HPWC Burned Up (Yikes!)

Discussion in 'Model S: Battery & Charging' started by ThirdMartini, Jul 23, 2015.

  1. ThirdMartini

    ThirdMartini Member

    Joined:
    Jan 10, 2015
    Messages:
    30
    Location:
    Colorado
    My charge cycle was interrupted 2 days in a row. I unplugged it and replugged it in the AM and everything seemed fine. ( but called Tesla to have them check the car out ) Just came back from work and figured I'd crack open the HPWC (Yes I flipped the breaker off first) because I thought I smelled that ozone smell... and here is what I found :

    burnedup.jpg

    The heck would cause the wiring on the TESLA cable side to burn up like this? Kind of looks like something arked across the bridge there.

    Should note that the car seems fine, and I charge at 40A even though the HWPC is on 100A breaker. I did charge once at 60A a few weeks back.
     
  2. Father Bill

    Father Bill Member

    Joined:
    Apr 30, 2015
    Messages:
    171
    Location:
    Brighton, IL
    2 things...
    1. Do not charge until it is replaced
    2. Call Tesla and get the warranty replacement started.

    Good luck

    Father Bill
     
  3. AB4EJ

    AB4EJ Member

    Joined:
    Feb 25, 2015
    Messages:
    584
    Location:
    Tuscaloosa, AL
    The last time I had something like this happen (on other electronics, not on an HPWC) was when there was a lightning strike close to my house (to lamp post in front of house) - it caused an EMP enough to burn up some electronics in a similar way. Have you had some monster thunderstorms in your area right before this?
     
  4. ThirdMartini

    ThirdMartini Member

    Joined:
    Jan 10, 2015
    Messages:
    30
    Location:
    Colorado
    No lightning storms or anything like that near me all week. It must have gone out between Sunday and Wed. Car now charging on the wall plug (sloooooowwwlllyyy) and I've left the breaker off. I did call tesla this morning , and again once I saw this.. waiting for a callback still.
     
  5. wk057

    wk057 Senior Tinkerer

    Joined:
    Feb 23, 2014
    Messages:
    4,722
    Location:
    Hickory, NC, USA
    Looks like high resistance/bad connection on the crimped connector on the black wire causing excess heat, possibly even the screw holding it being loose. I strongly urge you not to use it anymore. From the looks of it the wire has heated enough to burn the insulation, which means it got really really hot and is no longer safe even if the crimp or connection is fixed. It's a fire hazard and should be locked and tagged out until a replacement is installed.
     
  6. Electric700

    Electric700 Member

    Joined:
    May 21, 2013
    Messages:
    986
    Location:
    Florida, United States
    What was your amperage setting? Others have reported high temperatures for their units, but they were able to mitigate the problem by reducing the amperage (e.g. to 70 A, instead of 79 A).
     
  7. AWDtsla

    AWDtsla Active Member

    Joined:
    Mar 3, 2013
    Messages:
    2,134
    Location:
    NE
    improper torque or bad contact on that cable. Stopped charging when the heat started burning up components on the board.
     
  8. ThirdMartini

    ThirdMartini Member

    Joined:
    Jan 10, 2015
    Messages:
    30
    Location:
    Colorado
    The charger is set to 80A, but I charge the car on 30-40A. (Usually 30A) Bought the HPWC so I could get a quick charge if I needed too. I've only once ran it anywhere close to 80A and that was the first week I got the car just to see how quick that charge goes. Tesla support called back, they are going to send someone out from the local service center to look at it. I'm not going to mess with it untill they come by and look/replace it.

    Visibly nothing looks like its loose in there or anything, (like i said not touching anything in there until the service rep pokes at it ) . It was installed by the electrician Tesla told me to use. The unit looked like it still had power when I came home as the green light on it was still on. Good thing my paranoia made me pop it open before plugging the car into it this evening.
     
  9. kennybobby

    kennybobby Member

    Joined:
    Sep 14, 2014
    Messages:
    479
    Location:
    Heart o' Dixie
    Yes it is a good thing that you inspected it, close call and good catch.

    i wonder what sort of current sensor that is--i've never seen one used like that with both wires thru the toroid as it would seem that the ac currents would cancel each other.
     
  10. Bearman

    Bearman Member

    Joined:
    Nov 17, 2011
    Messages:
    363
    Location:
    Sweden
    Maybe the toroid only sees a difference if one wire is carrying less current than the other like when there is a leak?
     
  11. Rocky_H

    Rocky_H Member

    Joined:
    Feb 19, 2015
    Messages:
    885
    Location:
    Boise, ID
    I can't help getting a bit of a chuckle when I see these threads about HPWCs overheating, burning, melting because so often I see all these people telling everyone to get the HPWC, even if it's still on a 50A breaker because it's so much better/safer than the UMC because it's hard-wired and so much more heavy duty, etc. etc. Eh, maybe not so much.
     
  12. cephellow

    cephellow New Member

    Joined:
    Mar 7, 2015
    Messages:
    2
    Location:
    santa cruz california
    My suggestion: As long as your getting your HPWC replaced, you may as well wire in a nema 14-30 or 14-50 outlet off of the same circuit/breaker box. I did this arrangement (about $50 in extra parts) so I could use either the HPWC or my UMC, (since 30A is fine in most cases for overnight charging), and you get a back-up if either HPWC or UMC fail.
     
  13. wk057

    wk057 Senior Tinkerer

    Joined:
    Feb 23, 2014
    Messages:
    4,722
    Location:
    Hickory, NC, USA
    It is for the ground fault protection circuit so it only really matters if there is an imbalance since either line to ground would imbalance one and set off the protection.

    If you ever look closely there is even a small lead wrapped around the coil that is used to test this circuit automatically.
     
  14. kuttakamina

    kuttakamina Member

    Joined:
    Aug 23, 2014
    Messages:
    711
    Location:
    DC
    Does this sort of stuff also happen with UMC? How do you prevent this? Set the amperage lower?
     
  15. m6bigdog

    m6bigdog Member

    Joined:
    Mar 29, 2015
    Messages:
    142
    Location:
    San Ramon, CA
    #15 m6bigdog, Jul 23, 2015
    Last edited: Jul 24, 2015
    So you anticipate there will be no electrical component failures? That is a dream!!
    This failure is of no consequence and occurred as anticipated with minimal risk to property and people.

    Now for the reality!!

    The greater safety of the HPWC comes from the fact that the failures (heat & sparks) are contained within the HPWC's UL rated electrical enclosure, designed to safely contain the electrical failure event.

    However, the UMC (a non-NRTL listed device) and the typical failure (heat & sparks) occurs at the adapter plug/wall receptacle which is outside a rated electrical enclosure and as with any typical cord connected equipment is more likely to cause a structure fire by igniting flammable materials cluttered near by.

    This is no joke and nothing to chuckle about as if it happens it will not be funny since a fire caused by unattended electrical equipment is often life threating.
    So I will use the HPWC with the confidence that it is a NRTL listed device which is designed to fail with minimal risk to the structure and people sleeping inside.
     
  16. flybyhawaiian

    flybyhawaiian New Member

    Joined:
    Jul 23, 2015
    Messages:
    3
    Location:
    Kapolei, HI
    Cephellow, could you post a picture of your setup. I just installed a HWPC on an 100amp and it tripped my house power twice at 80amps. With a meter in place and everything on I didn't not pass 85amps at any given time. Replaced a few breakers showing wear and tear and blue indications on the bolt heads. Shut off the breaker to the HWPC while at work tonight and will revisit in the morning.

    ~MJ
     
  17. wk057

    wk057 Senior Tinkerer

    Joined:
    Feb 23, 2014
    Messages:
    4,722
    Location:
    Hickory, NC, USA
    Sounds like you don't have sufficient capacity in your panel for charging at 80A.
     
  18. AmpedRealtor

    AmpedRealtor Active Member

    Joined:
    Jun 30, 2013
    Messages:
    4,701
    Location:
    Buckeye, AZ
    This is the first report that I've seen of any such HPWC issue, whereas I've read many more reports of UMC failures. In fact, didn't Tesla recall one of the UMC connectors a couple of years ago? The vast majority of HPWC installs are rock solid.
     
  19. FlasherZ

    FlasherZ Sig Model S + Sig Model X + Model 3 Resv

    Joined:
    Jun 21, 2012
    Messages:
    7,019
    Just as a quick note - you may not install a receptacle off the same circuit if the HPWC is configured at greater than 50A. But having a backup 14-50 receptacle for your UMC is a good idea as a back-up.

    - - - Updated - - -

    If your main breaker is tripping, it means either you're considerably exceeding the rating for your main breaker, or you have a defective main breaker. What is the breaker rated at?
     
  20. scaesare

    scaesare Active Member

    Joined:
    Mar 14, 2013
    Messages:
    3,937
    Location:
    NoVA
    Are there other threads about this? First one I've seen.

    Would you mind pointing them out?
     