HPWC SER vs Romex Wire?

Discussion in 'Model 3: Battery & Charging' started by SureValla, Apr 10, 2018.

  1. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    I'm all set to get my HPWC installed and was planning on using romex wire. That is until I came upon SER cable. It seems like its just as safe and easy to use but costs less. Seems like I should switch no? Can anyone elaborate on the differences between these two cables?

    For reference:
    2-3 NM-B | $6.74/ft | 2-3 W/G NM-B Wire Black
    2-2-2-4 SER | $6.29/ft | 2-2-2-4 Copper SER Service Entrance Cable

    I am installing a 90 amp breaker, 75 ft of cable. Yes I know the M3 can only take 48amps but I am planning for a second tesla in the future with a second HPWC
     
  2. Craig-Tx

    Craig-Tx Member

    Joined:
    Aug 1, 2016
    Messages:
    112
    Location:
    Fort Worth, TX
    Standard Disclaimer - I'm not a professional... seek advice... etc.etc.

    It seems that SE cable is frequently used in Branch circuits and is permitted per NEC 338.10 (check with local authorities for your area...)
    You may also look for other electrical supply as you don't need 3 conductor for the HPWC, it doesn't need a neutral connection.
    For NM-B, you only need 2-2 with ground or 2-2-4 SER. If you can locate that (if they make it) it could save a lot in copper.
     
    • Like x 1
  3. Daniel in SD

    Daniel in SD Well-Known Member

    Joined:
    Jan 25, 2018
    Messages:
    5,446
    Location:
    San Diego
    You only need two conductors for HPWC. I would do it with THHN and conduit. Would be about the same price and safer.
    For 90A can't you use 3ga even for a 75ft run?
     
    • Helpful x 1
  4. Craig-Tx

    Craig-Tx Member

    Joined:
    Aug 1, 2016
    Messages:
    112
    Location:
    Fort Worth, TX
    For Romex (NM-B) and SER cable used in insulation, you must size the cables per the 60 degree ampacity limits. 2 AWG limit at 60 deg is 95 amps.

    THHN and Conduit is always a great idea when possible. I can't speak to the OP's situation, but when I ran my circuit, I had to cut about 8 holes in sheetrock to fish about 75 feet of romex to where I wanted it. No possible way without LOTS of sheetrock distruction to run conduit.
     
    • Helpful x 1
    • Like x 1
  5. Daniel in SD

    Daniel in SD Well-Known Member

    Joined:
    Jan 25, 2018
    Messages:
    5,446
    Location:
    San Diego
    THHN is actually way cheaper. $1.29/ft for 2ga. x2 of course and $0.37/ft for 8ga ground
     
  6. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    Thanks yeah not looking to exceed 95amp as I'm only going to have a 90amp breaker.

    I'm looking to avoid the hassle of running conduit. I just don't get why you'd ever use nm 2-2 with ground when 2-2-4 ser is cheaper
     
  7. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    I'm looking to avoid conduit
     
  8. Daniel in SD

    Daniel in SD Well-Known Member

    Joined:
    Jan 25, 2018
    Messages:
    5,446
    Location:
    San Diego
    If you're not making a bunch of turns it's really not that bad. You don't even have to fish it. I was able to push 3ga wire through 1 inch conduit no problem.
    I can't imagine fishing 2ga romex through studs!
     
  9. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    Wasn't thinking of running through studs I was think of using large plastic staples. I.e. GARDNER BENDER Cable Staple,1-1/2In,Plastic,Serv E,Pk2 - 6LVG1|GSE-402 - Grainger
     
  10. Craig-Tx

    Craig-Tx Member

    Joined:
    Aug 1, 2016
    Messages:
    112
    Location:
    Fort Worth, TX
    Depending on your scenario, you may not be able to pass an inspection if you go this route.
    Romex (and likely SER) cable cannot be exposed. It must be protected from physical damage. I believe it may be acceptable in garages above a certain height (i.e. near the ceiling) but not likely at the height of your HPWC.
     
  11. boaterva

    boaterva Supporting Member

    Joined:
    Apr 2, 2016
    Messages:
    7,436
    Location:
    Northern Virginia, USA
    Might find some useful info in Flasher’s FAQ: see the link in my sig. Lots of cabling info.
     
  12. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    Wire will be run along joists in basement then up inside wall to the rear entry of the HPWC so never exposed to physical damage
     
    • Like x 1
  13. eSpiritIV

    eSpiritIV Member

    Joined:
    Mar 24, 2016
    Messages:
    434
    Location:
    Portland, OR

    Craig is correct. SER cable should only be used for "service entrace" per the cable type, and as he said, you have to use the lower ampacity tables at 60 degrees. running single conductors of THHN in conduit is the way to go! In the long run a few bucks wont hurt you to go with the appropriate wire.
     
  14. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    my desire to go without conduit is not due to cost (in fact romex will cost more) its actually to make the install easier. Its very easy to fish the cable where it needs to go so I don't see having to change it in the future as being an issue at all.
     
  15. voip-ninja

    voip-ninja Give me some sugar baby

    Joined:
    Mar 15, 2012
    Messages:
    4,115
    Location:
    Colorado
    I think it is smarter to just run all four wires (three conductors and neutral) that way the circuit can be repurposed for another application later, if needed... rather than spending time and money having to run the circuit again.

    If you run all four wires you can also terminate to a new sub-panel, run the HPWC from that and run something else from the rest of it.
     
    • Like x 1
  16. voip-ninja

    voip-ninja Give me some sugar baby

    Joined:
    Mar 15, 2012
    Messages:
    4,115
    Location:
    Colorado
    It meets code for it to run in basement rafters where it is technically exposed as long as any gaps across drywall or open space are bridged with building structure such as 2x4 studs that the romex is attached to.
     
  17. SureValla

    SureValla Member

    Joined:
    Mar 15, 2016
    Messages:
    626
    Location:
    Shelton, CT
    exactly, I was planning on capping the neutral wire inside the HPWC. Would I also cap it inside the main panel or should that be connected to the neutral bar?
     
  18. mongo

    mongo Well-Known Member

    Joined:
    May 3, 2017
    Messages:
    12,227
    Location:
    Michigan
    SER is fine for branch circuits, it just has extra features (such as UV resistance) that make it usable for service connections. https://www.dli.mn.gov/ccld/PDF/eli_bulletin_cable.pdf

    For this size of cable, the bridging is not required.
    Connect at panel, prevents it from picking up induced voltages and prevents issues down the road if the HPWC is replaced.

    Have you looked at flexible metal conduit? I used it for a hot tub run (inside section). You can pre-install the THHN, then rout the whole thing. 1 in. Flexible Reduced Wall Aluminum Conduit, 50ft or 500ft
     
  19. cmaster

    cmaster Member

    Joined:
    Dec 4, 2014
    Messages:
    240
    Location:
    United States
    You can use #2 SER Aluminum then connect a disconnect switch (100A) from the circuit breaker. Next, from the disconnect switch, use #4 COpper to HPWC. It meets the NEC spec.

    How do I know? An electrician gave me a quote with that job. I did it myself.
     
  20. voip-ninja

    voip-ninja Give me some sugar baby

    Joined:
    Mar 15, 2012
    Messages:
    4,115
    Location:
    Colorado
    According to the electrician I spoke with you should terminate the neutral lead at the circuit breaker side.
     
    • Like x 1

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.