@JHCCAZ While that is a good technical explanation, I think you fell into the wrong thread:
No one is saying it is "preferred". No one is saying it is an "advantage".
The RV parks would call the police on you if you tried rewiring their infrastructure.
You seem to have missed what this thread about. People are not installing high amp 120V circuits to use by choice, which you are wagging your shaming finger at. This is people using what's already available. These TT-30 outlets already exist at the RV parks, and if people need charging, and it's all they can make use of, they will. It's not "preferred", but it's better than nothing.
Well I'm sorry if anyone felt shamed, I didn't think that's what I was doing at all, and frankly I think that response is a little harsh but I'll deal with it.
The OP clearly said, a couple of times, that he is the owner of the RV Park! And he talked about charging on 30 amp 110V. So my comment had nothing to do with telling him to rewire someone else's RV park, and no one's getting arrested here unless they burn it down, which if anything I'm trying to help prevent
So, understand that the spirit of what I was explaining was to a person who indeed has the right, and I thought the interest, in doing something about his own existing setup at his own RV park, in order to charge EVs. I certainly apologize to him, if he thought I was wagging my finger at him - not my intent at all.
On the other hand, for a non-owner user of the park who's trying to make use of the available infrastructure and not trip breakers, I would say this:
Scenario 1: You try to pull almost 30 amps, well let's call it 80% of 30A = 24A if you're minding the continuous- load rule, from an available 120V outlet, to get the highest possible 120V charge rate. This is around 2900W. If everything is in decent shape it shouldn't trip that breaker, which hopefully is dedicated (but if they're sharing circuits for 50 amp outlets, why wouldn't they be for 30 amp outlets? IDK). However, note that 24 amps is being added to the load of one pole of the upstream main breaker/fuse servicing that particular building or parking site (? no I'm not personally experienced with RV-park wiring). So if there isn't plenty of margin, it's a more significant extra risk of tripping a panel Main which would upset more people.
Scenario 2: You use the 240V 14-50, but knowing that it might be shared with another one based on historic practices, and not wanting to trip anything, you turn down the charge rate to 12 amps. This is the same ~2900W as in scenario 1, but the difference is you're only adding 12A of balanced loading, per pole, to the upstream Mains.
If you're feeling lucky, you could then go higher, up to 15A or 20A to get an even better charge rate, and yes at some point you might trip a shared 50A breaker being used by your family's RV or your immediate neighbor's RV, but you're still pulling less from upstream breaker poles.
I do understand that Scenario 1 is the original attempt to get the EV charged without tripping the 14-50 receptacle's breaker. But if there is a mix of 120V and 240V outlets available, I would think that you should prefer to run hair dryers or toaster ovens from the available 120V receptacle, and do your modest EV charging from the 14-50. I'm sure that might involve deploying a heavy duty extension cord and it's less convenient based on the way the RV is normally hooked up, but hey you're trying to adapt your situation to the EV. It's still better, either way, if you and your family can organize things to start the EV charging after everyone goes to bed. But in general I think the 240V for EV is a better strategy.