Code here dictates a disconnect switch must be installed near the load if the load is greater than 50A and the breaker panel is out of sight or on another wall. You don't need a fused disconnect. The breaker will handle that function.
Do you have a code reference for this?
This is absolutely not what is written in 2017 NEC.
What is written is that it has to be able to be locked in the off position if greater than 60a amps and it has to be readily accessible.
The definition of “readily accessible” in NEC code says nothing about line of sight or any distance requirements, just it can’t require ladders or tools to get to. Now your local AHJ could interpret this differently.
Also, it is very possible that your local jurisdiction has added their own requirements to the code beyond what is in NEC (hence I am curious about a code reference).
I personally dislike this requirement for local disconnects for EVSE’s as I think they are ugly and expensive and not really needed or relevant. Local disconnects are important for things like HVAC units where you have technicians working on them often and need to turn on/off the power a lot. EVSE’s really have no serviceable parts in them and so it does not seem like much of a burden to find the breaker panel and lock off the breaker in question.
I also don’t get what makes my Wall Connevtor more dangerous once I exceed 60a. It is the same exact unit doing the same thing fed from the same source.
I guess with thicker wiring and a higher amperage breaker there might be slightly more fault current available.