Curious how one would put (pull) 300 ft of copper service thru conduit? I've considered cutting thinwall pvc in half and laying the cable in it, then covering with the other half, mostly for physical protection. Seems better than just laying it nude in clay/topsoil and almost easier than trying to imbed in pure sand. Thoughts appreciated.
--
Cutting the conduit in half pretty much removes any benefits the conduit produces, at least for direct-burial cable. The two halves can shift fairly easily, and then begin to break apart, creating shattered plastic around the cable that can potentially cut into the cable over time - ever see a PVC downspout extension after it's been run over by a vehicle? You don't want to manufacture that from the start.
Pulling cable through conduit isn't all that hard. First, note that it is an NEC requirement that a raceway be fully assembled before any cable is pulled through it - it's not legal to assemble the raceway as you pull cable (although I've seen plenty of people do it). You start with a spool of twine connected to a ping pong ball (or other plastic ball or big cotton ball -- anything that becomes more of an obstacle to glide in the suction) that's roughly the size of the conduit. Put it in one end and use a shop-vac on the other to suck it through. If the cable is small enough, you can use that twine to pull the cable through. For heavier cables, however, that twine is used to pull a heavier rope back through the conduit, which in turn will be used to pull the cable through. Cable grippers that are effectively Chinese finger cuffs with a hook on the end are used to pull the cable through.
EDIT: note that it is legal to feed the pull twine as you assemble the conduit as well, although I will note that I've seen cases where the twine gets wedged or glued into a joint and becomes completely ineffective. The ping pong ball with twine and a good vacuum works every time.
In the case of my upgraded service, the old cable was used to pull the new conductors through the Carflex conduit beneath my driveway. They unhooked my service, tied the new conductors to the old ones, and used the hydraulics on the bucket truck to pull the cable through.