brakes is better for your car vs accelerating slowly and letting it regen to a stop. :)

Lower amp, longer draw, benefits both the electronics in the EV and the power company would appreciate it too.

I think it runs the cooling pump any time any charging is underway. So yeah, generally I agree that lower charge rates are good, but I think there are limits to it. The pump having to run longer is my main concern.
 