I have 200 amp service. The outside main service panel ( 200 amp ) is of the type : meter main MLO Distribution panel with no breaker in between the meter ( supply side ) and the panel itself. I has two breakers on the load side. One 100 amp breaker feeds the two outdoor AC condenser units and another 100 amp breaker feeds a sub-panel in the garage. The panel also has 10 kw solar back feed through a 50 amp OCPD. There is no way a new load can be added to the outside main panel due to its type as mentioned above and due to solar back feed , even though it has physical space. In fact, Tesla solar has put a red sticker in the panel saying "Caution: No new load to be added".
The sub panel has typical electrical loads of a 3375 sq ft home , like a 240V dryer and oven ( the only two 240V loads ) , kitchen circuits , microwave, dishwasher, cloth washer, indoor hvac air handlers ( gas heating ) and a whole house fan. There is no other major electrical load like electric range or water heater etc.
I am looking to add a circuit for Tesla Wall charger to this sub panel and need to do a load calculation to see if this panel can support one more 50-60 amp OCPD for a 40-48amp wall charger circuit. The panel itself is 200 amp capable although feed is 100 amp only from the main panel and has plenty of space for new breakers.
I tried following the guidelines of my city from here to calculate the load, but gotten throughly confused as to how to apply these to my situation. This link explains to add up the load for the entire house as served from the outside main panel and with this approach, I find enough capacity to add 60 amp OCPD to the system.
But the new circuit is being added to the sub panel which has only 100 amp supply. If I apply the above load calculation approach for just the sub panel loads ( i.e. not counting the AC load and treating the supply as 100 amp service ) , then sub panel appears to be already overloaded leaving no scope for adding wall charger circuit.
I have consulted two electricians who will be doing the install after pulling the permit and one says that sub panel may be over loaded without any calculation , while the other did a calculation to confirm that a 50 amp OCPD can be added. This 2nd electrician says that load calculation is done with the main service of 200 amp as total capacity as explained on city's web site in the link above and hence his recommendation.
I can go with the 2nd electrician , but concerned what if the inspection fails . Myself being an electrical engineer, my common sense says that the sub panel with 100 amp feed and its existing load only should be considered for load calculation despite main service being 200 amps. But I also see that the wall charger circuit and other major loads on the panel ( dryer and electric oven ) will never run together.
Requesting experts on the forum to help enlighten me on this issue .
The sub panel has typical electrical loads of a 3375 sq ft home , like a 240V dryer and oven ( the only two 240V loads ) , kitchen circuits , microwave, dishwasher, cloth washer, indoor hvac air handlers ( gas heating ) and a whole house fan. There is no other major electrical load like electric range or water heater etc.
I am looking to add a circuit for Tesla Wall charger to this sub panel and need to do a load calculation to see if this panel can support one more 50-60 amp OCPD for a 40-48amp wall charger circuit. The panel itself is 200 amp capable although feed is 100 amp only from the main panel and has plenty of space for new breakers.
I tried following the guidelines of my city from here to calculate the load, but gotten throughly confused as to how to apply these to my situation. This link explains to add up the load for the entire house as served from the outside main panel and with this approach, I find enough capacity to add 60 amp OCPD to the system.
But the new circuit is being added to the sub panel which has only 100 amp supply. If I apply the above load calculation approach for just the sub panel loads ( i.e. not counting the AC load and treating the supply as 100 amp service ) , then sub panel appears to be already overloaded leaving no scope for adding wall charger circuit.
I have consulted two electricians who will be doing the install after pulling the permit and one says that sub panel may be over loaded without any calculation , while the other did a calculation to confirm that a 50 amp OCPD can be added. This 2nd electrician says that load calculation is done with the main service of 200 amp as total capacity as explained on city's web site in the link above and hence his recommendation.
I can go with the 2nd electrician , but concerned what if the inspection fails . Myself being an electrical engineer, my common sense says that the sub panel with 100 amp feed and its existing load only should be considered for load calculation despite main service being 200 amps. But I also see that the wall charger circuit and other major loads on the panel ( dryer and electric oven ) will never run together.
Requesting experts on the forum to help enlighten me on this issue .