NEMA 14-50 8 gauge wire

This site may earn commission on affiliate links.
Thanks for this level of detail.

I'm using 8AWG Romex that shows rated for 90C. This is run through walls (inside).

I have it wired up now to a 40a breaker, but I was thinking of putting in a 50a breaker for the Tesla
I use the same 40a setup on our PHEV with a 32a Siemens Versicharge without issue.

Link to cable:
Southwire 125 ft. 8/3 Stranded Romex SIMpull CU NM-B W/G Wire-63949202 - The Home Depot

Product documentation shows max Amperage on the cable @ 40a, so I was thinking the UMC1 would work.

Because that is NM wire (Romex), NEC says you must use the 60c rating instead of 75c or 90c even if that is what is labeled on the cable. So that wire is only good for up to 40 amps.

Electric Vehicle Chargers are considered "Continuous Loads" under the NEC and so you must size the wire and circuit breaker 25% larger. So for a 32a charger you need a 40a capable wire and breaker. For a 40a charger you need 50a capable wire and breaker.

So please do not just switch the breaker to 50a! That would be dangerous and not code compliant. Note that the new UMC Gen 2 that ships with all new Tesla's now is only 32a so it would be fine on a 40a circuit.

Why not just folllow Tesla’s installation instructions as posted above (post #4). They specify the wire and breaker sizes for a NEMA 14-50 outlet for the UMC. Tesla has a similar document for every outlet type, linked from the home charging page. Don’t try to reinvent the wheel, RTFM instead.

So I appreciate the doc that was linked to from Tesla, but I disagree with it. #8 AWG copper wire is ok for a 50a circuit if run in conduit (though I might still use #6 myself). I think Tesla just dumbs it down to 6awg since that is safe in virtually all conditions. From a code standpoint, I don't think that doc has any applicability. I went and looked at the actual UMC Gen 2 manual and it does not specify how to wire up the NEMA 14-50 receptacle. So even if the "you must follow the manufacturers instructions" would apply for wiring a NEMA 14-50 receptacle, the manual says nothing (and I don't know that the following manufacturers instructions thing even applies to non-hard wired devices). The fact that an extra document exists on Tesla's web site I am not sure gives it any standing.
 
  • Like
Reactions: jsmay311
Because that is NM wire (Romex), NEC says you must use the 60c rating instead of 75c or 90c even if that is what is labeled on the cable. So that wire is only good for up to 40 amps.

Electric Vehicle Chargers are considered "Continuous Loads" under the NEC and so you must size the wire and circuit breaker 25% larger. So for a 32a charger you need a 40a capable wire and breaker. For a 40a charger you need 50a capable wire and breaker.

So please do not just switch the breaker to 50a! That would be dangerous and not code compliant. Note that the new UMC Gen 2 that ships with all new Tesla's now is only 32a so it would be fine on a 40a circuit.

Great, thanks for responding and confirming. I'll just work with the Gen2 then and forget it.
 
Just to those asking why am I trying to save money on the wire, that is not the issue. my electrician recommended #8, not #6 wire, and I don't know anything about electricity so I was asking for advice. This is not a money issue, especially if it is just 30 bucks, just looking for why he would say that and what it means
 
He probably recommended #8 because it’s easier to pull through conduit than thicker wire. Laziness is a powerful motivator.

Yeah, I do tend to agree here. I probably would ask what the cost delta would be to use #6 AWG and I might just go with that... Hopefully it would not require upsizing the conduit and so the only difference would be conductor cost. I ran my NEMA 14-50 with #6 AWG since it was only a few feet of wire and it was in flex conduit. I also ran my Wall Connector with #6 in EMT and put it on a 60a breaker.

An EV is likely the highest current draw device in the house and it is on for many hours a day potentially, so the worst case is you spend a big more and have some cooler running wires and lower line losses...
 
(I encourage anyone to double check my calcs here. Split-phase circuits can trip me up sometimes.)

A quick check of an online voltage drop calculator shows that upgrading from 8AWG to 6AWG on a 35 foot run will reduce line losses on a 240V circuit drawing 32A from 0.59% down to 0.37%. So a you'd get a 0.22% reduction/improvement in line losses.

If you drive 10,000 miles per year and get the EPA efficiency of 0.26 kWh/mile, then you'd save (10,000 x 0.26 x 0.0022 =) 5.7 kWh/year. Multiply that by your $/kWh rate to get $/year, then multiply by years you expect to use this circuit for charging an EV to get total cost savings.

For example, if you pay $0.20/kWh, you'd save $1.14/year. If you expect to use the circuit/outlet for 15 years, then you'd save $17 over that period.

He probably recommended #8 because it’s easier to pull through conduit than thicker wire. Laziness is a powerful motivator.

Or maybe it's just because the smallest wire that meets code is what is used the vast majority of the time. No need to impugn his character.
 
Don’t buy a Tesla and the skimp on the wire. Buy a Bolt and skimp. What’s the price difference? $30? $100? If it’s a $100 I would skimp to get it down to $30. But that’s just me.

So people who buy Bolts (or other non-Teslas) skimp on electrical work? Dafuq? Seriously? :rolleyes:

I just had an electrician install a 14-50 outlet. 6 gauge wire, 50A breaker, no skimping . Sorry for not living up to your stereotype.
 
This is an old thread but one thing I read here really concerns me is that ppl are putting a 40 Amp breaker on a Nema 14-50 outlet. Even though the Gen 2 mobile connector only pulls 32A in theory necessitating a 40A breaker, the expectation of a Nema 14-50 outlet is that it is 50 A amp capable. The next owner of the house may plug in a dryer, welder, or compressor expecting a 50A circuit with a 50 A outlet for 40 Amp continuous service (there is a 20% derating between peak and continuous). It is dangerous to undersize the breaker as a future device may pull 40A continuous, tripping (best case) or worse overheating the the undersized 40 A peak breaker. An overheating breaker can lead to a fire caused by the resistance heating.

If installing a HPWC set to 40A for a 32 Amp continuous draw, then the 40 Amp breaker is permissable as the device is permanently wired to the 40 Amp device and will not be disconnected to operate a device of higher and lower current.
 
  • Like
Reactions: StealthP3D
This is an old thread but one thing I read here really concerns me is that ppl are putting a 40 Amp breaker on a Nema 14-50 outlet. Even though the Gen 2 mobile connector only pulls 32A in theory necessitating a 40A breaker, the expectation of a Nema 14-50 outlet is that it is 50 A amp capable. The next owner of the house may plug in a dryer, welder, or compressor expecting a 50A circuit with a 50 A outlet for 40 Amp continuous service (there is a 20% derating between peak and continuous). It is dangerous to undersize the breaker as a future device may pull 40A continuous, tripping (best case) or worse overheating the the undersized 40 A peak breaker. An overheating breaker can lead to a fire caused by the resistance heating.

If installing a HPWC set to 40A for a 32 Amp continuous draw, then the 40 Amp breaker is permissable as the device is permanently wired to the 40 Amp device and will not be disconnected to operate a device of higher and lower current.
I get your concern, but the fact is that it's to code, and it's even the recommended install for a number of 30-32a J1772 EVSEs out there (like the one I own). My take is that people should install a 50a circuit if they can, but if their service or existing wiring can only handle 40a, then go ahead and do that.
 
  • Helpful
Reactions: Rocky_H
My electrician installed a NEMA 14-50 with a 50 amp breaker next to the panel which is about 1 foot and used an 8 gauge wire. I asked him and he said it is ok since it is very close to the panel. I noticed later that he hasn't used the separate ground, instead, he connected the ground and neutral (white wire). Is it safe? Please advice. Thank you
 
used an 8 gauge wire.
This isn't enough information to answer by just telling the wire gauge. Different types of wire or cable have different amp ratings, so you haven't given enough of a description of exactly what it is to tell. Is this separate wires run though conduit? Or is it that a whole cable that has several wires bundled together inside a tight rubber sheath? 8 gauge would be acceptable if it's separate wires in conduit, but not acceptable if it's NM-B cable.

I noticed later that he hasn't used the separate ground, instead, he connected the ground and neutral (white wire).
Connected them where? If they are just tied together in the outlet box, then that is definitely wrong. They need to stay separate all the way back to the main panel in the house. If that main panel, then yes, ground and neutral can be interchanged and tied together there (and ONLY there).
 
This isn't enough information to answer by just telling the wire gauge. Different types of wire or cable have different amp ratings, so you haven't given enough of a description of exactly what it is to tell. Is this separate wires run though conduit? Or is it that a whole cable that has several wires bundled together inside a tight rubber sheath? 8 gauge would be acceptable if it's separate wires in conduit, but not acceptable if it's NM-B cable.


Connected them where? If they are just tied together in the outlet box, then that is definitely wrong. They need to stay separate all the way back to the main panel in the house. If that main panel, then yes, ground and neutral can be interchanged and tied together there (and ONLY there).
Thank You so much for the quick reply. Yes, there are 3 separate cables. Black, Red, and White. The wires running from the electric panel to NEMA14-50 is just 1 ft. long and all wires are separate but the gauge is 8. Is that enough to charge my Tesla Model Y(which is delivering next month).? My main concern is neutral and Ground wire since it is connected with a small 2-inch wire in the NEMA receptacle. Is that safe?
 
Thank You so much for the quick reply. Yes, there are 3 separate cables. Black, Red, and White. The wires running from the electric panel to NEMA14-50 is just 1 ft. long and all wires are separate but the gauge is 8.
You didn't mention a conduit, but there should be some if they are individual wires. But yes, if those are separate wires, 8 gauge is acceptable for a 50A rated circuit. If you look up in the table here, the wires in conduit would be THWN or THHN, those both have a rating of at least 50A. So the thickness of the wire would be OK, but only 3 wires is definitely a problem.

My main concern is neutral and Ground wire since it is connected with a small 2-inch wire in the NEMA receptacle. Is that safe?
But this is still a problem. A 14-50 outlet MUST have 4 wires to connect it properly. Do you mean that the white wire goes to it, and then it uses a small 2 inch wire to basically "jumper" the neutral and ground pins together on the outlet itself? That is definitely wrong. Neutral and ground each need to have their own separate wires running all the way back to the panel. The ground wire is allowed to be much smaller and can be a bare copper wire that's not insulated, but it does need to be there.

I'm getting really concerned about who the person is who did this. An actual electrician would know that a 14-XX type of outlet can't be installed with just 3 wires.

*EDIT* Oh, I did just remember something. In some places, the metal conduit the wires are in can be used as the ground wire that goes back to the panel if it is connected on both ends. Is this in metal conduit that is being used as the ground?
 
Thank You so much for the quick reply. Yes, there are 3 separate cables. Black, Red, and White. The wires running from the electric panel to NEMA14-50 is just 1 ft. long and all wires are separate but the gauge is 8. Is that enough to charge my Tesla Model Y(which is delivering next month).? My main concern is neutral and Ground wire since it is connected with a small 2-inch wire in the NEMA receptacle. Is that safe?
I think it just needs a ground and the two 120V wires to be able to charge at 240V. I find it strange that he didn't run a green ground wire. Is this in a conduit? Is the box that the receptacle is installed in, metal? You should definitely have a green ground wire attached to the receptacles ground terminal.
 
I think it just needs a ground and the two 120V wires to be able to charge at 240V. I find it strange that he didn't run a green ground wire. Is this in a conduit? Is the box that the receptacle is installed in, metal? You should definitely have a green ground wire attached to the receptacles ground terminal.
Yes, an EVSE only needs the two hots and a ground. But it's a 14-50 receptacle, which is required to have a neutral. The car won't care if there isn't a neutral connected to the neutral lug in the receptacle, in fact I don't believe the neutral pin is connected to anything in the mobile connector. But something else like an RV or electric range would DEFINITELY care if the neutral isn't there. A floating neutral will burn up all sorts of things in something expecting it to be there. If you don't want to run a neutral, install a NEMA 6-50 receptacle instead.

If it's solid conduit all the way back to the panel (NO flex in the run at all), a separate equipment grounding conductor is not necessary as the conduit serves that purpose. That could possibly explain the conduit only containing two hots and a neutral.
 
  • Informative
Reactions: Rocky_H
But something else like an RV or electric range would DEFINITELY care if the neutral isn't there. A floating neutral will burn up all sorts of things in something expecting it to be there.
Why? A 120V device is the only thing looking for a neutral. If the neutral leg isn't there, the device simply wouldn't get power.

As for this installation, with such a small run, it seems there wouldn't be much reason not to run the 6 ga wires and have a proper ground. Even replacing the wires at this point would be trivial.
 
Why? A 120V device is the only thing looking for a neutral. If the neutral leg isn't there, the device simply wouldn't get power.

As for this installation, with such a small run, it seems there wouldn't be much reason not to run the 6 ga wires and have a proper ground. Even replacing the wires at this point would be trivial.
Most appliances use a 14-50 because they need both 120v and 240v. Unfortunately, leaving the neutral out does not necessarily mean the 120v parts simply get no power. Instead the return voltage can find it's way through other parts of the circuit to the other leg or to ground.

It's even worse in the case of something like an RV which will have appliances connected to both 120v legs. The return voltage will find it's way through the wiring to another appliance and through it to the other leg. Since the neutral is floating one appliance may see a low voltage and the other may see a very high one. Finally, you can end up with a hot chassis if one of those appliances only has a two prong plug, creating a shock hazard.