    I will be installing the Home wall connector soon in anticipation of my Model X WITHOUT the High Amperage Charging Upgrade. I know I'm only required to have a 60Amp Circuit Breaker but my question is other than possibly increased installation cost, Is there any reason I shouldn't opt for a 90Amp Circuit Breaker to future proof my installation in case I upgrade later?

    Maybe a dumb question I'm just not sure if the increased power will have an adverse effect when charging the car or if it will regulate it's self to what the car can handle. I'm fairly confident it won't be an issue but I'd rather ask then find out after I installed.


    THANKS.
     
  2. john pane

    john pane Member

    Joined:
    Apr 6, 2017
    Messages:
    54
    Location:
    PA, USA
    It's more than a matter of selecting a circuit breaker. Higher amperage will require heavier wire, and greater than 60A will require a disconnect within sight of the charger. Notwithstanding these differences and the associated costs, it is worth considering.
     
  3. Solarman004

    Solarman004 Member

    Joined:
    Apr 27, 2016
    Messages:
    392
    Location:
    Colorado
    Protecting the HPWC is the secondary function of the breaker. The primary function is preventing over-current and fire in the wire. You certainly can go with a 90 amp breaker (assuming compatibility with your breaker box and total house service), but per code, you need the appropriate gauge wire, for the run length, to the HPWC.
    For THWN copper wire, you need AWG 3 wire or larger in a 90 amp circuit. This can change for long runs. It's best to hire an electrician to make sure you are code compliant.
    You can find wire size requirements here.
     
  4. Zero CO2

    Zero CO2 a long term goal

    Joined:
    Apr 24, 2017
    Messages:
    161
    Location:
    NYC -Staten Island
    You are not required to have a 60 A breaker.... the HPWC can be set to many different breaker sizes 15A-100A there is a rotary switch that you set to the desired output current and breaker size ... so you need to figure out what your electrical feed/panel and household load can handle
     
    • Helpful x 1
  5. animorph

    animorph Member

    Joined:
    Apr 1, 2016
    Messages:
    514
    Location:
    Scottsdale, AZ
    We installed a 100A circuit and breaker. We expect to have the current Model X and a Model 3 in the future. One HPWC now and we'll install another before the 3 gets here. They can share the 100A circuit as needed. The X has the 72A charger, so it can charge a bit faster with the 100A circuit all by itself.

    You could also share a 60A or 90A circuit, so all you get is a bit more charge speed, if you can use it, for your extra amps.
     
    • Like x 1
  6. ThomascCTT

    ThomascCTT Member

    Joined:
    Apr 5, 2017
    Messages:
    5
    Location:
    Fort Lauderdale, FL
    Thanks for the responses. It sounds like I shouldn't have a problem installing the 90 or 100A circuit (assuming the house can handle it).
     
  7. sdorn

    sdorn Director of Awesome

    Joined:
    Oct 9, 2016
    Messages:
    906
    Location:
    Georgia
    Yes, it really depends on your house. If you have plenty of capacity and a breaker box in your garage, that is going to be the cheapest install. In my situation the breaker boxes were in the basement, and I was already over capacity on my 200 amp service, so I ended up spending just under $10,000 to have the service to my house upgraded to 400 amps and a 100 amp circuit run to my garage from the basement including the required local disconnect and installation of the Tesla HPWC.
     
  8. Zero CO2

    Zero CO2 a long term goal

    Joined:
    Apr 24, 2017
    Messages:
    161
    Location:
    NYC -Staten Island
    One other point on this topic.... i see in many of the posts on this site EV owners wanting to maximize the output current , it seems to me that you also needs to think about your typical driving pattern and how many EVs you think you will own over time before investing in upgrading your entire house electrical system(which can get quite expensive) ... in some cases there will be no choice but to upgrade....however....
    as an example if you commute/drive 70 ,miles per day it takes ~ 2 hours of charge time with a 48 amp output current... how often will you need to charge in 1 hour vs 2 hours overnight?.... I would speculate that for most people 1 hr vs 2 hrs of charge time while you are sleeping provides no real benefit for the potential increased cost in your homes electrical system.... just sayin...
     
    • Helpful x 1
  9. TallPaulS

    TallPaulS Member

    Joined:
    Feb 28, 2017
    Messages:
    45
    Location:
    Colorado Springs, CO
    There are so many variables to consider as most have pointed out. Keep in mind the 80% rule for load vs breaker. A 60A breaker will allow charging at 48 amps, a 90 will give you the max for model X (72) and 100 is for an S with dual charging (80).

    Wiring for 90/100 amp service can get atrociously expensive, not to mention that even with 200 amp service you may breach capacity when considering A/C and other potential concurrent draws. Most jurisdictions tend to follow NEC for wiring requirements but each jurisdiction may also have their own requirements above and beyond.

    Even if you have dual units for your home (the new generation) they can share a 60A just fine, and unless you're doing >200 miles on both electric vehicles every day an overnight charge can easily fill both.
     
    • Helpful x 2
    • Like x 1
  10. Teacherspet

    Teacherspet New Member

    Joined:
    Oct 9, 2017
    Messages:
    3
    Location:
    Punta Gorda Fl
    Do you use two 50amp breakers and number 6 wire
     
  11. Teacherspet

    Teacherspet New Member

    Joined:
    Oct 9, 2017
    Messages:
    3
    Location:
    Punta Gorda Fl
     
  12. Solarman004

    Solarman004 Member

    Joined:
    Apr 27, 2016
    Messages:
    392
    Location:
    Colorado
    This will work if the HPWC is set internally for 40 amps maximum output.
    You can refer to this chart: http://www.cerrowire.com/ampacity
    and see that 6 AWG copper THHN or THWN is an appropriate size for a 50 amp circuit.
    Note that you will not use 2 separate breakers, but rather a double 50 breaker where both poles are connected and turned on or off at the same time.
     
  13. Krazaak

    Krazaak Member

    Joined:
    Jul 30, 2017
    Messages:
    146
    Location:
    Charlotte, NC
    If you're wiring for 80A of charging, it requires a 100A double-pole breaker and #3 THWN wire in conduit. The only cars that use 80A though are older Model S with dual chargers.

    The most you need for refresh Model S or X with high amperage chargers is 90A on the breaker for 72A continuous, but that still requires #3 wire, so nothing really saved.

    If you have the regular charger on the S or X, it tops out at 48A and you need a 60A breaker and #6 THWN wire. That's more than enough for most people.
     
  14. Rocky_H

    Rocky_H Active Member

    Joined:
    Feb 19, 2015
    Messages:
    1,547
    Location:
    Boise, ID
    It's called a 2-pole circuit breaker, not two breakers.
     