I have a similar situation as many other posters here. I read through many threads here but couldn't find a definite answer.

Can I install the Tesla HPWC on a 60amp breaker with #6 wire and use up to 48amp (max used by model 3) ? The distance from panel to the installation point is about 15ft. About 6-7 feet will be inside the ceiling/wall, the rest exposed in garage on the ceiling. The previous owner of my house is an electrician by profession and I consulted him. He proposed this idea.

As he has no prior experience with a Tesla connector or charging needs and I have read somany posts here somewhat contrary to this idea, I wanted to get clarification from folks here who have this experience.

So is this a good idea?

I would like to get a Tesla connector installed.

Thank you!
 
Depends on the wire ratings and installation methods. For instance, #6 is rated for a 60A circuit with THHN wire (wires in conduit), but not NM-B ("Romex").
Thanks! Why is a conduit stressed upon so much (am assuming it's nothing but a metal tube)? Is it to avoid the wire touching anything else around it? Or is there something more to it?
 
iluvmax is correct, in conduit, #6 and a 60 amp breaker would be fine. In Romex, its gotta be derated to the 60C rating, meaning a maximum of 55 amps. You might then contend that 55>48, so you are all good with 6-2 romex, but then the NEC would come back at you with "Its a continuous load, so you gotta increase the wiring and breaker to be able to handle 25% more than the real continuous load...aka 60 amps."

Additionally, since its gonna be used continuously(>3 hours at max load), the circuit breaker isn't supposed to be 60 amps... this flies in the face of the next-size-up rule, since there aren't 55 amp breakers out there.

I'm gonna be doing the panel connection of my HPWC using 6-2 romex this morning. I'm sure my 50 amp breaker will be fine for the 40 amp setting on the HPWC, and even though I'd love to get that little extra bit of speed, I really don't need it at all.

BTW, I had originally intended to use a 60 amp breaker, until reading about the continuous load rules. I'm sure it wouldn't burn down my house to run the thing with a 60 amp breaker and 48 amp setting, since the NEC is pretty conservative, and my entire run of romex is exposed in a basement(not buried in an insulated wall, for example). Even the 50 amp breaker would be able to reliably drive the HPWC at 48 amps because its in a basement panel where the temperature stays 65-70f.
 
  • Informative
Reactions: GSP and njsrikar
iluvmax is correct, in conduit, #6 and a 60 amp breaker would be fine. In Romex, its gotta be derated to the 60C rating, meaning a maximum of 55 amps. You might then contend that 55>48, so you are all good with 6-2 romex, but then the NEC would come back at you with "Its a continuous load, so you gotta increase the wiring and breaker to be able to handle 25% more than the real continuous load...aka 60 amps."

Additionally, since its gonna be used continuously(>3 hours at max load), the circuit breaker isn't supposed to be 60 amps... this flies in the face of the next-size-up rule, since there aren't 55 amp breakers out there.

I'm gonna be doing the panel connection of my HPWC using 6-2 romex this morning. I'm sure my 50 amp breaker will be fine for the 40 amp setting on the HPWC, and even though I'd love to get that little extra bit of speed, I really don't need it at all.

BTW, I had originally intended to use a 60 amp breaker, until reading about the continuous load rules. I'm sure it wouldn't burn down my house to run the thing with a 60 amp breaker and 48 amp setting, since the NEC is pretty conservative, and my entire run of romex is exposed in a basement(not buried in an insulated wall, for example). Even the 50 amp breaker would be able to reliably drive the HPWC at 48 amps because its in a basement panel where the temperature stays 65-70f.
Thanks for the input. Curious, why aren't you going with a #6 thhn so you can use the HPWC up to 48amps?
 
Lets be real however, given the actual amp draw never exceeds 48A, you will never cross the 60c temp rating of the NM-B 6/3. NM-B 6/3 is rated for up to 55amps, and that is continuous load not @ 80%. Everything with electrical code is over engineered, yes for good reason, but in an environment like this I would personally (and in fact do) use 6/3 NM-B on a 60a to pull 48a. The wire doesn't even get slightly warm it is room temperature after 4 hours of charging.
 
  • Like
Reactions: Kant.Ing
Thanks! Why is a conduit stressed upon so much (am assuming it's nothing but a metal tube)? Is it to avoid the wire touching anything else around it? Or is there something more to it?
Thanks for the input. Curious, why aren't you going with a #6 thhn so you can use the HPWC up to 48amps?

To be honest, I'm just not that familiar with running conduit. I also didn't realize until after the 6-2 romex was delivered that it wouldn't officially drive the full 48 due to the derating and continuous-load issues.

I also really don't need the extra 7 mph of charging. I charge at work, and could technically recharge every night at 120 until Winter and still be fully charged every morning. I could even get by with not ever charging at home, unless I drive more than 200 miles in a weekend.
 
  • Like
Reactions: GSP and njsrikar
Lets be real however, given the actual amp draw never exceeds 48A, you will never cross the 60c temp rating of the NM-B 6/3. NM-B 6/3 is rated for up to 55amps, and that is continuous load not @ 80%. Everything with electrical code is over engineered, yes for good reason, but in an environment like this I would personally (and in fact do) use 6/3 NM-B on a 60a to pull 48a. The wire doesn't even get slightly warm it is room temperature after 4 hours of charging.
Got it. Just curious why you didn't go with a thhn ? Does it cost more or is it a pain to work with?
 
So, my 3 is out there charging on my HPWC... and I must say I'm a bit disappointed. Before I started the charging, I was seeing 236-237 volts at the main lugs of the main panel, a little lower than I'd like, but well within parameters.

I started it at 40 amps, not wanting any surprises. It worked okay enough, but I found the car was reporting it was seeing only 225 volts, and only charging at 32mi/hr, after several minutes of 30/31. I traced the voltage back, and found it was only 228 volts at the main lugs now. At least my 60 feet of 6 gauge wasn't losing more than predicted.

I noticed my main panel was very gently sizzling at this point. More than a bit unsettling. I tightened the screws on the 60 amp breaker feeding the subpanel right next to it where the HPWC is connected(via a 50 amp breaker), which while not loose, were not as tight as the specs suggest. I found this stopped the sizzling, but wasn't real sure whether it was really the cause, or just my touching the breakers moved something a bit. I had intended to(and have the wire for) an upgrade of the subpanel feed breaker to 80 amps, but I might return those if I can't get any more power out of the mains.

I put the cover back on the main panel, and found the sizzling returned. It appears to be the main breaker making the noise... I've made a note to replace that ASAP.

I went out to the 3 and turned down the amperage using the touchscreen. At 35 amps, the voltage rises to 233, and I get a stable 30mi/hr of charge. I shudder to think what I really might see if I asked for 48(will do that tomorrow, or maybe after the main breaker has been replaced). I assume the 3 would stop asking for more amps way before it actually reaches 48, because the voltage will likely drop too much, not unlike when it only takes 9 of 12 amps when the 120V hits 105.

I did notice that the 6-2, while not at all warm to the touch, was detectably not as cold as when the power was off(this was checked after 10 minutes of 40Amps) I'll pull out the infrared measurer in a little while.

I'll probably give the electric company a call, I don't think that my home which is probably taking about 20 amps in addition to the HPWC is taking, should be drawing down the input voltage this much.
 
I have mine hooked up this way but dialed it down to 50 amps rather than 60 on the HPWC. Probably not necessary, but I can’t see myself ever needing that extra 7 miles/hour and now I know I’m code compliant. As others have said, I imagine the wire ratings are incredibly conservative and keeping it dialed to 60 amps wouldn’t be an issue if the extra power is important to you, but it’s not compliant either.
 
I have mine hooked up this way but dialed it down to 50 amps rather than 60 on the HPWC. Probably not necessary, but I can’t see myself ever needing that extra 7 miles/hour and now I know I’m code compliant. As others have said, I imagine the wire ratings are incredibly conservative and keeping it dialed to 60 amps wouldn’t be an issue if the extra power is important to you, but it’s not compliant either.

Yes, that's what I meant.... the 50A circuit breaker setting on the HPWC, for 40A expected draw.
 
So, my 3 is out there charging on my HPWC... and I must say I'm a bit disappointed. Before I started the charging, I was seeing 236-237 volts at the main lugs of the main panel, a little lower than I'd like, but well within parameters.

I started it at 40 amps, not wanting any surprises. It worked okay enough, but I found the car was reporting it was seeing only 225 volts, and only charging at 32mi/hr, after several minutes of 30/31. I traced the voltage back, and found it was only 228 volts at the main lugs now. At least my 60 feet of 6 gauge wasn't losing more than predicted.

I noticed my main panel was very gently sizzling at this point. More than a bit unsettling. I tightened the screws on the 60 amp breaker feeding the subpanel right next to it where the HPWC is connected(via a 50 amp breaker), which while not loose, were not as tight as the specs suggest. I found this stopped the sizzling, but wasn't real sure whether it was really the cause, or just my touching the breakers moved something a bit. I had intended to(and have the wire for) an upgrade of the subpanel feed breaker to 80 amps, but I might return those if I can't get any more power out of the mains.

I put the cover back on the main panel, and found the sizzling returned. It appears to be the main breaker making the noise... I've made a note to replace that ASAP.

I went out to the 3 and turned down the amperage using the touchscreen. At 35 amps, the voltage rises to 233, and I get a stable 30mi/hr of charge. I shudder to think what I really might see if I asked for 48(will do that tomorrow, or maybe after the main breaker has been replaced). I assume the 3 would stop asking for more amps way before it actually reaches 48, because the voltage will likely drop too much, not unlike when it only takes 9 of 12 amps when the 120V hits 105.

I did notice that the 6-2, while not at all warm to the touch, was detectably not as cold as when the power was off(this was checked after 10 minutes of 40Amps) I'll pull out the infrared measurer in a little while.

I'll probably give the electric company a call, I don't think that my home which is probably taking about 20 amps in addition to the HPWC is taking, should be drawing down the input voltage this much.
When I installed my HCWC I deliberately ran the car down a few days then began charging soon as I got home so I could check on it repeatedly over the course of hours. To think 10minutes is enough time to plateau wire temp is absurd.

Sizzling I would suspect is anti-oxidation grease getting hot at bad connections.
 
When I installed my HCWC I deliberately ran the car down a few days then began charging soon as I got home so I could check on it repeatedly over the course of hours. To think 10minutes is enough time to plateau wire temp is absurd.

Sizzling I would suspect is anti-oxidation grease getting hot at bad connections.

I totally agree, but my 3 didn't have a low enough SoC to run for hours and hours charging. I also haven't found my infrared temp checker yet, so giving an actual number or declaring it had reached a plateau would be impossible. I was just stating that it was a detectable rise in 10 minutes, not that it stopped rising.
 
Additionally, since its gonna be used continuously(>3 hours at max load), the circuit breaker isn't supposed to be 60 amps... this flies in the face of the next-size-up rule, since there aren't 55 amp breakers out there.

I am not entirely sure what is being referenced here. #6 AWG Copper NM cable must use the rating from the 60c column (even though it likely has insulation rated to 90c). It is good to 55 amps in this configuration. So you could put some load on that wire that was 55 amps non continuous, or 44 amps continuous. Somewhat sadly, the HPWC does not have a rotary dial setting for 44 amps, so your choices are 40 amps or 48 amps. Since 48 exceeds the ampacity of the wire, you have to set it at 40. While you technically could install that wire on a 60a breaker since that is the next size up, there is no reason to do that since you are going to be setting the HPWC to 40 amps and hence a 50a breaker is sufficient (I actually don't know if you are allowed to use the next size up rule if your load does not actually require it - the 50a breaker is the safer choice).

I'm gonna be doing the panel connection of my HPWC using 6-2 romex this morning. I'm sure my 50 amp breaker will be fine for the 40 amp setting on the HPWC, and even though I'd love to get that little extra bit of speed, I really don't need it at all.

BTW, I had originally intended to use a 60 amp breaker, until reading about the continuous load rules. I'm sure it wouldn't burn down my house to run the thing with a 60 amp breaker and 48 amp setting, since the NEC is pretty conservative, and my entire run of romex is exposed in a basement(not buried in an insulated wall, for example). Even the 50 amp breaker would be able to reliably drive the HPWC at 48 amps because its in a basement panel where the temperature stays 65-70f.

So two comments here: Yes, I suspect you are correct that a NM line of 6 AWG would probably be fine with 48 amps continuous on a 60a breaker if it was not installed in any insulation, hot areas, etc... My understanding is that the reason for the NM derating to 60c was because of small gauge circuits in ceilings running to lighting fixtures all surrounded by insulation. There is intended to be a lot of margin in the NEC calculations for good reason. I don't have laboratories with decades of experience in order for me to figure out where it is OK to push the limits and where it is not. I outsource that work to the NEC and just follow their guidelines. ;-)

The second comment about 48amps continuous on a 50a breaker: I am not so sure about that. So breakers are tested under "standard test conditions" which I believe are 104f but with the breaker installed in free air (i.e. in a panel but with no surrounding breakers). They are supposed to break at their rated amperage under those standard test conditions. By putting a breaker in a panel full of surrounding breakers that themselves heat up you could easily find yourself over 104f within the breaker. The breakers are also not that accurate, so you are likely to have nuisance trips.

Thanks for the input. Curious, why aren't you going with a #6 thhn so you can use the HPWC up to 48amps?

Running THHN requires conduit. The labor and cost to run conduit is quite high in many cases. Though I personally like the look of EMT conduit in a lot of settings.

Lets be real however, given the actual amp draw never exceeds 48A, you will never cross the 60c temp rating of the NM-B 6/3. NM-B 6/3 is rated for up to 55amps, and that is continuous load not @ 80%. Everything with electrical code is over engineered, yes for good reason, but in an environment like this I would personally (and in fact do) use 6/3 NM-B on a 60a to pull 48a. The wire doesn't even get slightly warm it is room temperature after 4 hours of charging.

Hrm, I am not sure how you can say you would never cross the temp rating of 60c on NM-B. 48a continuous violates the 60c rating on that cable. If the cable was installed in thermal insulation it might get really hot.

So the whole reason you have to upsize 25% for continuous loads is I believe because the wire gets warm/hot and conducts heat into the circuit breaker which causes the bimetallic strip to heat up more and cause a trip. No, the wire is not likely to melt, but it might cause nuisance trips or damage the connectors on either end.

Using 6/3 NM-B on a 60a to pull 48a is very unequivocally a code violation. If a house burns down that you wire (regardless of the actual cause of the fire), do you want to explain why you thought you knew more than the NEC?

So, my 3 is out there charging on my HPWC... and I must say I'm a bit disappointed. Before I started the charging, I was seeing 236-237 volts at the main lugs of the main panel, a little lower than I'd like, but well within parameters.

I started it at 40 amps, not wanting any surprises. It worked okay enough, but I found the car was reporting it was seeing only 225 volts, and only charging at 32mi/hr, after several minutes of 30/31. I traced the voltage back, and found it was only 228 volts at the main lugs now. At least my 60 feet of 6 gauge wasn't losing more than predicted.

I noticed my main panel was very gently sizzling at this point. More than a bit unsettling. I tightened the screws on the 60 amp breaker feeding the subpanel right next to it where the HPWC is connected(via a 50 amp breaker), which while not loose, were not as tight as the specs suggest. I found this stopped the sizzling, but wasn't real sure whether it was really the cause, or just my touching the breakers moved something a bit. I had intended to(and have the wire for) an upgrade of the subpanel feed breaker to 80 amps, but I might return those if I can't get any more power out of the mains.

I put the cover back on the main panel, and found the sizzling returned. It appears to be the main breaker making the noise... I've made a note to replace that ASAP.

I went out to the 3 and turned down the amperage using the touchscreen. At 35 amps, the voltage rises to 233, and I get a stable 30mi/hr of charge. I shudder to think what I really might see if I asked for 48(will do that tomorrow, or maybe after the main breaker has been replaced). I assume the 3 would stop asking for more amps way before it actually reaches 48, because the voltage will likely drop too much, not unlike when it only takes 9 of 12 amps when the 120V hits 105.

I did notice that the 6-2, while not at all warm to the touch, was detectably not as cold as when the power was off(this was checked after 10 minutes of 40Amps) I'll pull out the infrared measurer in a little while.

I'll probably give the electric company a call, I don't think that my home which is probably taking about 20 amps in addition to the HPWC is taking, should be drawing down the input voltage this much.

Sizzling of your main panel is NOT OK. I highly recommend you stop charging altogether right now and immediately isolate the issue. Sizzling (especially combined with unexpected voltage drop) could be arcing or an overheated terminal. What might be a simple bolt tightening could become a full panel replacement if you overheat things (not to mention we are in serious "burn your house down" danger mode). Note that while adding the EV charging might have finally triggered some failure mode, just stopping EV charging might not cause it to go away since the joint or connection that has an issue may be more weakened.

You need to isolate where the noise is coming from exactly - a flir camera (if you know anyone with one like an iPhone attached one) or an infrared thermometer may be the best way to figure this out. Once you find the location, the question is can a simple tightening fix it? Or will it require a breaker or bus or whatever to be replaced to fix it? If you get lucky, it is just the main breaker needing tightened to the bus. Maybe that could be done by just shutting off the main breaker, but you may also need to shut the main breaker, cut the seal on the meter base, pull the meter, then do your work, put the meter back, and re-energize. This would HAVE to be done with permission of the utility. I think they will let you cut the tag in some cases yourself (and come back and replace it later) if you get permission upfront (otherwise it is considered power theft).

I have mine hooked up this way but dialed it down to 50 amps rather than 60 on the HPWC. Probably not necessary, but I can’t see myself ever needing that extra 7 miles/hour and now I know I’m code compliant. As others have said, I imagine the wire ratings are incredibly conservative and keeping it dialed to 60 amps wouldn’t be an issue if the extra power is important to you, but it’s not compliant either.

50 amps (40a continuous) is the NEC approved way to make use of 6 AWG NM-B. I actually have not read the details on the next size up breaker rule to be sure, but I see no reason to use a 60a breaker on 6 AWG NM-B if you are hooking it to a HPWC since there is no 55a/44a setting that could make use of those extra five amps.

When I installed my HCWC I deliberately ran the car down a few days then began charging soon as I got home so I could check on it repeatedly over the course of hours. To think 10minutes is enough time to plateau wire temp is absurd.

Sizzling I would suspect is anti-oxidation grease getting hot at bad connections.

Yeah, sizzling is no bueno. That is a stop everything and figure out what is going on kind of an issue.
 
I am not entirely sure what is being referenced here. #6 AWG Copper NM cable must use the rating from the 60c column (even though it likely has insulation rated to 90c). It is good to 55 amps in this configuration. So you could put some load on that wire that was 55 amps non continuous, or 44 amps continuous. Somewhat sadly, the HPWC does not have a rotary dial setting for 44 amps, so your choices are 40 amps or 48 amps. Since 48 exceeds the ampacity of the wire, you have to set it at 40. While you technically could install that wire on a 60a breaker since that is the next size up, there is no reason to do that since you are going to be setting the HPWC to 40 amps and hence a 50a breaker is sufficient (I actually don't know if you are allowed to use the next size up rule if your load does not actually require it - the 50a breaker is the safer choice).



So two comments here: Yes, I suspect you are correct that a NM line of 6 AWG would probably be fine with 48 amps continuous on a 60a breaker if it was not installed in any insulation, hot areas, etc... My understanding is that the reason for the NM derating to 60c was because of small gauge circuits in ceilings running to lighting fixtures all surrounded by insulation. There is intended to be a lot of margin in the NEC calculations for good reason. I don't have laboratories with decades of experience in order for me to figure out where it is OK to push the limits and where it is not. I outsource that work to the NEC and just follow their guidelines. ;-)

The second comment about 48amps continuous on a 50a breaker: I am not so sure about that. So breakers are tested under "standard test conditions" which I believe are 104f but with the breaker installed in free air (i.e. in a panel but with no surrounding breakers). They are supposed to break at their rated amperage under those standard test conditions. By putting a breaker in a panel full of surrounding breakers that themselves heat up you could easily find yourself over 104f within the breaker. The breakers are also not that accurate, so you are likely to have nuisance trips.



Running THHN requires conduit. The labor and cost to run conduit is quite high in many cases. Though I personally like the look of EMT conduit in a lot of settings.



Hrm, I am not sure how you can say you would never cross the temp rating of 60c on NM-B. 48a continuous violates the 60c rating on that cable. If the cable was installed in thermal insulation it might get really hot.

So the whole reason you have to upsize 25% for continuous loads is I believe because the wire gets warm/hot and conducts heat into the circuit breaker which causes the bimetallic strip to heat up more and cause a trip. No, the wire is not likely to melt, but it might cause nuisance trips or damage the connectors on either end.

Using 6/3 NM-B on a 60a to pull 48a is very unequivocally a code violation. If a house burns down that you wire (regardless of the actual cause of the fire), do you want to explain why you thought you knew more than the NEC?



Sizzling of your main panel is NOT OK. I highly recommend you stop charging altogether right now and immediately isolate the issue. Sizzling (especially combined with unexpected voltage drop) could be arcing or an overheated terminal. What might be a simple bolt tightening could become a full panel replacement if you overheat things (not to mention we are in serious "burn your house down" danger mode). Note that while adding the EV charging might have finally triggered some failure mode, just stopping EV charging might not cause it to go away since the joint or connection that has an issue may be more weakened.

You need to isolate where the noise is coming from exactly - a flir camera (if you know anyone with one like an iPhone attached one) or an infrared thermometer may be the best way to figure this out. Once you find the location, the question is can a simple tightening fix it? Or will it require a breaker or bus or whatever to be replaced to fix it? If you get lucky, it is just the main breaker needing tightened to the bus. Maybe that could be done by just shutting off the main breaker, but you may also need to shut the main breaker, cut the seal on the meter base, pull the meter, then do your work, put the meter back, and re-energize. This would HAVE to be done with permission of the utility. I think they will let you cut the tag in some cases yourself (and come back and replace it later) if you get permission upfront (otherwise it is considered power theft).



50 amps (40a continuous) is the NEC approved way to make use of 6 AWG NM-B. I actually have not read the details on the next size up breaker rule to be sure, but I see no reason to use a 60a breaker on 6 AWG NM-B if you are hooking it to a HPWC since there is no 55a/44a setting that could make use of those extra five amps.



Yeah, sizzling is no bueno. That is a stop everything and figure out what is going on kind of an issue.

I totally agree with all your comments, including the bit about the 60 amp breaker being disallowed for a 40 amp continuous load. I still doubt it would be a danger in my case, but why should I chance it.

Regarding the sizzling, I think i'm interpreting the very faint buzzing of the magnetics of the breaker for very faint sizzling. I'm likely to still replace(or have replaced) the main breaker. Its getting pretty old, and I don't want a nuisance trip of my main breaker! I've turned the HPWC(or actually the 3) to only charge at 10 amps for now, which is more than I'll need until I get the main changed.
 
I totally agree with all your comments, including the bit about the 60 amp breaker being disallowed for a 40 amp continuous load. I still doubt it would be a danger in my case, but why should I chance it.

Regarding the sizzling, I think i'm interpreting the very faint buzzing of the magnetics of the breaker for very faint sizzling. I'm likely to still replace(or have replaced) the main breaker. Its getting pretty old, and I don't want a nuisance trip of my main breaker! I've turned the HPWC(or actually the 3) to only charge at 10 amps for now, which is more than I'll need until I get the main changed.

Correction, I turned the 3 to charge at 20 amps. For unknown reasons, at 10amps, the mi/hr plummeted far more than I'd expect.

On the plus side, It looks like my mains voltage has increased a good bit during the day, at 20amps charging rate, its seeing 241V in the 3.
 
I totally agree with all your comments, including the bit about the 60 amp breaker being disallowed for a 40 amp continuous load. I still doubt it would be a danger in my case, but why should I chance it.

Regarding the sizzling, I think i'm interpreting the very faint buzzing of the magnetics of the breaker for very faint sizzling. I'm likely to still replace(or have replaced) the main breaker. Its getting pretty old, and I don't want a nuisance trip of my main breaker! I've turned the HPWC(or actually the 3) to only charge at 10 amps for now, which is more than I'll need until I get the main changed.

I agree that the 60 amp breaker on the 6 awg NM-B but with a HPWC with its max set to 50a (40a actual continuous draw) would likely not be dangerous (since the next breaker up rule would allow for that size breaker if you had a 51a load - I don't know if it is allowed to use the next size up rule if you don't *need* it). The HPWC should *never* draw more than 40a in that configuration, so unless something malfunctions, you will never trip that breaker due to actual loading. You could have a short and in that case, it is an alternate trip path in the breaker that causes it to break. Most likely a 50a or a 60a breaker would have pretty similar short circuit trip characteristics.

So buzzing is not as bad a sizzling, though still not great. I can not say I have ever really heard residential breaker panels buzz. Buzzing is pretty common in transformers (60 cycle), though it is also not great since in transformers the moving of the wire coils will eventually wear down the insulation and cause a short. We just replaced one at my office due to excessive buzzing.

I have a friend with a couple Tesla's that had his main 200a breaker go bad. Probably due to all the heavy loads and cycling of the Tesla's (and all sorts of other crazy stuff in his house).

Turning way down your car while you work on getting the panel resolved is a great idea. I might also even consider trying to do the bulk of my charging during waking hours (even if that meant speeding it up) so that if something did go wrong I was awake to deal with it (do your smoke alarms work?). ;-)

I forgot to mention earlier:

It is normal for grid voltage to fluctuate during the day - say + or - 5% or so perhaps. At the output side of your substation transformer is generally an "online tap changer" unit which is constantly monitoring voltage and boost/dropping it by a couple volt increments throughout the day. The transmission grid fluctuates quite a bit along with the distribution to your house and so it tries to compensate for that as much as possible (not as much can be done about the distribution to your house sagging). If your utility transformer by your house has issues or is undersized you can also see big drops there when loads on the connected houses are high.

Additionally, I forgot to mention that the hottest part of wire in a circuit is generally at the connectors. So while undersized wire may not melt in the wall, it is likely to get hot at the terminal ends and melt the insulation there or damage the thing it is attached to (breaker or receptacle).

I would be curious to see pictures of your main panel with the "schedule" of breakers, the detailed sticker on the door about what kind of breakers and such can be used, and with the cover removed (if that can be safely done). Basically I am wondering if you can still get a new main breaker for that panel, or if you are entering "new panel" territory? A lot of older panels are not really up to snuff even if you can get parts.
 
I have a similar situation as many other posters here. I read through many threads here but couldn't find a definite answer.

Can I install the Tesla HPWC on a 60amp breaker with #6 wire and use up to 48amp (max used by model 3) ? The distance from panel to the installation point is about 15ft. About 6-7 feet will be inside the ceiling/wall, the rest exposed in garage on the ceiling. The previous owner of my house is an electrician by profession and I consulted him. He proposed this idea.

As he has no prior experience with a Tesla connector or charging needs and I have read somany posts here somewhat contrary to this idea, I wanted to get clarification from folks here who have this experience.

So is this a good idea?

I would like to get a Tesla connector installed.

Thank you!
Just use 4awg then you don't have to worry. Bonus points if you use 4awg THHN, but sure 6awg THHN in conduit should be ok. Difference in price is negligible though, might as well run 4awg. 6awg Romex however you will need to set the limit to 40 amps. At 40 amps you may was well install a 14-50 and get the newer HPWC so it can be removed more easily.

I'm currently using 4awg THHN with a 60 amp breaker, HPWC set to 48 amps continuous. I can change the breaker to something higher in the future (90 amp) (NEC seems to rate this wire at 95 amps, but from other charts I found 80 is recommended breaker) if I get another car that can charge over 48 amps, I'll swap out the breaker.
 
Last edited:
Just use 4awg then you don't have to worry. Bonus points if you use 4awg THHN, but sure 6awg THHN in conduit should be ok. Difference in price is negligible though, might as well run 4awg. 6awg Romex however you will need to set the limit to 40 amps. At 40 amps you may was well install a 14-50 and get the newer HPWC so it can be removed more easily.

I'm currently using 4awg THHN with a 60 amp breaker, HPWC set to 48 amps continuous. I can change the breaker to something higher in the future (90 amp) (NEC seems to rate this wire at 95 amps, but from other charts I found 80 is recommended breaker) if I get another car that can charge over 48 amps, I'll swap out the breaker.

A few months back when I was at Lowes picking up the wire, they didnt have enough 4 awg for my run. They recommended 2 awg since it was there and they had enough. I said if you can price match, im game. Well now I have my HPWC on an 80 amp breaker and can load share if/when I end up with two Teslas. However, 2 awg wire is a massive pain. But I feel really good when I am charging at 48 amps that I am nowhere near the limit.