    Obligatory new Model 3P owner, 500miles old, yadda yadda, love it, it's fast, ICE cars are awful, red lights are my enemy.

    Moving on.

    I need to charge this puppy at home (renting), and it came down to a choice between spending ~1,000 for an electrician (Northern VA, am I right?((Also landlords demand a professional installation))) OR using the old 10-30R dryer plug that's already there.

    I chose the latter... I only commute like 15 miles each way to work -.-

    So per recommendation, I bought a new industrial strength 10-30R outlet and went to go install it. Confirming that the wire installed does not have a GROUND wire, I couldn't replace it with a 14-30R. So I turn it off at the breaker, take it out and I find gooey stuff on the wires. See pics.

    Is this stuff normal? Bad news bears? Should I wipe it clean before throwing on the new one?

    Also, to connect to this outlet, I will have to use an extension cord. Is the #1 method a bad idea? Too many breaks in the line?

    #1 - Mobile connector w/ 10-30 adapter -> 10-30/14-50 adapter -> 14-50 extension cord (larger guage wire for safety reasons?)-> 14-50/10-30 adapter -> outlet

    OR

    #2 - Mobile connector w/ 10-30 adapter -> 10-30 extension cord -> outlet

    I am choosing to use the 10-30 adapter so I don't have to worry about manually changing the cars amp draw.

    Sorry this is all a mess, thanks in advance to anyone with advice for me.

    Don't wanna burn the house down.

    Imgur
     
    • Like x 1
  2. Akikiki

    Akikiki A'-Lo-HA ! y'all

    Joined:
    Nov 26, 2012
    Messages:
    3,544
    Location:
    Kaneohe
    Me too. I'm not an electrician. I think you need to first talk to your landlord. Sell him on the valuable going forward of his house being EV charging capable. Then tell him it needs a 14-50 outlet 50 amp circuit. If he back away from that, why not offer to pay half, and deduct it from the rent? If he doesn't like that, tell him how the 14-30 circuit will just get by, but needs a pro to look at it and maybe it will require an upgrade over the existing circuit. Again, if you must, share the cost. And try to take it off the rent.

    I would not be surprised if the pro electrician wants to replace the wire. And if the box will handle it, maybe the smarter thing is to pull two wires one for 30 and one for 50. Who knows.

    But I would worry about that gooey stuff. I personally would not use it until you/we know more. And I would not use an extension cord with it. Like you said, you don't want to burn the house down. Maybe the landlord will pickup the cost of the pro coming by. He should.

    You might want to put this in writing to him. Google your state and city statutes to see if there are regs that support your request.
     
    • Funny x 1
  3. solodogg

    solodogg Member

    Joined:
    Apr 8, 2019
    Messages:
    114
    Location:
    Orlando
    That gooey stuff is no-ox, used to keep the wires from corroding and causing any issues with the connections.

    With that said, i'm still going to suggest you contact an electrician to swap the receptacle out with the questions you're asking. You're playing with something that could potentially cause a fire if installed improperly, or worse yet kill you don't know what you're doing.
     
    • Like x 3
    • Informative x 1
  4. GoFaster

    GoFaster Supporting Member

    Joined:
    Nov 16, 2018
    Messages:
    16
    Location:
    Wayland, MA
    I am not an electrician (but I've had more than one tell me I do better work than most of those that are...)

    The gooey stuff is nothing to worry about. Assuming that the insulation is intact (hot wire can cause some insulation to get soft and gooey), it's probably either no-ox or even just cable lube.

    Suggestion #1: Find an electrician, with or without your landlord paying for it, to take a look and swap out the receptacle. Why? You're asking too many questions. Yes, questions are good but with a circuit pulling that much power for that long a period of time it's not the "attach red wire to the screw on receptacle where it says the red wire goes" kind of things you need to worry about. It's the subtle stuff that's going to bite you in the butt. Or, more precisely, cause a house fire.

    Suggestion #2: Go with your choice #2 above. Why? Every plug/receptacle connection is a potential fire hazard. Especially if you're not using good quality stuff (i.e., usually, but not always, non-Home Depot parts).

    Again, given your questions, find an electrician. House fires are no fun.
     
    • Like x 1
  5. qdeathstar

    qdeathstar Member

    Joined:
    May 17, 2019
    Messages:
    319
    Location:
    VB
    #5 qdeathstar, Aug 16, 2019 at 4:43 AM
    Last edited: Aug 16, 2019 at 4:49 AM

    Hi. Electrician here. The dryer outlet without a ground is perfectly fine to use to charge the tesla. Old dryer outlets had the case of the dryer bonded to the neutral of dryer, as the dryer required 110v for its lightsgue and timer circuits. However, the neutral wire of the circuit is bonded to the ground at your panel. Because the tesla charger does not require a neutral, you can essential treat the neutral eire as a ground wire in this case.

    The goo is definitely anti oxidation compound, which is perfectly fine. My only concern is now that you took the outlet out, making sure you have the correct torque on the screws is important, most homeowners do not tighten them enough, and that will result in a fire.

    Choice 2 is the better choice because it will ground the tesla charger, despite the fact it is using the “neutral” conductor.

    You definitely do not need to run a new wire, but the extension cords will really need to be monitored and replaced at the first sigh of corrosion/damage
     
    • Like x 3
    • Informative x 1
  6. Manitoba Keith

    Joined:
    Jul 28, 2019
    Messages:
    69
    Location:
    Brandon, Manitoba
    Another electrician. Please note, that is Aluminum wire Thus the compound. It requires special consideration and handling. Do not ring strip the cable. If you are just replacing, you should be OK if you torque the connections well. You can also put a DYMO tape on the receptacle with some words (just to raise letters) if the letters shrink back down you have a HEAT ISSUE.
     
    • Informative x 3
    • Helpful x 1
    • Like x 1
  7. Cmunny

    Cmunny Member

    Joined:
    Jul 23, 2019
    Messages:
    10
    Location:
    Savannah, GA
    Another electrician here.

    It is worth noting that the 1030 outlet only puts out 30 amps, so the charge rate is between the stage 1 120v (2-4 mi/hr) and the stage 2 NEMA 1560 (30 mi/hr charge rate). You will get around a 10-14 mile and hour charge rate using the 1030.

    If your daily commute is only 15 miles, you could very well charge it off of a standard 120v 20amp circuit and forego the need for the 220v circuit at all. At least for your daily charges. If you have a particularly long range day and you need more than the normal 15 miles, then you could run an extension cord from the 1030 to boost charge rate to catch up.

    I always advise against the habitual use of extension cords. Even mindful people can get complacent, and any time you are dealing with 220v circuits, complacency kills.
     
    • Like x 1
  8. voip-ninja

    voip-ninja Give me some sugar baby

    Joined:
    Mar 15, 2012
    Messages:
    3,929
    Location:
    Colorado
    So if the landlord won't acquiesce to his request for a subsidized EV outlet he should go see if he can get city/state to hassle the guy to give it to him?

    Did the landlord advertise that the home/apartment came with EV charging? No? Then if they don't see any value in adding it then it's nobody's damn business but theirs as it's their property.

    Oh, I see you're from Hawaii.... well that explains a lot.
     
  9. mswlogo

    mswlogo Active Member

    Joined:
    Aug 27, 2018
    Messages:
    2,767
    Location:
    MA
    #1) Don’t use an extension cord.

    #2) See #1

    #3) See #2
     
  10. ilyak

    ilyak Member

    Joined:
    Mar 16, 2019
    Messages:
    7
    Location:
    Rochester, NY
    This is incorrect. I get 21-22 miles/hour from a 10-30, as [email protected] produces 5.5kW. Tesla also lists 22 miles/hour for the 10-30 for Model 3.
     
    • Like x 2
  11. SSedan

    SSedan Active Member

    Joined:
    Jul 24, 2017
    Messages:
    1,515
    Location:
    Greenville Wisconsin
    10-30 is fine for this circumstance and an under considered option.
    I got by on one with a much more power hungry P85 thru a Green Bay winter
     
  12. qdeathstar

    qdeathstar Member

    Joined:
    May 17, 2019
    Messages:
    319
    Location:
    VB
    I don’t think charging a car off of a 120v outlet is a good idea. A constant 12a load on push-in receptacles that may have other existing loads on them is doomed for failure at some point...
     
    • Disagree x 1
  13. AKinDC

    AKinDC Member

    Joined:
    Apr 30, 2019
    Messages:
    118
    Location:
    DC
    More than $1000 for an electrician? Is it a really complicated job?
    I had to run cable from the breaker box in my basement, up through the ceiling, over two rooms, into the garage, and then wrap conduit around to where I wanted the 14-50, and it was still only a little more than $1000.
    Might want to give https://www.havepower.com/ a call and see what they can do.
     
  14. qdeathstar

    qdeathstar Member

    Joined:
    May 17, 2019
    Messages:
    319
    Location:
    VB
    I charge at least 625 for a 50a circuit.
     
  15. Casmium

    Casmium Member

    Joined:
    Sep 14, 2018
    Messages:
    93
    Location:
    Mississauga
    Also just make sure the new outlet you bough is compatible with aluminum wire, if it isn't you'll need to get one that is, or if it is allowed in your area get some al-cu splices and make some pigtail cables to the outlet. You don't want to use a copper only outlet with aluminum cable.
     
    • Like x 2
  16. jat255

    jat255 Member

    Joined:
    Sep 11, 2017
    Messages:
    76
    Location:
    Boulder, CO
    In Virginia? Good luck!
     
  17. qdeathstar

    qdeathstar Member

    Joined:
    May 17, 2019
    Messages:
    319
    Location:
    VB
    All dryer outlets are going to rated for aluminum
     
  18. Octo

    Octo Member

    Joined:
    Jun 28, 2019
    Messages:
    269
    Location:
    Dallas
    Haha. I just pulled 140ft of three 3/0 copper wires plus ground through 2” conduit with 10 90 degree bends and 3 LB conduit boxes from a basement through a crawl space to my garage in 100F weather.

    I would pay someone a couple thousand $ now instead.
     
    • Funny x 4
  19. jebinc

    jebinc M3 LR AWD w/FSD and white premium interior

    Joined:
    Jun 19, 2019
    Messages:
    1,966
    Location:
    Seattle, WA
    I ran in a 10-30 plug for a while (before I installed a HPWC) and you’ll find 24amps charging adequate. Do clean and restrooms those wires before installing the better receptacle.
     
  20. qdeathstar

    qdeathstar Member

    Joined:
    May 17, 2019
    Messages:
    319
    Location:
    VB
    Why did you pull three wires? You can also only have 3 90s before a junction box (or LB)
     
    • Informative x 1

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.