I installed the Hubbel 9450 in preparation for my delivery and have it connected to a 40Amp breaker. I planned on setting my Grizzl-E charger to 32A as I read you can only use 80% of the capacity of the breaker for EV charging. The inspector when he came to my house actually wrote 32A MAX charging on my outlet.
As others have mentioned, I'll be charging overnight and probably could reduce the 32A output to the next lower setting, as I won't need the car until the morning. I only have 100A service in my house.
Located in Canada
You have touched on one of the really *sticky* issues (at least in Canada) on the 14-50 plug.
Up until late 2016 the Gen1 UMC came with a 40 amp rated 14-50 plug. There was a garage fire in Toronto that year and it was attributed to the charging Tesla's 14-50 connector getting too hot. Could have been the plug - could have been the receptacle....we'll never know. What did happen, at the end of 16/beginning of 17, Tesla started sending out new UMC, and new 14-50 adapter to ALL existing Canadian owners, all rated 32 amps. (We were supposed to return the old ones, and some people did
). All new Canadian Teslas were now equipped with the 32 amp connector. For a brief period, there was a bit of an uproar about smuggling the US adapter up to Canada, but eventually, the US models also were de-rated to 32 amps.
So, as economics go, some of the new owners began to look at wiring up 14-50's on a 40 amp breaker (80% = 32 amps). Smaller wire, less expensive installation. This ticked off the Electrical Safety Authority (ESA). In their eyes, If a 50 amp (40 amp rated) receptacle is in play, what is to stop someone in an older Tesla, or others, from plugging in and drawing 40 amps. There are a couple of threads about this on this forum.
I was a supplier to the electrical industry (Including Receptacles - Midwest, and Aluminium/copper building wire - Alcan, Nexans), so I wrote an email to one of the chief inspectors at ESA for his opinion. He wrote a long answer - someone may be able to find it here -but in essence, he said 'If it's rated at 50 amps, you'd better use 50 amp rated cable, and a 50 amp breaker".
This comment was generally ignored, and eventually, ESA softened their position. That's why he wrote it on your receptacle, and it's a good idea. This is why we should always draw a permit, and get the job inspected
Canada folks. Other Countries/States YMMV.
PS I won't comment on the aluminium/copper wire discussion, above, it's a 5 page story. Also, Midwest does make a great metal heavy duty outdoor receptacle U054. The actual receptacle
was Cooper, but may have changed in the last few years.