Jordan0301 - since you are new to electricity here are a couple of things to consider.
- Different postings in these forums will talk in amps, volts and watts. Without getting too technical, the simple math is that Amps x Volts = Watts. Most US homes have what is nominally called "220v", but may in fact range from 203v to 250v (mine is 240-245v). But at a supercharger (aka SC) you may see 300-400v so 300a would produce 90kW - 120kW.
- The car battery is DC, the charger in the car converts AC to DC. The only exception to this is at a Supercharger or CHAdeMO charger which both put out DC and bypass the charger in the car. The supplied "charger" (aka UMC) or wall charger (HPWC) have a little bit of smarts to control the flow of electricity, but do not do any conversion from AC to DC.
- This is something you really want to get right, not a place to skimp. Your house and family could be at risk. Every plug connection is a weak point in the electrical path. Ideally the only plug is the one into your MS. You will also find it a bit of pain to use the supplied charger (UMC) for daily charging, though there are certainly people who use it for daily charging.
- The circuit breaker protects the wire and prevents it from becoming a heating element (think toaster) that would burn down your house. The circuit breaker is sized to the wire and wire run length to protect the wire and your house.
- Continuous use like charging the car should never use more than 80% of the rated capacity. So as others have pointed out, with a 30a circuit you would want to set the charger to be limited to 24a, IF your outlet is fed by a wire that can actually handle 30a.
- You didn't say which charger you had, but assuming a new MS without the larger charger option, then it will max out at 48a (so nominally 48 x 220v ~ 10,000 watts aka 10kW).
- Based on the picture you posted, it looks like this is in your garage, probably not too far from main electrical panel the way most homes are built. I strongly recommend hiring a good electrician who could, in order of time/cost and preferred solution:
a) verify the wire size and adjust the circuit breaker if needed so you can use an adapter.
b) replace your current wiring with larger wiring that would allow a 60a circuit to a 14-50 outlet so you can use the supplied charger without an adapter.
c) install an HPWC with a new 60a circuit.
If you're charging at night when most of your big home consumers are off (ovens, hair dryers, pool pump, A/C) you shouldn't have to increase the capacity of your main panel.
Good luck and enjoy your MS!