JuiceBox 40 cable heat
Discussion in 'Model 3: Battery & Charging' started by nateads, Feb 26, 2021.
  1. davewill
    davewill Active Member
    San Diego, CA, US
    #21 davewill, Mar 1, 2021 at 1:52 PM
    I agree with you that they should have used a 50a rated pigtail, but the one they used probably meets specs. A little searching finds that the 40a rated range cords generally have 10awg wire and the 50a rated ones have 8awg. Once you're past the wallbox, it's a different set of rules, and cables in air have different ratings than cables in wall or in conduit.
    I'm also pretty sure the whole 80% rule no longer applies once you're out of the wall. However, if the cord is regularly getting that hot, they should have bumped it up...and the OP may want to do so for his own comfort and peace of mind. He could also simply set the JuiceBox for 30a and I'm sure it would be much cooler.
    I just had to make a similar decision. I have an OpenEVSE and the J1772 cord and plug was rated for 40a, so I had my unit set to deliver 40a. The Rav4EV has the same charger as the original Model S, so it happily charged at 40a. Everything seemed OK, but I recently found that the plug was getting hot, and opened the housing to find that the wires inside had the insulation burnt off.
    I bought a replacement cord and plug that was was more sturdily built and I now run the unit at 30a.
    Here's the new one:
    Funnily enough, it's Leviton branded, but the wire gauge is much thicker than the one I was using. It also has a much higher quality Yazaki branded plug which I've been using on my other EVSE for years. It's only rated for 30a, but unlike the one I was using, it really IS rated for that and specifically for EV use.
  2. DMC-Orangeville
    DMC-Orangeville 85D and John Deere 5100E
    NW of the 6ix Canada
    #22 DMC-Orangeville, Mar 1, 2021 at 1:54 PM
    Well - the Canadian electrical code publishes tables showing maximum amperage allowed by a cable. Here is table 2, copper wire Not free air rated (your cable) You'll see that a 10 AWG cable should be rated for 30 amps (60C). If a cable has a 90C insulation, it could be used *in certain circumstances* for a 40 amp load.
    Now....the cable used to supply the power to the Juicebox is NMD. NMD has its' own rating in Canada see below: NMD 8 AWG has a rating of 45 amps - too small for a 50 amp rated circuit. NMD 6 AWG is rated for 65 amps - so the electrician used the correct cable.. NOTE to the Americans on this post: This is a Canadian application, only. Why can an 8AWG cable be used on the Juicebox vs 6 wiring it in?(your question): - from CEC table, above- a 60C cable, 8 AWG, is rated at 40 amps. A 90C cable, 8 AWG, is rated for 55 amps. It will still get warm, but shouldn't get hot. I'd probably still recommend a 6 AWG cable.
  3. DMC-Orangeville
    Your explanation is correct, However, "Romex" (NMD or NMWU) in Canada has different current ratings than NM-B in the USA. See my post, above
  4. Rocky_H
    Rocky_H Well-Known Member
    Boise, ID
    Very unusual circumstances that probably aren't applicable here, because you have to stay within the rated temperature limits of everything along the chain, including all of the connection lugs that clamp the wires. And most residential or normal commercial breakers and junction boxes don't have connection points rated to use above the 75 degree C rating, so you almost never get to use the 90 C column unless it's on very particular industrial kinds of things.
  5. TheRFMan
    TheRFMan Member
    Ottawa, Canada
    I though we were talking about the cord from the 14-50 plug to the JuiceBox. That is stranded flexible cord, not NMD, isn't it? I can't find the standard off hand, but I thought those were rated to higher currents because they are assumed to be in air, not in walls surrounded by insulation (which is why the electrical code prohibits their use walls or ceilings). Surely, if the device received UL certification, the cord must be adequate as per regulation.
    That being said, I'm not too fond of regulations or standards that allow cables to get hot under load.
  6. Gasaraki
    Gasaraki Active Member
    Syracuse, NY
    Umm, there's your problem... I would switch to 6 gauge between the plug and the wall connector box.
  7. MY-Y
    MY-Y Member
    MD
    #27 MY-Y, Mar 5, 2021 at 4:38 AM
    The Tesla HPWC Gen 3 provides 48 amps to my car through a cord much thinner than the pigtail between my 14-50 and JuiceBox. Yes, the HPWC cord gets warm. If I have two loops across the holder (top of the HPWC), it gets pretty hot.
    I was concerned about the warmth of the 14-50 on my JuiceBox as well. Even charging at 32 amps (max for my other EV), it got quite toasty. At Rocky's recommendation, I swapped out the Leviton outlet for a higher quality one. I got a Hubbell 14-50 on Amazon for $70 and a new faceplate because the outlet is bigher. This dropped the temperature quite a bit. I posted about replacing the outlet in post #8 and the warmth of the HPWC cord in post #11 here: JuiceBox 40
  8. nateads
    nateads Member
    Markham, ON
    With my JuiceBox being indoor wall mounted I'm tempted just to open the box again and run a 6AWG hardline right from the breaker strait to the JuiceBox with no plug. I cannot see that idea being any worse than the plug that is there now as it's I think a 8AWG and I don't find the breaker or white 6AWG wire to get warm at all.
  9. davewill
    San Diego, CA, US
    Getting a beefier plug pigtail would accomplish the same thing and leave the possibility of using your UMC if the JuiceBox went down for any reason.