Small correction, number 5 has nothing to do with it. Many 30a or 32a EVSEs are installed on 40a circuits with 14-50 or 6-50 outlets.This is done in residential homes usually only for the range in the kitchen. This specific instance (50A outlet on 40A breaker with 8 ga wire) is allowed because:
1. There is no such thing as a 40A outlet. Available NEMA outlets jump from 30A to 50A.
2. 8 ga wire is rated for 40A, and breaker is 40A, thus protecting the wire.
3. The appliance nameplate rating is 40A, so it will not attempt to draw more current than that.
4. The appliance is permanently installed, so it's highly unlikely someone would plug a different device into the 50A outlet.
5. The appliance is not classified as a "continuous load", so it's not subject to the 80% rating rule.
If any of those things are not true, then you cannot use the 50A outlet on a 40A breaker.