How I upgraded from NEMA 5-15 to NEMA 6-20 for $66

This site may earn commission on affiliate links.
Figured I'd document this for anyone else's amusement. A relatively cheap and easy upgrade path (with a few caveats) is to use your existing wiring and simply switch out the breaker to a double pole so it get's both phases of 120v and convert the neutral (white) wire to a hot (black/red) wire.

There are three main caveats for this to work:
1) The outlet you're converting can be the only outlet on the circuit. Otherwise you risk anything 120v plugging in to go POOF and start a potential fire.
2) Your existing wiring is 12 gauge. Most new homes use 12 gauge and 20 amp breakers even though the outlets are only 15 amp.
3) You're breaker box can take the added 120v 16a load.

Luckily for me there was an existing outlet in my garage right by the charge port. Even more lucky was it was a dedicated circuit! I decided to give NEMA 6-20 a shot. I may still upgraded to 48a service as I have a HPWC that was gifted to me. Jury is still out.

Anyhoo on to the process:

Before shot: Great, my 60a sub-panel was already maxed out with breakers, no free slots. Drats:
11783679830188461386.jpg


However there was a way around that. I simply converted one of the full size breakers to a twin.

Here's the parts list I got from Home Depot. Left to right, plus a few glorious 18650s thrown in for good measure:
$9.68 20 Amp 2 Pole Circuit Breaker
$9.97 2-20 Amp Single Pole Tandem Circuit Breaker
$4.97 NEMA 6-20 Outlet
$0.98 NEMA 6-20 Outlet Cover
Not shown: $35 NEMA 6-20 Mobile Adapter

29456170375332468644.jpg


The finished product after ~30 minutes of fiddling around swapping breakers and reconnecting the conductors. I added black electrical tape to the neutral that is now getting an extra 120v going to my Tesla outlet. Finding that neutral on the bus bar was not fun, it took several tries trying to trace it in my rats nets of wires.
00009302118640120452.jpg


All done and ready for the Mobile Charger :D
63283374293622180082.jpg


I consume ~20% of my P3D+ battery daily and it takes ~3-4 hours to recharge back to 80% SoC on my NEMA 6-20. There really isn't much need to go for more amperage TBH for my needs. Only one time so far have I taken my car down to less than 10% and it was back up to 80% within 14 hours.

Hope this helps and cheers!

PS I am not a licensed electrician. Do not follow my advice yada yada yada.
 
Looks good. Any thoughts of a more industrial 6-20 outlet or do they not have as much concern with heat due to low amperage? Will you be doing a lot of plug / unplugging?
It is much less of an issue because of the lower amperage. Notice how thick the wires are that need to carry 40+ amps? It is difficult to make the right kind of clamping connection that can continue/imitate that thickness at a connection point. But you notice how thin 12 gauge wires are? It's not too hard to make a screw clamp approximate that same amount of connection point, so far less likely to have problems with it.
 
Figured I'd document this for anyone else's amusement. A relatively cheap and easy upgrade path (with a few caveats) is to use your existing wiring and simply switch out the breaker to a double pole so it get's both phases of 120v and convert the neutral (white) wire to a hot (black/red) wire.

There are three main caveats for this to work:
1) The outlet you're converting can be the only outlet on the circuit. Otherwise you risk anything 120v plugging in to go POOF and start a potential fire.
2) Your existing wiring is 12 gauge. Most new homes use 12 gauge and 20 amp breakers even though the outlets are only 15 amp.
3) You're breaker box can take the added 120v 16a load.

Luckily for me there was an existing outlet in my garage right by the charge port. Even more lucky was it was a dedicated circuit! I decided to give NEMA 6-20 a shot. I may still upgraded to 48a service as I have a HPWC that was gifted to me. Jury is still out.

Anyhoo on to the process:

Before shot: Great, my 60a sub-panel was already maxed out with breakers, no free slots. Drats:
11783679830188461386.jpg


However there was a way around that. I simply converted one of the full size breakers to a twin.

Here's the parts list I got from Home Depot. Left to right, plus a few glorious 18650s thrown in for good measure:
$9.68 20 Amp 2 Pole Circuit Breaker
$9.97 2-20 Amp Single Pole Tandem Circuit Breaker
$4.97 NEMA 6-20 Outlet
$0.98 NEMA 6-20 Outlet Cover
Not shown: $35 NEMA 6-20 Mobile Adapter

29456170375332468644.jpg


The finished product after ~30 minutes of fiddling around swapping breakers and reconnecting the conductors. I added black electrical tape to the neutral that is now getting an extra 120v going to my Tesla outlet. Finding that neutral on the bus bar was not fun, it took several tries trying to trace it in my rats nets of wires.
00009302118640120452.jpg


All done and ready for the Mobile Charger :D
63283374293622180082.jpg


I consume ~20% of my P3D+ battery daily and it takes ~3-4 hours to recharge back to 80% SoC on my NEMA 6-20. There really isn't much need to go for more amperage TBH for my needs. Only one time so far have I taken my car down to less than 10% and it was back up to 80% within 14 hours.

Hope this helps and cheers!

PS I am not a licensed electrician. Do not follow my advice yada yada yada.


Well done sir!! I'm surprised this isn't more popular. It's by FAR the most cost effective L2 option and 16A @ 240 is more than enough unless you're a full time Uber driver... especially as Superchargers become more plentiful so on the very rare occasion you need a quick boost you can just use that...
 
Figured I'd document this for anyone else's amusement. A relatively cheap and easy upgrade path (with a few caveats) is to use your existing wiring and simply switch out the breaker to a double pole so it get's both phases of 120v and convert the neutral (white) wire to a hot (black/red) wire.

There are three main caveats for this to work:
1) The outlet you're converting can be the only outlet on the circuit. Otherwise you risk anything 120v plugging in to go POOF and start a potential fire.
2) Your existing wiring is 12 gauge. Most new homes use 12 gauge and 20 amp breakers even though the outlets are only 15 amp.
3) You're breaker box can take the added 120v 16a load.

Luckily for me there was an existing outlet in my garage right by the charge port. Even more lucky was it was a dedicated circuit! I decided to give NEMA 6-20 a shot. I may still upgraded to 48a service as I have a HPWC that was gifted to me. Jury is still out.

Anyhoo on to the process:

Before shot: Great, my 60a sub-panel was already maxed out with breakers, no free slots. Drats:
11783679830188461386.jpg


However there was a way around that. I simply converted one of the full size breakers to a twin.

Here's the parts list I got from Home Depot. Left to right, plus a few glorious 18650s thrown in for good measure:
$9.68 20 Amp 2 Pole Circuit Breaker
$9.97 2-20 Amp Single Pole Tandem Circuit Breaker
$4.97 NEMA 6-20 Outlet
$0.98 NEMA 6-20 Outlet Cover
Not shown: $35 NEMA 6-20 Mobile Adapter

29456170375332468644.jpg


The finished product after ~30 minutes of fiddling around swapping breakers and reconnecting the conductors. I added black electrical tape to the neutral that is now getting an extra 120v going to my Tesla outlet. Finding that neutral on the bus bar was not fun, it took several tries trying to trace it in my rats nets of wires.
00009302118640120452.jpg


All done and ready for the Mobile Charger :D
63283374293622180082.jpg


I consume ~20% of my P3D+ battery daily and it takes ~3-4 hours to recharge back to 80% SoC on my NEMA 6-20. There really isn't much need to go for more amperage TBH for my needs. Only one time so far have I taken my car down to less than 10% and it was back up to 80% within 14 hours.

Hope this helps and cheers!

PS I am not a licensed electrician. Do not follow my advice yada yada yada.

Fantastic job and documentation!

A few notes for others that read this:

I presume that breaker slot was rated for tandem use (probably was). Usually will have a notched bus stab.

When moving circuits around to tandems, you must be careful to keep multi wire branch circuits (shared neutral) on opposite phase legs. Otherwise you can overload the shared neutral.

I should also note that most household circuits are 14 gauge, so only capable of a 15a circuit. Garage circuits are often (but not always) 12 gauge (for whatever reason NEC allows 15a receptacles on 20a circuits). Regardless, you can also play this trick on 15 amp circuits too. Just do a 6-15 receptacle instead of 6-20.

*very* nice job!

P.S. That panel is tiny! What gauge wire and circuit breaker feed it? You sure you are not pushing the load calcs on it? :)
 
  • Like
Reactions: Big Earl
If the OP is still out there: One tip on doing this is to wrap the repurposed neutral (white) wire with red tape, on both ends, to indicate its new role. Otherwise, job well done.
I added black electrical tape to the neutral that is now getting an extra 120v going to my Tesla outlet.
Wrong color.
No, it is not the "wrong" color.
Citation from NEC here:

200.7 Use of Insulation of a White or Gray Color or with Three Continuous White or Gray Stripes

(C) Circuits of 50 Volts or More.

The use of insulation that is white or gray or that has three continuous white or gray stripes for other than a grounded conductor for circuits of 50 volts or more shall be permitted only as in (1) and (2).

(1) If part of a cable assembly that has the insulation permanently reidentified to indicate its use as an ungrounded conductor by marking tape, painting, or other effective means at its termination and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, or green. If used for single-pole, 3-way or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white or gray stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.


The color requirement is only that it be a color "other than white, gray, or green". That may be any of the types of colors that are used on hot wires, which can be red or black or blue or orange or many others.
 
nice thread to pop up. My new Y has stolen my 30A EVSE from my old LEAF - so it may be time to upgrade a dedicated 120V 20a outlet I have. I even had it run with an extra conductor so I really should be able to swap out the 120v outlet for a 14-20. My portable EVSE can plug right in -- or I can plug in an adaptor instead and split it out to 120v... the only trick I've got left if figuring out the panel side of things.
 
Looks likely you used the wrong wire. You must use four conductor wire. Red black white and an insulated ground. So you’re using the ground as the white wire and there’s no dedicated ground. The ground wire is an insulated and usually thinner than the other ones. Not safe at all. all powerlines have Two layers of insulation. There’s the outer layer of insulation plus each wire individually has its own insulation for a good reason. Get the right wire as soon as possible