I had an electrician install ~55 feet of 6/3 from an existing (unused) 50 amp circuit breaker in my main panel through (unused) conduit into a Tesla wall charger in my garage; I configured the charger for a 50 amp breaker to get 40 amps of charge rate. After ~5 minutes, the breaker tripped and was hot to the touch. No faults were detected.
I changed the wall charger config to expect a 40 amp breaker and I reset the circuit breaker in the panel. It will now charge at 32A (I’ve gone from 150-250 miles of charge a couple of times) but the breaker makes a light sizzling sound and gets pretty warm - after an hour or so, it’s ~180 degrees F on my laser thermometer.
I just sent a note to the electrician suggesting we replace the old breaker with a new 60 amp unit…does this sound like I’m on the right track? I’m getting 27mph charging, which plenty fast (though faster is better) but the sound and heat make me nervous. I’m not sure I want to come home late at night, plug in, and go to sleep unless this is normal.
I should add that the main (100A) breaker is also a bit warm and registering 140-150 degrees while charging and running the home AC simultaneously. I plan to not run AC and charge at the same time once I sort this out, assuming everything is running off a 100A breaker. Charging at night means I don’t need both of those on at the same time.
I changed the wall charger config to expect a 40 amp breaker and I reset the circuit breaker in the panel. It will now charge at 32A (I’ve gone from 150-250 miles of charge a couple of times) but the breaker makes a light sizzling sound and gets pretty warm - after an hour or so, it’s ~180 degrees F on my laser thermometer.
I just sent a note to the electrician suggesting we replace the old breaker with a new 60 amp unit…does this sound like I’m on the right track? I’m getting 27mph charging, which plenty fast (though faster is better) but the sound and heat make me nervous. I’m not sure I want to come home late at night, plug in, and go to sleep unless this is normal.
I should add that the main (100A) breaker is also a bit warm and registering 140-150 degrees while charging and running the home AC simultaneously. I plan to not run AC and charge at the same time once I sort this out, assuming everything is running off a 100A breaker. Charging at night means I don’t need both of those on at the same time.