Hi,
I got my 10kW system installation done a few days ago and I the peak values (midday and sunny) never go over 6.5kW and I was wondering if that's normal. It is two systems connected to two Powerwall+. The inclination is 9/12 (36.86 degrees) and they are facing south (azimuth is 209).
This is the house (It shows some shadow in the picture but it has none when I notice the peak value may be too low).
Inverter 1 wiring:
Inverter 2 wiring:
Data from PyPowerwall:
Battery power level: 44%
Combined power metrics: {'site': 90, 'solar': 6260, 'battery': -5400, 'load': 965.25}
Grid Power: 0.09kW
Solar Power: 6.26kW
Battery Power: -5.40kW
Home Power: 0.97kW
Grid raw: {'last_communication_time': '2022-06-13T12:43:54.064582899-04:00', 'instant_power': 90, 'instant_reactive_power': -131, 'instant_apparent_power': 158.93709447451215, 'frequency': 0, 'energy_exported': 417, 'energy_imported': 39544, 'instant_average_voltage': 247.45, 'instant_average_current': 8.58, 'i_a_current': 0, 'i_b_current': 0, 'i_c_current': 0, 'last_phase_voltage_communication_time': '0001-01-01T00:00:00Z', 'last_phase_power_communication_time': '0001-01-01T00:00:00Z', 'last_phase_energy_communication_time': '0001-01-01T00:00:00Z', 'timeout': 1500000000, 'num_meters_aggregated': 1, 'instant_total_current': 8.58}
Solar raw: {'last_communication_time': '2022-06-13T12:43:54.088864433-04:00', 'instant_power': 6260, 'instant_reactive_power': 0, 'instant_apparent_power': 6260, 'frequency': 59.980000000000004, 'energy_exported': 63310, 'energy_imported': 0, 'instant_average_voltage': 246.8, 'instant_average_current': 25.364667747163693, 'i_a_current': 0, 'i_b_current': 0, 'i_c_current': 0, 'last_phase_voltage_communication_time': '0001-01-01T00:00:00Z', 'last_phase_power_communication_time': '0001-01-01T00:00:00Z', 'last_phase_energy_communication_time': '0001-01-01T00:00:00Z', 'timeout': 1000000000, 'num_meters_aggregated': 2, 'instant_total_current': 25.364667747163693}
Vitals: {'STSTSM--1538000-25-F--GF22206600017G': {'partNumber': '1538000-25-F', 'serialNumber': 'GF22206600017G', 'manufacturer': 'TESLA', 'firmwareVersion': '2022-04-28-ga12200ec2', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 207}, 'STSTSM-Location': 'SolarPowerwall', 'alerts': ['GridCodesWrite', 'GridCodesWrite', 'FWUpdateSucceeded', 'BackfeedLimited', 'SystemConnectedToGrid', 'PodCommissionTime']}, 'TETHC--3012170-25-C--TG122130001JNG': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '3012170-25-C', 'serialNumber': 'TG122130001JNG', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 224}, 'THC_State': 'THC_STATE_AUTONOMOUSCONTROL', 'THC_AmbientTemp': 24.5}, 'TEPOD--1081100-33-V--T22D0000006': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0000006', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 226}, 'POD_nom_energy_to_be_charged': 8944.0, 'POD_nom_energy_remaining': 6510.0, 'POD_nom_full_pack_energy': 14889.0, 'POD_available_charge_power': 7000.0, 'POD_available_dischg_power': 8760.0, 'POD_state': 'POD_ACTIVE', 'POD_enable_line': True, 'POD_ChargeComplete': False, 'POD_DischargeComplete': False, 'POD_PersistentlyFaulted': False, 'POD_PermanentlyFaulted': False, 'POD_ChargeRequest': False, 'POD_ActiveHeating': False, 'POD_CCVhold': False}, 'TEPINV--1081100-33-V--T22D0000006': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0000006', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 253}, 'PINV_EnergyDischarged': 13020.0, 'PINV_EnergyCharged': 18130.0, 'PINV_VSplit1': 124.7, 'PINV_VSplit2': 122.60000000000001, 'PINV_PllFrequency': 59.971000000000004, 'PINV_PllLocked': True, 'PINV_Pout': -2.7, 'PINV_Qout': 0.04, 'PINV_Vout': 247.20000000000002, 'PINV_Fout': 59.988, 'PINV_ReadyForGridForming': True, 'PINV_State': 'PINV_GridFollowing', 'PINV_GridState': 'Grid_Compliant', 'PINV_HardwareEnableLine': True, 'PINV_PowerLimiter': 'PWRLIM_POD_Power_Limit', 'alerts': ['PINV_a067_overvoltageNeutralChassis']}, 'TETHC--3012170-25-C--TG122117000WLV': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '3012170-25-C', 'serialNumber': 'TG122117000WLV', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 224}, 'THC_State': 'THC_STATE_AUTONOMOUSCONTROL', 'THC_AmbientTemp': 24.10000000000001}, 'TEPOD--1081100-33-V--T22D0003283': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0003283', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 226}, 'POD_nom_energy_to_be_charged': 8953.0, 'POD_nom_energy_remaining': 6473.0, 'POD_nom_full_pack_energy': 14876.0, 'POD_available_charge_power': 7000.0, 'POD_available_dischg_power': 8770.0, 'POD_state': 'POD_ACTIVE', 'POD_enable_line': True, 'POD_ChargeComplete': False, 'POD_DischargeComplete': False, 'POD_PersistentlyFaulted': False, 'POD_PermanentlyFaulted': False, 'POD_ChargeRequest': False, 'POD_ActiveHeating': False, 'POD_CCVhold': False}, 'TEPINV--1081100-33-V--T22D0003283': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0003283', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 253}, 'PINV_EnergyDischarged': 13060.0, 'PINV_EnergyCharged': 18260.0, 'PINV_VSplit1': 124.5, 'PINV_VSplit2': 122.4, 'PINV_PllFrequency': 59.976, 'PINV_PllLocked': True, 'PINV_Pout': -2.67, 'PINV_Qout': 0.05, 'PINV_Vout': 246.8, 'PINV_Fout': 59.989000000000004, 'PINV_ReadyForGridForming': True, 'PINV_State': 'PINV_GridFollowing', 'PINV_GridState': 'Grid_Compliant', 'PINV_HardwareEnableLine': True, 'PINV_PowerLimiter': 'PWRLIM_POD_Power_Limit', 'alerts': ['PINV_a067_overvoltageNeutralChassis']}, 'PVAC--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1538100-01-F', 'serialNumber': 'CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 296}, 'PVAC_Iout': 10.68, 'PVAC_VL1Ground': 124.19999999999999, 'PVAC_VL2Ground': 121.5, 'PVAC_VHvMinusChassisDC': -212.0, 'PVAC_PVCurrent_A': 5.67, 'PVAC_PVCurrent_B': 5.73, 'PVAC_PVCurrent_C': 0.0, 'PVAC_PVCurrent_D': 0.0, 'PVAC_PVMeasuredVoltage_A': 241.60000000000002, 'PVAC_PVMeasuredVoltage_B': 241.9, 'PVAC_PVMeasuredVoltage_C': -0.29999999999999893, 'PVAC_PVMeasuredVoltage_D': -1.299999999999999, 'PVAC_PVMeasuredPower_A': 1368.0, 'PVAC_PVMeasuredPower_B': 1377.0, 'PVAC_PVMeasuredPower_C': 0.0, 'PVAC_PVMeasuredPower_D': 0.0, 'PVAC_LifetimeEnergyPV_Total': 29090.0, 'PVAC_Vout': 247.60000000000002, 'PVAC_Fout': 59.976, 'PVAC_Pout': 2760.0, 'PVAC_Qout': 20.0, 'PVAC_State': 'PVAC_Active', 'PVAC_GridState': 'Grid_Compliant', 'PVAC_InvState': 'INV_Grid_Connected', 'PVAC_PvState_A': 'PV_Active', 'PVAC_PvState_B': 'PV_Active_Parallel', 'PVAC_PvState_C': 'PV_Active', 'PVAC_PvState_D': 'PV_Active', 'PVI-PowerStatusSetpoint': 'on'}, 'PVS--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'PVAC--1538100-01-F--CN321286C1F0OR', 'partNumber': '1538100-01-F', 'serialNumber': 'CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': '0eb61d6819b2b3', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 297}, 'PVS_vLL': 247.4, 'PVS_State': 'PVS_Active', 'PVS_SelfTestState': 'PVS_SelfTestOff', 'PVS_EnableOutput': True, 'PVS_StringA_Connected': True, 'PVS_StringB_Connected': True, 'PVS_StringC_Connected': False, 'PVS_StringD_Connected': False, 'alerts': ['PVS_a019_MciStringC', 'PVS_a020_MciStringD']}, 'PVAC--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1538100-01-F', 'serialNumber': 'CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 296}, 'PVAC_Iout': 14.76, 'PVAC_VL1Ground': 124.5, 'PVAC_VL2Ground': 121.5, 'PVAC_VHvMinusChassisDC': -212.0, 'PVAC_PVCurrent_A': 10.42, 'PVAC_PVCurrent_B': 0.01, 'PVAC_PVCurrent_C': 0.0, 'PVAC_PVCurrent_D': 0.0, 'PVAC_PVMeasuredVoltage_A': 365.90000000000003, 'PVAC_PVMeasuredVoltage_B': 0.3000000000000007, 'PVAC_PVMeasuredVoltage_C': -0.7999999999999989, 'PVAC_PVMeasuredVoltage_D': -1.299999999999999, 'PVAC_PVMeasuredPower_A': 3758.0, 'PVAC_PVMeasuredPower_B': 0.0, 'PVAC_PVMeasuredPower_C': 0.0, 'PVAC_PVMeasuredPower_D': 0.0, 'PVAC_LifetimeEnergyPV_Total': 34220.0, 'PVAC_Vout': 247.20000000000002, 'PVAC_Fout': 59.980000000000004, 'PVAC_Pout': 3450.0, 'PVAC_Qout': -10.0, 'PVAC_State': 'PVAC_Active', 'PVAC_GridState': 'Grid_Compliant', 'PVAC_InvState': 'INV_Grid_Connected', 'PVAC_PvState_A': 'PV_Active', 'PVAC_PvState_B': 'PV_Active', 'PVAC_PvState_C': 'PV_Active', 'PVAC_PvState_D': 'PV_Active', 'PVI-PowerStatusSetpoint': 'on'}, 'PVS--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'PVAC--1538100-01-F--CN322025C1F0F5', 'partNumber': '1538100-01-F', 'serialNumber': 'CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': '0eb61d6819b2b3', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 297}, 'PVS_vLL': 246.20000000000002, 'PVS_State': 'PVS_Active', 'PVS_SelfTestState': 'PVS_SelfTestOff', 'PVS_EnableOutput': True, 'PVS_StringA_Connected': True, 'PVS_StringB_Connected': False, 'PVS_StringC_Connected': False, 'PVS_StringD_Connected': False, 'alerts': ['PVS_a018_MciStringB', 'PVS_a019_MciStringC', 'PVS_a020_MciStringD']}, 'TEMSA--1624171-00-G--GF2220660001AL': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '1624171-00-G', 'serialNumber': 'GF2220660001AL', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 300}, 'ISLAND_VL1N_Main': 122.5, 'ISLAND_FreqL1_Main': 60.0, 'ISLAND_VL1N_Load': 122.5, 'ISLAND_FreqL1_Load': 60.0, 'ISLAND_PhaseL1_Main_Load': 0.0, 'ISLAND_VL2N_Main': 124.5, 'ISLAND_FreqL2_Main': 60.0, 'ISLAND_VL2N_Load': 124.5, 'ISLAND_FreqL2_Load': 60.0, 'ISLAND_PhaseL2_Main_Load': 0.0, 'ISLAND_VL3N_Main': 0.0, 'ISLAND_FreqL3_Main': 0.0, 'ISLAND_VL3N_Load': 0.0, 'ISLAND_FreqL3_Load': 0.0, 'ISLAND_PhaseL3_Main_Load': -256.0, 'ISLAND_L1L2PhaseDelta': 179.5, 'ISLAND_L1L3PhaseDelta': -256.0, 'ISLAND_L2L3PhaseDelta': -256.0, 'ISLAND_GridState': 'ISLAND_GridState_Grid_Compliant', 'ISLAND_L1MicrogridOk': True, 'ISLAND_L2MicrogridOk': True, 'ISLAND_L3MicrogridOk': False, 'ISLAND_ReadyForSynchronization': True, 'ISLAND_GridConnected': True, 'METER_Z_CTA_InstRealPower': 320.0, 'METER_Z_CTB_InstRealPower': -172.0, 'METER_Z_CTA_InstReactivePower': -100.0, 'METER_Z_CTB_InstReactivePower': -81.0, 'METER_Z_LifetimeEnergyNetImport': 39544.0, 'METER_Z_LifetimeEnergyNetExport': 417.0, 'METER_Z_VL1G': 122.89, 'METER_Z_VL2G': 124.74000000000001, 'METER_Z_CTA_I': 4.745, 'METER_Z_CTB_I': 3.95}, 'TESLA--GF2220660001AL': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'GF2220660001AL', 'manufacturer': 'TESLA', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [1]}}, 'NEURIO--VAH4755AB5813': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'VAH4755AB5813', 'manufacturer': 'NEURIO', 'firmwareVersion': '1.7.1-Tesla', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [5]}, 'NEURIO_CT0_Location': 'solarRGM', 'NEURIO_CT0_InstRealPower': -2724.0}, 'NEURIO--VAH4644AB0258': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'VAH4644AB0258', 'manufacturer': 'NEURIO', 'firmwareVersion': '1.7.1-Tesla', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [5]}, 'NEURIO_CT0_Location': 'solarRGM', 'NEURIO_CT0_InstRealPower': 3460.56005859375}, 'TESLA--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': '1538100-01-F--CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'pvInverterAttributes': {'nameplateRealPowerW': 7680}}, 'TESLA--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': '1538100-01-F--CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'pvInverterAttributes': {'nameplateRealPowerW': 7680}}}
String Data: {'A': {'Current': 5.67, 'Voltage': 241.60000000000002, 'Power': 1368.0, 'State': 'PV_Active', 'Connected': True}, 'B': {'Current': 5.73, 'Voltage': 241.9, 'Power': 1377.0, 'State': 'PV_Active_Parallel', 'Connected': True}, 'C': {'Current': 0.0, 'Voltage': -0.29999999999999893, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'D': {'Current': 0.0, 'Voltage': -1.299999999999999, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'A1': {'Current': 10.42, 'Voltage': 365.90000000000003, 'Power': 3758.0, 'State': 'PV_Active', 'Connected': True}, 'B1': {'Current': 0.01, 'Voltage': 0.3000000000000007, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'C1': {'Current': 0.0, 'Voltage': -0.7999999999999989, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'D1': {'Current': 0.0, 'Voltage': -1.299999999999999, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}}
So with all this data, any idea if there's anything wrong?
Also, why are the strings A and B always showing the same power?
Thank you.
I got my 10kW system installation done a few days ago and I the peak values (midday and sunny) never go over 6.5kW and I was wondering if that's normal. It is two systems connected to two Powerwall+. The inclination is 9/12 (36.86 degrees) and they are facing south (azimuth is 209).
This is the house (It shows some shadow in the picture but it has none when I notice the peak value may be too low).
Inverter 1 wiring:
Inverter 2 wiring:
Data from PyPowerwall:
Battery power level: 44%
Combined power metrics: {'site': 90, 'solar': 6260, 'battery': -5400, 'load': 965.25}
Grid Power: 0.09kW
Solar Power: 6.26kW
Battery Power: -5.40kW
Home Power: 0.97kW
Grid raw: {'last_communication_time': '2022-06-13T12:43:54.064582899-04:00', 'instant_power': 90, 'instant_reactive_power': -131, 'instant_apparent_power': 158.93709447451215, 'frequency': 0, 'energy_exported': 417, 'energy_imported': 39544, 'instant_average_voltage': 247.45, 'instant_average_current': 8.58, 'i_a_current': 0, 'i_b_current': 0, 'i_c_current': 0, 'last_phase_voltage_communication_time': '0001-01-01T00:00:00Z', 'last_phase_power_communication_time': '0001-01-01T00:00:00Z', 'last_phase_energy_communication_time': '0001-01-01T00:00:00Z', 'timeout': 1500000000, 'num_meters_aggregated': 1, 'instant_total_current': 8.58}
Solar raw: {'last_communication_time': '2022-06-13T12:43:54.088864433-04:00', 'instant_power': 6260, 'instant_reactive_power': 0, 'instant_apparent_power': 6260, 'frequency': 59.980000000000004, 'energy_exported': 63310, 'energy_imported': 0, 'instant_average_voltage': 246.8, 'instant_average_current': 25.364667747163693, 'i_a_current': 0, 'i_b_current': 0, 'i_c_current': 0, 'last_phase_voltage_communication_time': '0001-01-01T00:00:00Z', 'last_phase_power_communication_time': '0001-01-01T00:00:00Z', 'last_phase_energy_communication_time': '0001-01-01T00:00:00Z', 'timeout': 1000000000, 'num_meters_aggregated': 2, 'instant_total_current': 25.364667747163693}
Vitals: {'STSTSM--1538000-25-F--GF22206600017G': {'partNumber': '1538000-25-F', 'serialNumber': 'GF22206600017G', 'manufacturer': 'TESLA', 'firmwareVersion': '2022-04-28-ga12200ec2', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 207}, 'STSTSM-Location': 'SolarPowerwall', 'alerts': ['GridCodesWrite', 'GridCodesWrite', 'FWUpdateSucceeded', 'BackfeedLimited', 'SystemConnectedToGrid', 'PodCommissionTime']}, 'TETHC--3012170-25-C--TG122130001JNG': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '3012170-25-C', 'serialNumber': 'TG122130001JNG', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 224}, 'THC_State': 'THC_STATE_AUTONOMOUSCONTROL', 'THC_AmbientTemp': 24.5}, 'TEPOD--1081100-33-V--T22D0000006': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0000006', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 226}, 'POD_nom_energy_to_be_charged': 8944.0, 'POD_nom_energy_remaining': 6510.0, 'POD_nom_full_pack_energy': 14889.0, 'POD_available_charge_power': 7000.0, 'POD_available_dischg_power': 8760.0, 'POD_state': 'POD_ACTIVE', 'POD_enable_line': True, 'POD_ChargeComplete': False, 'POD_DischargeComplete': False, 'POD_PersistentlyFaulted': False, 'POD_PermanentlyFaulted': False, 'POD_ChargeRequest': False, 'POD_ActiveHeating': False, 'POD_CCVhold': False}, 'TEPINV--1081100-33-V--T22D0000006': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0000006', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 253}, 'PINV_EnergyDischarged': 13020.0, 'PINV_EnergyCharged': 18130.0, 'PINV_VSplit1': 124.7, 'PINV_VSplit2': 122.60000000000001, 'PINV_PllFrequency': 59.971000000000004, 'PINV_PllLocked': True, 'PINV_Pout': -2.7, 'PINV_Qout': 0.04, 'PINV_Vout': 247.20000000000002, 'PINV_Fout': 59.988, 'PINV_ReadyForGridForming': True, 'PINV_State': 'PINV_GridFollowing', 'PINV_GridState': 'Grid_Compliant', 'PINV_HardwareEnableLine': True, 'PINV_PowerLimiter': 'PWRLIM_POD_Power_Limit', 'alerts': ['PINV_a067_overvoltageNeutralChassis']}, 'TETHC--3012170-25-C--TG122117000WLV': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '3012170-25-C', 'serialNumber': 'TG122117000WLV', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 224}, 'THC_State': 'THC_STATE_AUTONOMOUSCONTROL', 'THC_AmbientTemp': 24.10000000000001}, 'TEPOD--1081100-33-V--T22D0003283': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0003283', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 226}, 'POD_nom_energy_to_be_charged': 8953.0, 'POD_nom_energy_remaining': 6473.0, 'POD_nom_full_pack_energy': 14876.0, 'POD_available_charge_power': 7000.0, 'POD_available_dischg_power': 8770.0, 'POD_state': 'POD_ACTIVE', 'POD_enable_line': True, 'POD_ChargeComplete': False, 'POD_DischargeComplete': False, 'POD_PersistentlyFaulted': False, 'POD_PermanentlyFaulted': False, 'POD_ChargeRequest': False, 'POD_ActiveHeating': False, 'POD_CCVhold': False}, 'TEPINV--1081100-33-V--T22D0003283': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1081100-33-V', 'serialNumber': 'T22D0003283', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 253}, 'PINV_EnergyDischarged': 13060.0, 'PINV_EnergyCharged': 18260.0, 'PINV_VSplit1': 124.5, 'PINV_VSplit2': 122.4, 'PINV_PllFrequency': 59.976, 'PINV_PllLocked': True, 'PINV_Pout': -2.67, 'PINV_Qout': 0.05, 'PINV_Vout': 246.8, 'PINV_Fout': 59.989000000000004, 'PINV_ReadyForGridForming': True, 'PINV_State': 'PINV_GridFollowing', 'PINV_GridState': 'Grid_Compliant', 'PINV_HardwareEnableLine': True, 'PINV_PowerLimiter': 'PWRLIM_POD_Power_Limit', 'alerts': ['PINV_a067_overvoltageNeutralChassis']}, 'PVAC--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'TETHC--3012170-25-C--TG122130001JNG', 'partNumber': '1538100-01-F', 'serialNumber': 'CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 296}, 'PVAC_Iout': 10.68, 'PVAC_VL1Ground': 124.19999999999999, 'PVAC_VL2Ground': 121.5, 'PVAC_VHvMinusChassisDC': -212.0, 'PVAC_PVCurrent_A': 5.67, 'PVAC_PVCurrent_B': 5.73, 'PVAC_PVCurrent_C': 0.0, 'PVAC_PVCurrent_D': 0.0, 'PVAC_PVMeasuredVoltage_A': 241.60000000000002, 'PVAC_PVMeasuredVoltage_B': 241.9, 'PVAC_PVMeasuredVoltage_C': -0.29999999999999893, 'PVAC_PVMeasuredVoltage_D': -1.299999999999999, 'PVAC_PVMeasuredPower_A': 1368.0, 'PVAC_PVMeasuredPower_B': 1377.0, 'PVAC_PVMeasuredPower_C': 0.0, 'PVAC_PVMeasuredPower_D': 0.0, 'PVAC_LifetimeEnergyPV_Total': 29090.0, 'PVAC_Vout': 247.60000000000002, 'PVAC_Fout': 59.976, 'PVAC_Pout': 2760.0, 'PVAC_Qout': 20.0, 'PVAC_State': 'PVAC_Active', 'PVAC_GridState': 'Grid_Compliant', 'PVAC_InvState': 'INV_Grid_Connected', 'PVAC_PvState_A': 'PV_Active', 'PVAC_PvState_B': 'PV_Active_Parallel', 'PVAC_PvState_C': 'PV_Active', 'PVAC_PvState_D': 'PV_Active', 'PVI-PowerStatusSetpoint': 'on'}, 'PVS--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'PVAC--1538100-01-F--CN321286C1F0OR', 'partNumber': '1538100-01-F', 'serialNumber': 'CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': '0eb61d6819b2b3', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 297}, 'PVS_vLL': 247.4, 'PVS_State': 'PVS_Active', 'PVS_SelfTestState': 'PVS_SelfTestOff', 'PVS_EnableOutput': True, 'PVS_StringA_Connected': True, 'PVS_StringB_Connected': True, 'PVS_StringC_Connected': False, 'PVS_StringD_Connected': False, 'alerts': ['PVS_a019_MciStringC', 'PVS_a020_MciStringD']}, 'PVAC--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'TETHC--3012170-25-C--TG122117000WLV', 'partNumber': '1538100-01-F', 'serialNumber': 'CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 296}, 'PVAC_Iout': 14.76, 'PVAC_VL1Ground': 124.5, 'PVAC_VL2Ground': 121.5, 'PVAC_VHvMinusChassisDC': -212.0, 'PVAC_PVCurrent_A': 10.42, 'PVAC_PVCurrent_B': 0.01, 'PVAC_PVCurrent_C': 0.0, 'PVAC_PVCurrent_D': 0.0, 'PVAC_PVMeasuredVoltage_A': 365.90000000000003, 'PVAC_PVMeasuredVoltage_B': 0.3000000000000007, 'PVAC_PVMeasuredVoltage_C': -0.7999999999999989, 'PVAC_PVMeasuredVoltage_D': -1.299999999999999, 'PVAC_PVMeasuredPower_A': 3758.0, 'PVAC_PVMeasuredPower_B': 0.0, 'PVAC_PVMeasuredPower_C': 0.0, 'PVAC_PVMeasuredPower_D': 0.0, 'PVAC_LifetimeEnergyPV_Total': 34220.0, 'PVAC_Vout': 247.20000000000002, 'PVAC_Fout': 59.980000000000004, 'PVAC_Pout': 3450.0, 'PVAC_Qout': -10.0, 'PVAC_State': 'PVAC_Active', 'PVAC_GridState': 'Grid_Compliant', 'PVAC_InvState': 'INV_Grid_Connected', 'PVAC_PvState_A': 'PV_Active', 'PVAC_PvState_B': 'PV_Active', 'PVAC_PvState_C': 'PV_Active', 'PVAC_PvState_D': 'PV_Active', 'PVI-PowerStatusSetpoint': 'on'}, 'PVS--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'PVAC--1538100-01-F--CN322025C1F0F5', 'partNumber': '1538100-01-F', 'serialNumber': 'CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': '0eb61d6819b2b3', 'lastCommunicationTime': 1655138633, 'teslaEnergyEcuAttributes': {'ecuType': 297}, 'PVS_vLL': 246.20000000000002, 'PVS_State': 'PVS_Active', 'PVS_SelfTestState': 'PVS_SelfTestOff', 'PVS_EnableOutput': True, 'PVS_StringA_Connected': True, 'PVS_StringB_Connected': False, 'PVS_StringC_Connected': False, 'PVS_StringD_Connected': False, 'alerts': ['PVS_a018_MciStringB', 'PVS_a019_MciStringC', 'PVS_a020_MciStringD']}, 'TEMSA--1624171-00-G--GF2220660001AL': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'partNumber': '1624171-00-G', 'serialNumber': 'GF2220660001AL', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'teslaEnergyEcuAttributes': {'ecuType': 300}, 'ISLAND_VL1N_Main': 122.5, 'ISLAND_FreqL1_Main': 60.0, 'ISLAND_VL1N_Load': 122.5, 'ISLAND_FreqL1_Load': 60.0, 'ISLAND_PhaseL1_Main_Load': 0.0, 'ISLAND_VL2N_Main': 124.5, 'ISLAND_FreqL2_Main': 60.0, 'ISLAND_VL2N_Load': 124.5, 'ISLAND_FreqL2_Load': 60.0, 'ISLAND_PhaseL2_Main_Load': 0.0, 'ISLAND_VL3N_Main': 0.0, 'ISLAND_FreqL3_Main': 0.0, 'ISLAND_VL3N_Load': 0.0, 'ISLAND_FreqL3_Load': 0.0, 'ISLAND_PhaseL3_Main_Load': -256.0, 'ISLAND_L1L2PhaseDelta': 179.5, 'ISLAND_L1L3PhaseDelta': -256.0, 'ISLAND_L2L3PhaseDelta': -256.0, 'ISLAND_GridState': 'ISLAND_GridState_Grid_Compliant', 'ISLAND_L1MicrogridOk': True, 'ISLAND_L2MicrogridOk': True, 'ISLAND_L3MicrogridOk': False, 'ISLAND_ReadyForSynchronization': True, 'ISLAND_GridConnected': True, 'METER_Z_CTA_InstRealPower': 320.0, 'METER_Z_CTB_InstRealPower': -172.0, 'METER_Z_CTA_InstReactivePower': -100.0, 'METER_Z_CTB_InstReactivePower': -81.0, 'METER_Z_LifetimeEnergyNetImport': 39544.0, 'METER_Z_LifetimeEnergyNetExport': 417.0, 'METER_Z_VL1G': 122.89, 'METER_Z_VL2G': 124.74000000000001, 'METER_Z_CTA_I': 4.745, 'METER_Z_CTB_I': 3.95}, 'TESLA--GF2220660001AL': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'GF2220660001AL', 'manufacturer': 'TESLA', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [1]}}, 'NEURIO--VAH4755AB5813': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'VAH4755AB5813', 'manufacturer': 'NEURIO', 'firmwareVersion': '1.7.1-Tesla', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [5]}, 'NEURIO_CT0_Location': 'solarRGM', 'NEURIO_CT0_InstRealPower': -2724.0}, 'NEURIO--VAH4644AB0258': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': 'VAH4644AB0258', 'manufacturer': 'NEURIO', 'firmwareVersion': '1.7.1-Tesla', 'lastCommunicationTime': 1655138634, 'meterAttributes': {'meterLocation': [5]}, 'NEURIO_CT0_Location': 'solarRGM', 'NEURIO_CT0_InstRealPower': 3460.56005859375}, 'TESLA--1538100-01-F--CN321286C1F0OR': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': '1538100-01-F--CN321286C1F0OR', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'pvInverterAttributes': {'nameplateRealPowerW': 7680}}, 'TESLA--1538100-01-F--CN322025C1F0F5': {'componentParentDin': 'STSTSM--1538000-25-F--GF22206600017G', 'serialNumber': '1538100-01-F--CN322025C1F0F5', 'manufacturer': 'TESLA', 'firmwareVersion': 'a54352e6706386', 'lastCommunicationTime': 1655138634, 'pvInverterAttributes': {'nameplateRealPowerW': 7680}}}
String Data: {'A': {'Current': 5.67, 'Voltage': 241.60000000000002, 'Power': 1368.0, 'State': 'PV_Active', 'Connected': True}, 'B': {'Current': 5.73, 'Voltage': 241.9, 'Power': 1377.0, 'State': 'PV_Active_Parallel', 'Connected': True}, 'C': {'Current': 0.0, 'Voltage': -0.29999999999999893, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'D': {'Current': 0.0, 'Voltage': -1.299999999999999, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'A1': {'Current': 10.42, 'Voltage': 365.90000000000003, 'Power': 3758.0, 'State': 'PV_Active', 'Connected': True}, 'B1': {'Current': 0.01, 'Voltage': 0.3000000000000007, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'C1': {'Current': 0.0, 'Voltage': -0.7999999999999989, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}, 'D1': {'Current': 0.0, 'Voltage': -1.299999999999999, 'Power': 0.0, 'State': 'PV_Active', 'Connected': False}}
So with all this data, any idea if there's anything wrong?
Also, why are the strings A and B always showing the same power?
Thank you.