Tannergroup2

Member
Jan 2, 2018
39
23
Lake Worth, FL
So I thought I had 2-3 weeks till delivery and just got a call and I am getting it next Monday lol SO electrician is coming Thursday. Just going to do the 50a for now and figure out the HPWC when the time comes. Unless I am missing something
 
  • Like
Reactions: mongo

Big Earl

bnkwupt
Jul 12, 2017
4,963
8,870
Springfield, VA
All of the above - have it wired for the HPWC & it will be overspec'd for the 14-50.

FYI, have the 14-50 outlet installed 'upside down', i.e., ground on the top. That way the cable hangs down when plugged in. It's less stress.

Install instructions for the HPWC: https://www.tesla.com/sites/default...l_connector_installation_manual_80A_en_US.pdf

That's right side up. Outlets should be installed with the ground up to prevent shorting of the hots and/or hot and neutral if something rests across the pins when the plug isn't fully inserted. Of course, NEC doesn't actually provide official guidance on which way is correct and there are arguments that are contrary to the one I provided above. ;)
 

Rocky_H

Well-Known Member
Feb 19, 2015
5,908
6,783
Boise, ID
I do think it's overkill that people are still recommending 100A breakers for the wall connectors. The 100kWh battery size cars can only take 72A max, but most of the cars can't even take that much. A 90A breaker would do that, but you could still get 64A from an 80A breaker, which is almost there and a bit lower cost on wire. For the Model 3, it can only take 32A or 48A, so the 100A is beyond overkill for that. A 50 or 60A breaker should be plenty for home overnight charging.
 
  • Like
Reactions: mspohr

mongo

Well-Known Member
May 3, 2017
12,878
37,970
Michigan
So I thought I had 2-3 weeks till delivery and just got a call and I am getting it next Monday lol SO electrician is coming Thursday. Just going to do the 50a for now and figure out the HPWC when the time comes. Unless I am missing something

As mentioned above, a 14-50 such as Leviton 279 can handle 4 AWG wire. If you have the electrician run that size now, you may never need to upgrade (I believe that makes you good for a 70 amp charge rate with [email protected] wire and 90A breaker).
 
  • Like
Reactions: paperjohn

About Us

Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.

Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.